Power Saving Calculations Through Power Factor Improvement

03/14/2011 8:38 AM

What is the actual power saving through power factor improvement at motors / LT panels / Generators. How one can calculate the reduction in electricity consumption after power factor improvement.

__________________
arjmand.nec@gmail.com
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Power Saving Calculations Through Power Factor Improvement

03/14/2011 8:54 AM

Hmmm... simple really.

kWh without PFC = kWh with PFC

Get it?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Power Saving Calculations Through Power Factor Improvement

03/14/2011 10:59 AM

PFC devices benefit the power producer more, hence the added fees for poor power factor by the end user. Your equipment uses the same power as before, but devices with windings tend to run warmer producing more heat as a "waste" product, but operating exactly as designed. Improved PF may benefit the user by extending the life of their equipment.

Register to Reply
Participant

Join Date: Mar 2011
Posts: 4
#4
In reply to #2

Re: Power Saving Calculations Through Power Factor Improvement

03/15/2011 6:44 AM

Thanks a lot. Can I calculate it through reduction is I2R Losses due to PFI.

__________________
arjmand.nec@gmail.com
Register to Reply
Anonymous Poster #1
#5
In reply to #4

Re: Power Saving Calculations Through Power Factor Improvement

03/15/2011 10:08 AM

You can but it is not as simple as that.

You see the reactive current (or power) is the demand of the load, and that has to be met (say a motor runs at 0.85pf then it will draw the reactive current corresponding to this, no matter what.

What you can do is to put the pf compensator (PFC) so that the reactive power is supplied by the compensator and not from the source (ie power supply utility).

The reactive current now loops between the load and the pfc and the corresponding I2R loss will take place here, in addition to a bit of loss in the capacitors that you have added.

The saving will be in the I2R loss between the PFC and the say supply transformer. However these usually will have cables with sufficiently low resistance and thus the saving may not be worth the effort.

Same happens to the generators- which try to compensate (or supply) the reactive power by controlling its field excitation, thus increasing its field coil losses along with the increased I2R loss in the armature.

Again the saving will not be significant unless the pf is really low.

This matter has been discussed several times in CR4 with the net result- not worth it unless

a) pf is too low

b) There is a penalty on low pf

c) The loads are distributed over sufficiently long distances (thus having significant line losses) and the pfc is put in the vicinity of the loads (or at least local nodes, as is done in our factory)

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #5

Re: Power Saving Calculations Through Power Factor Improvement

03/15/2011 11:00 AM

I never heard it explained quite like that...

Register to Reply
Participant

Join Date: Mar 2011
Posts: 4
#7
In reply to #5

Re: Power Saving Calculations Through Power Factor Improvement

03/16/2011 1:33 AM

Sir, Thanks a lot for you kind review of the Issue.

__________________
arjmand.nec@gmail.com
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Power Saving Calculations Through Power Factor Improvement

03/14/2011 11:26 AM

You will get a saving if you pay for power in KVA and not KW. A bigger saving if you are penalised for low PF.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#8

Re: Power Saving Calculations Through Power Factor Improvement

03/16/2011 10:08 AM

Capacitors added will only increase - not decrease - although, slightly, the power consumption.

Register to Reply