Measuring Ground Current

03/18/2011 11:02 PM

Hai,

I need your valuable answers.I am having 132KW AC drive in our plant operate the motors in the rotating kiln(75 meter cable laid in totally metal body wound with asbestos strip for insulation),it will set for tripping for ground fault current.is there is any instrument/measuring methods are there for measure this ground current which makes us to take precaution/finding the perfect grouding of cable.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#1

Re: Measuring Ground Current

03/19/2011 11:01 AM

Your question is hard (for me) to understand.

Is that motor / drive actually tripping due to ground fault and you're trying to find out why, or are you trying to determine the correct setting for the ground fault relay to protect the motor / drive?

Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 19
#3
In reply to #1

Re: Measuring Ground Current

03/31/2011 3:48 AM

Thank you for your response regarding my question,actually the drive is tripping due to ground fault but we need to indicate the actual ground current that makes us to become alert before tripping.

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4
In reply to #3

Re: Measuring Ground Current

03/31/2011 8:59 AM

See #2.

I'd probably like to have a strip chart recorder in the CT circuit to see what the current looks like before tripping.

But, you have a setting on the current ground fault trip device--obviously the ground fault current is exceeding that setting when it trips. I guess you want a warning before the trip--I'm not sure how much warning you can get, but try setting another ground fault relay, driving an alarm, at 1/2 the value of the trip...

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#2

Re: Measuring Ground Current

03/20/2011 2:50 AM

Yes, it is very easy to measure. A current transformer of expected maximum earth fault current and an ampmeter will do the job. The earth fault current is the ratio of the applied voltage over the total earth fault loop impedance. I = V/ R, were R is the resistance of earth fault loop.

__________________
There is peace in silence and achievement in plans.
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Dickson (1); rhkramer (2); rubeshkrishna (1)

Previous in Forum: Calibration Chart   Next in Forum: Area Classification
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement