kW Consumption Calculations

03/13/2011 3:00 PM

I am serving as an Electrician in Karachi Water & Sewerage Board, Karachi, Pakistan. I have calculated kW consumption of 3-phase, 50 C/s, 440 volts, o.8 pf electric induction motors of our Water Pumping Station by taking their amperes and with the formula: ampere x voltage x pf x 1.73 / 1000. Then multiply the kW consumption with hours operation perday and further multiply it with number of days in a month. But the problem is, the calculated kW consumption is very high then the consumption charged by our electric supply agency. Please help me with this. I want to show some improvement to my fellows and juniors.

Register to Reply
Pathfinder Tags: kW by Calculations
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: kW consumption calculations

03/13/2011 3:13 PM

Your method is correct. You need to check the actual amperage and voltage and calculate again. Verify the operation hours and days running. The motor may not be running full load at all times.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: kW Consumption Calculations

03/13/2011 3:58 PM

Ancillary equipment often gets overlooked, in a large plant just the lighting can account for a considerable amount. Just one building I worked in had 30KW of lights burning day and night, that was just one of over 30 buildings.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2011
Location: Malaysia
Posts: 46
#3

Re: kW Consumption Calculations

03/13/2011 11:07 PM

I don't know if this will help but when we provided Solar power to the pumping stations, we were told to buy very big and very expensive, DC to AC Inverters, to change the Solar power DC supply to 240v AC, to run the AC motors. These Inverters cost 3 times more than DC motors would cost. So to save money, we bought DC motors instead and ran them directly from the DC Solar Power supply.

The Interesting part, is that the DC motors now pumped 300% MORE water, than the AC motors of the same wattage. So we were able to SAVE 70% of the power needed.

This would indicate that you should save Electricity cost, if you change to DC motors. BUT if you only have AC power supply available, then you would have to convert this to DC, which may have high losses in the conversion. I would guess that you would still save energy with DC motors, even after conversion losses. (OR you could buy some Solar Power systems, to save the conversion losses and have NO electricity bill at all)

Register to Reply Score 2 for Off Topic
2
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#4

Re: kW Consumption Calculations

03/13/2011 11:48 PM

You seem to be putting fictitious values in the formula and thus getting wrong assessment.

For instance the standard voltage in Pakistan is 415 volts and not 440 volts, similarly you have to practically assess the actual current and power factor to come to a reliable conclusion.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: kW Consumption Calculations

03/14/2011 2:20 AM

The formula is correct.But as suggested by forum members, u have to take the actual voltage and PF and current and calculate.Other option is to take a calibrated watt hour meter and compare the readings of both meters.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#6

Re: kW Consumption Calculations

03/14/2011 8:22 PM

make your connections and start your motor.when in normal operation,measure your voltage input,operating current and with the pf,calculate the KW=√3VIcosφ.

For the energy(kwh) consumption,multiply by hours run.

__________________
Patrick Whowha
Register to Reply
Active Contributor

Join Date: Mar 2011
Location: INDIA
Posts: 10
#7

Re: kW Consumption Calculations

11/16/2011 10:49 AM

Actually speaking in √3VIcosΦ formula all were variables except 1.732. Hence the thereotical calculation you do with right formula by calculating the current and voltage at a instant may give you a margin of actual figure only.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: kW Consumption Calculations

11/16/2011 2:02 PM

Are you taking the motor NAMEPLATE amperes or are you MEASURING the amperes? The same for voltage, are you ASSUMING the voltage or are you measuring it? And even if you measured, does it change during the day / week / month? Most likely all of those things change constantly. If you go out and measure on one day at one moment, you are only taking a snapshot of consumption, not a full picture.

Think of it this way: if you stood on the side of a road with a radar gun and measured speed of a single passing car at noon on a weekend, does that tell you anything about the average speed on that road? What if you had taken a single radar reading at commute time on a week day? Is that any more indicative of the average speed?

If you really want to determine consumption, you must determine an avaerage consumption periodic cycle length and measure that entire cycle. Anything else is just a snapshot and should not be used to determine anything important.

By the way, your calculation is also missing the motor efficiency, and that too will vary by loading, voltage etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

A.A.Khi (1); chandru1982b4u (1); JRaef (1); nesubra (1); Patrick Whowha (1); Paulmil (1); TonyS (1); wareagle (1)