Pump, AC, Refrigerator Motor Burn

03/13/2011 11:17 PM

Hi,

We've utility here bad, voltage sometime drop from normal 380VAC/50hz to 300VAC/50Hz. So I bought stabilizer 20 amps (servo type) to stabilize my equipments. Pump, refrigerator, AC work at 380VAC/50HZ total load only 3.5 kW but 2 times get burn at all motor. What's the problem ?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: Pump, AC, refri motor burn

03/14/2011 1:14 AM

Do you have surge protectors?.

__________________
pnaban
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#2
In reply to #1

Re: Pump, AC, refri motor burn

03/14/2011 2:41 AM

Pnaban, no I have not. I ever thought but for home application I just ignored it. So, what could be the cause of frequent damaged my equipment ?

Thanks

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Pump, AC, refri motor burn

03/14/2011 11:55 AM

Please give ratings(I/W) of pump,refrigerator and AC to check whether the total is 3.5kW. If load is high there will be VD and if no OL protection is provided items will burn

__________________
pnaban
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#5
In reply to #4

Re: Pump, AC, refri motor burn

03/14/2011 12:32 PM

2xAC @1650 W + Waterpump 175 w = 3,475 W, Sorry,I'm out of my house for a month- i can't give you spec of each equipment eg. I/HP/range volt etc. Could you please also recommend me what kind of surge surpressor to protect these ?

Thanks

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Pump, AC, refri motor burn

03/15/2011 12:55 AM

You didn't mention the rating of refrigerator,voltage and capacity(amp/kVA) of power contract with the utility. The contracted supply should be at least 30A. Check with them whether your load is acceptable to them to be supplied with their existing capacity of feeder We do not know the VD in the distribution lines. If it is too low stabiliser may not help. Regarding SPD you should use one recommended for use at the incoming supply main breaker.

__________________
pnaban
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Pump, AC, Refrigerator Motor Burn

03/14/2011 11:03 AM

"So I bought stabilizer 20 amps (servo type) to stabilize my equipments."

Not sure what that device might be. A servo controlled variac perhaps?

A lot of devices that people call "stabilizers" are a scam. All they do is REDUCE the voltage on all 3 phases to the LOWEST level of the 3. The only way to boost voltage, permanently like this, is either with a tap changing transformer or a variable transformer (variac), of which maybe there are servo controlled versions. But neither of those is going to protect you from voltage spikes, they react way too slowly. If you have a line voltage that drops over 20% like that, chances are you have other very serious supply problems and a very good surge suppressor would be a wise investment.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Member

Join Date: Mar 2011
Posts: 8
#6
In reply to #3

Re: Pump, AC, Refrigerator Motor Burn

03/14/2011 12:42 PM

Can I make temperory conclusion that these equipment burned because these working undervoltage due to stabilizer (motorize type) had slow respond to recovery the voltage ?

I've read some thread in this forum regarding motor heat, motor protection..helps me better understanding about motor.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#8
In reply to #6

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 2:07 AM

Your conclusion is correct. Replace the stabilizer with quality one and observe .

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#9

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 7:18 AM

Please confirm if you had installed MCB in circuit?. What protection you have provided for overload, Short Circuit?.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#10
In reply to #9

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 9:22 AM

Yes, Only main CB for short-circuit, sorry-I didn't remember the rate amps of MCB. No special protection such as surge protector, termal overload relay, overcurrent (ref to thread in this forum)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #10

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 9:52 AM

<...No......protection.....overcurrent.....>

That would be why the motors burn out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 9:37 AM

You need a UPS.

Register to Reply
Commentator

Join Date: Jan 2011
Posts: 61
#13

Re: Pump, AC, Refrigerator Motor Burn

03/15/2011 1:25 PM

The normal load might be 3.5 kW, but the starting current for each motor is several times that of normal load. If the supply V drops on starting, the stabilizer may saturate and the motors stall and burn out. UPS is normally used for electronic and control equipment. Check with your utility if they can supply 6 x rated current at 380V -10% for starting only, for each motor. Don't forget other loads, such as hot water (switch off when not home) or cooking.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#14

Re: Pump, AC, Refrigerator Motor Burn

03/18/2011 5:24 AM

Please check all the calbes whether they are hot or not. Then check the specification of electric wire installed in your facility. Then, check any connection for any loosen wire since these would contribute to the problem.

Check the frequency of voltage drop then you will switch off some loads to be operated at predetermined time avoiding the worst voltage drop. If the voltage drops too much so the pump is impossible to start, then it overloads and burns.

After you ensure things are in good condition. Then, 20amp stabilizer seems not enough for those load because you may certainly have lighting, and other loads. You should increase it to 40amp.

If the voltage drop is permanent. Then, the UPS or stabilizer are recommended. If the voltage frequently is fluctuated. This will also reduce the life of these equipments.

I have once faced this problem when installing the temporary power system for the contruction site. (Cable cross section was not enough, connection was loosen, terminal burned, wiring distance was too far... that caused the voltage drop). The worst case is we have the total black-out over the site. (AC burned, motor burned, photocopier burned, lamps burned).

__________________
Anything that can go wrong, will go wrong
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Dave Simpson (1); Fredski (1); hien.nguyenquoc (1); JRaef (1); mrswamy (1); Pandu78 (4); pnaban (3); PWSlack (1); suresh sharma (1)

Previous in Forum: Converting Three Phase Motor to a Generator   Next in Forum: VVVF Voltage Output

Advertisement