Asynchronous Machine Efficiency

03/14/2011 11:33 AM

whether the efficiency of an asynchronous machine are the same in motor mode and generator mode??

because ussually in name plate only written the machine efficiency as motor.

this is for non high efficiency or high power rating.

*sorry for the mistake of words usage and thanks for the answer...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Asynchronous Machine Efficiency

03/15/2011 9:45 AM

Efficiency values are basically the same in either direction.

But realize that the value on the nameplate is only the efficiency at full load, which is easier to define when motoring. It goes down (as a percentage) as the load decreases because of fixed losses in the windings and magnetics. So for a motor, full load means the mechanical power expressed at the shaft as it tries to drive the load is equal to the rating of the motor. But what is the "load" on an induction generator? You must have a sufficient overhauling mechanical load from a prime mover on the shaft to spin it at super-synchronous speed. But to get full efficiency the "load" on it as a generator would have to come from the grid it is connected to. So that actually happens only when your prime mover attempts to drive it beyond the initial super synchronous speed at which it started generating, increasing up to the point where the negative torque expressed by the grid resisting it's influence gets to the kW rating of the machine.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2011
Posts: 3
#2

Re: Asynchronous Machine Efficiency

03/20/2011 10:01 AM

thanks for advance mate.....

Register to Reply
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: Power Saving Calculations Through Power Factor Improvement   Next in Forum: Batteries

Advertisement