Anonymous Poster #1

Grounding Problem

03/16/2011 2:57 PM

I am facing problem with instruments like Pressure transmiter flow transmiters which are giving fluctuate reading in the PLC which located 15 meters away from field & perfect reading in the field monitors,even we checked the grounding cables are perfect,other than that what are the things to be checked?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Grounding Problem

03/16/2011 4:14 PM

What type of loop? 4-20Ma, 0-10V........ Do you own a loop calibrator? Are you talking to a PLC or a display of some sort? More info please.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Anonymous Poster #1
#6
In reply to #1

Re: Grounding Problem

03/18/2011 4:52 AM

We are having Rosemount Pressure Transmitter(Range -2 mBar to +2 mBar) in the field we are having the Transmitter & the transmitter have its own display which shows correct reading proportional to field pressure but we had taken 4-20 mA through signal cable to PLC around 70 meters from field initially its shields are grounded both side while we faced problem recently we removed the grounding at one end(near transmitter).even though we are having reading fluctuation in PLC.Please give your valuables suggestions

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #6

Re: Grounding Problem

03/18/2011 8:19 AM

You must ground once, it sounds as though you are not grounded at all. There must be a return path for the signal.

As I cannot "see" your cable arrangements, it would be dangerous to speculate further.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#2

Re: Grounding Problem

03/16/2011 4:17 PM

Are you using shielded cable? Every transducer I've ever used needed a shielded cable, otherwise you can pick up stray noise from other sources, which will cause erratic readings.

__________________
Don't believe everything you read on the Internet!
Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: Grounding Problem

03/16/2011 5:25 PM

If you are using a shielded cable are you grounding the shield at one end or both ends? Based on your description of the problem, it sounds like you are picking up line "noise".

__________________
The first 5 days after a weekend are always the hardest................................
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4
In reply to #3

Re: Grounding Problem

03/17/2011 7:57 AM

Only one cable should be grounded at both ends between units, all the others at the "more-nearer" ground end only!!!

Often safety ground and logic/signal ground need to be kept fully seperate......

As if more than one cable is grounded at both ends you make ground loops......

Its usually best to cut the ground NOT in the cable, but in the socket(s) in the end equipment, so that "normal" cables can all be connected and you only need one type of cable.....avoids mix ups with cable types.....

If I am not fully clear enough for you, please ask me further for more infos/diagrams.

Signals generally need to run along shielded cables for proper operation......do not change that.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Member

Join Date: Mar 2011
Posts: 6
#5

Re: Grounding Problem

03/17/2011 11:13 AM

Good call Andy, grounding both side of cable will case the problem. These are other problems that I have run into when I worked in the test industry. 1. If you build you own interfaces make sure you bring all you internal grounds to a single point in the box the box, then ground all your equipment to enclosure. 2. If you equipment is installed in an enclosure (Bud, Hoffman) make sure each piece of equipment has a good ground to the enclosure. 3. Run separate ground to both system chassis at least 4 awg. 4. Any coil switched devices (relays, solenoids) that are being drive by logic will cause large short burst spiking in the control lines these can be generated into the controls power supply. Make sure you have diode protection across the coil. 4. If you still have problems try installing a ground rod into ground next to high current equipment. 5. I had a problem at one facility where the power coming into the company was generation a 100khz signal on their lines. It's reaching, but also a possibility. Bottom line is noise is an ongoing battle.

Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#7

Re: Grounding Problem

03/18/2011 5:49 AM

Use calibator to input the signal and read the instrument output to see how to fluctuate.

__________________
Anything that can go wrong, will go wrong
Reply
2
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#9

Re: Grounding Problem

03/18/2011 12:47 PM

We use twisted pair double shielded cable. The shields are grounded at the instrument end only as you don't want the noise coming back to the analog inputs. In high noise areas we run the cables in metal conduit for added immunity. Do not run power and instrument cables in the same conduit and keep the instrument cables routed as far as possible from high noise generators like variable speed drives and switching power supplies. If there are power feeds in the same panel try to cross them at 90 degrees. It might also be a good idea to check your PLC power feed with a scope to check for Noise on the power the neutral (if it has one), and the ground wires. Your noise might be there.

Elroy

__________________
Knowledge makes what was impossible, seem easy.
Reply Good Answer (Score 2)
Reply to Forum Thread 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Anonymous Poster (1); Elroy (1); hien.nguyenquoc (1); James Williams (1); KJK/USA (1); RDGRNR (1); RVZ717 (1)

Previous in Forum: Injected Copper Rotor Bars   Next in Forum: How Does an ALU Work?

Advertisement