Neutral Current Transformer

03/10/2011 6:30 AM

1. Core dimensions, turns and wire size of the Netural ct are given but the VA or burden is not given, can we design the neutral Ct with these inputs ?

2. What is the accuarcy class that Neutral CT needed?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Neutral Current transformer

03/10/2011 7:55 AM

Those are already design outputs, no design activity is left in that except for few things like insulation consideration etc,All needed is fabrication based output you suggested.

All the CT across the world may not have uniform standard,Chose standard based on Who is the buyer, Where to be used?Or you should disclose more details so that members knows that may help you,

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#3
In reply to #1

Re: Neutral Current transformer

03/10/2011 8:40 AM

VA is needed to design the CT/or any transformer, But since transformer is already designed thats why he has not given you VA, if you fabricate the transformer with the said requirement It will meet the VA requirements automatically, If who so ever gave you those details is a qualified person,

Register to Reply
Member

Join Date: Mar 2010
Location: Salem, Tamil Nadu , India
Posts: 6
#4
In reply to #1

Re: Neutral Current transformer

03/10/2011 11:10 PM

Thank u for the opinion.

Best Regards,

M.R.Thayalan

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Neutral Current transformer

03/10/2011 8:20 AM

1. Yes! It is possible to calculate the rated burden of the CT with the given inputs, but it is a cumbersome calculation.

2. The accurcay class of the neutral CT depends upon the application. If it is for REF (Restricted Earth Fault) Relay then you might need Class PS. If it is for back-up earth fault protection, then may be Class 5P10 or 10P10 might do. Else, if it is for metering (which, I doubt), then yopu should go for Class 1.0 or Class 0.5.

Register to Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#5

Re: Neutral Current Transformer

03/19/2011 2:02 AM

Mr. Dayalan, from the Secondary current of the CT and with the values of lead resistances, Relay resistance, And CT Internal resistance we can arrive at a tentative value of the Actual Value of the Burden.

It can be derived as VA or Burden = Is x (2x Lead Resistance + Relay Resistance + CT internal Resistance).

I request other members to please come up with comments on this answer.

__________________
"Engineering is Passion"