Conductor Size Related To Current

03/13/2011 5:56 AM

For any conductor to carry a current the dearating factor is considered. But the doubt is that for a bare aluminium flat, factor usually considered for capacity is 0.8 to 1 ampere per square metre. But we found the same ampere / sqm is high in case of XLPE cables.

For eg: 10 ( breadth) x 12 (thickness) alumium flat carries a maximum current of (10x12=120 sqmm; 120x0.8 = 96 approx 100amps)

But for the same 120sqmm Al.Ar.XLPE cable can carry about 180 to 200amperes when laid on open atmosphere.

Where can we trace this difference?

Register to Reply
Pathfinder Tags: conductor size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: CONDUCTOR SIZE RELATED TO CURRENT

03/13/2011 7:14 AM
__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Conductor Size Related To Current

03/13/2011 2:56 PM

Chandru

Let me know what you find here. I want to know the answer.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Conductor Size Related To Current

03/14/2011 6:40 AM

Are you aware of Skin Effect & Proximity Effect?

Register to Reply
Active Contributor

Join Date: Mar 2011
Location: INDIA
Posts: 10
#6
In reply to #3

Re: Conductor Size Related To Current

03/15/2011 12:51 PM

yes sir

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#4

Re: Conductor Size Related To Current

03/14/2011 9:00 AM

An important limitation for bus bars is the thermal limit. The allowable current/cross sectional area is based on the electrical power dissipated and the convection cooling of the bus. At low frequency, the cross sectional area of the bus will allow you to calculate the power dissipated, but the exposed area of the bus is part of the cooling calculation. This means, a large piece of sheet metal will dissipate more heat than a round or square cross section of the same material. There is more to it, but that's the fundamental reason. Obviously, anything that inhibits cooling (like insulation) changes the equation.

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#5

Re: Conductor Size Related To Current

03/15/2011 9:18 AM

But the doubt is that for a bare aluminium flat, factor usually considered for capacity is 0.8 to 1 ampere per square metre.

In the above statement the words "square meter" should be read as "square mm".Coming to the answer to your question,it is the skin effect .it may be noted that current flows in the periphery of the cross section of the conductor ie.the surface .Hence major part of the cross section of the Al. flat remains unused,where as in case of cable which comprises of a number of strands of smaller diameter,optimum utilisation of the cross section is achieved,thereby resulting in higher current flow in cables of equivalent cross section.

__________________
Learning is a never-ending process.
Register to Reply
Active Contributor

Join Date: Mar 2011
Location: INDIA
Posts: 10
#7
In reply to #5

Re: Conductor Size Related To Current

03/15/2011 12:53 PM

thanx sir, i can understand. Can i get a table relating ampere rating and cable size (al / cu)

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#8
In reply to #7

Re: Conductor Size Related To Current

03/16/2011 2:26 AM

You can see the links given by TonyS & Wareagle in response to your question.

__________________
Learning is a never-ending process.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

chandru1982b4u (2); electricalexpert65 (1); spradhan (2); TonyS (1); wareagle (1); welderman (1)

Previous in Forum: Neutral   Next in Forum: kW Consumption Calculations

Advertisement