Electronic Soft Starter for 3 Phase Motor

03/10/2011 5:03 AM

Hello,

I would like to know the technique used in SCR based soft starter although i have tried it ans started the motor but some times there occurs stalling effects as not taking the speed moving very slow 1-3 revolution per second. after 3-9 seconds it get fast acceleration.

Please clarify.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: electronic soft starter for 3 phase motor

03/10/2011 8:01 AM

How many SCR'S are you using 3 or 6?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: electronic soft starter for 3 phase motor

03/10/2011 8:22 AM

Probably , the Voltage Ramp and/or the Current Ramp Settings are incorrect.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Electronic Soft Starter for 3 Phase Motor

03/10/2011 9:38 PM

Most probably, the 'Initial Voltage' setting is low or the 'Start Ramp' setting is high. Try changing both of the settings.

See page 36 (Common Settings) of this document (Softstarter Handbook)

http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/2985284834bcff7fc1256f3a00274038/$file/1sfc132002m0201.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Electronic Soft Starter for 3 Phase Motor

03/11/2011 5:32 AM

I think we need to know if you are trying to USE a commercially available soft starter made by someone else, or you are trying to MAKE YOUR OWN soft starter. Two totally different aspects of the problem you describe.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5

Re: Electronic Soft Starter for 3 Phase Motor

03/11/2011 9:23 AM

What is your application? You'll usually find these type of starters used to power conveyor or some type of gear sets. The starter slowly takes up the slack in the system before coming up to full speed, rather than a hard 3 phase start that can damage your equipment. So it should be starting slow! That's what its for.

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#6

Re: Electronic Soft Starter for 3 Phase Motor

03/11/2011 9:36 PM

How many phases are controlled in the troublesome system?

One phase at reduced voltage was offered in an SCR soft starter via RS components some 20 years ago but better electrical balance will result from more complex starters.

If one of an inverse-parallel pair of SCR's misfires DC will flow braking the motor, this could cause the 'stalling' trouble. If pulse firing (one ca 0.01ms pulse) is too early (during current flow through the other SCR) missfire follows. DC gate drive (say 6.0ms) is resistant to this trouble and the SCR will not backfire if the winding current has reversed. A gated pulse train (@ca 10kHz) may be used in lieu of DC gate drive and can be cheaper to build.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#7

Re: Electronic Soft Starter for 3 Phase Motor

03/15/2011 12:30 AM

Hi

I would suggest looking at the startup voltage boost settings, incresae this setting to improve startup break away torque. But I am not sure if the soft starter you are using has this facility.

Best Regards

Joe