Vacuum Circuit Breaker

03/12/2011 6:37 AM

how does a high voltage vaccum circuit breaker works

__________________
ahb
Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: vacuum circuit breaker

03/12/2011 7:26 AM

Please download and study this document : ect198.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: vacuum circuit breaker

03/12/2011 8:08 AM

Excellent site.

But I still don't trust vacuum after the failure of a 11KV 1200A unit. It was only switching 300A but welded closed on 2 phases.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: vacuum circuit breaker

03/12/2011 8:12 AM

Did the vacuum fail or did the mechanism fail to keep the contacts open ?

i have a (probably unjustified) feeling that if some linkage fails in a VCB, the contact closes due to external air pressure, as against other switchgear which fail safe...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #3

Re: vacuum circuit breaker

03/12/2011 11:09 AM

The vacuum failed. It didn't do the motor much good either. One the electricians had to trip the plant incoming breaker. The power company phoned up to fined out what the hell was going on. The PLC that controlled the plant sent a signal on start up and shut down to warn them, tripping the main breaker took them by surprise. Each section of the plant would use 10MW, that just vanishing with out warning, it didn't go down to well

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: vacuum circuit breaker

03/12/2011 11:22 AM

Don't they have vacuum integrity monitors on these? Seems elementary. If the vacuum fails, i can thinlk of many ways to make the CB/Contactor inoperable. Surprising that you had this issue.

Anyway, not my primary area. Still, i would think it was an elementary design feature.

Pity you had this problem. What did the manufacturer say ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #6

Re: vacuum circuit breaker

03/12/2011 12:27 PM

It's not my problem now, I'm retired.

There was no vacuum monitoring on any breaker, common sense says there should have been. But economics get in the way of engineering sense.

It did have one benefit, regular testing of VCB's which probably cost more than the monitoring had it been installed.

I used to hate writing the switching procedures for these, I knew the fault rating of the 440V boards wasn't high enough for parallel operation, all be it for a matter of seconds while the bus-section was closed and one of the feeders opened.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#4

Re: Vacuum Circuit Breaker

03/12/2011 9:25 AM

Thanks 4 the reference

__________________
One system
Register to Reply
Participant

Join Date: Sep 2006
Posts: 2
#8

Re: Vacuum Circuit Breaker

03/12/2011 10:52 PM

Check this out. http://www.joslynhivoltage.com/catVBU.htm

Register to Reply
Active Contributor

Join Date: May 2016
Location: Ahmedabad
Posts: 21
#9

Re: Vacuum Circuit Breaker

06/13/2016 7:38 AM

Vacuum circuit breakers in values high-voltage electrical distribution systems perform the same dynamic function as the breakers in your home’s electrical panel. They cut off electrical current in the event of short circuits. To understand vacuum circuit breakers, you need to know a few things about how it works. Circuit breakers contain metal electrical contacts held together by a spring-loaded trip mechanism. This trip linkage contains a mechanical heat sensor that trips off the breaker when it detects the rising temperatures generated by overloading the electrical conductor.

__________________
Control Panels India
Register to Reply Off Topic (Score 5)