Electrical Engineering

03/19/2011 3:06 AM

I have a machine which has got 2 power inputs, one is 220V AC in and the other other is 110V ac in. the first i.e. 220Vac is for running the machine with its drives and the other i.e. 110Vac is for running the computer and the coolant pump which has to be of the same input.

Can anybody please tell me if I use the 220Vac input in place of 110vac as I have the computer and the coolant pump of that 220vac inputs, then would there be any problem with the panel or shall it work fine? As the function of 110vac in is to run the computer and the coolant pump from the switch provided in the panel of the machine only.

Thank you in advance for the answers.

__________________
CNC Solution Provider
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Electrical Engineering

03/19/2011 8:52 AM

If you want straight answer yes it should work. But I will come up with a counter question,If you are replacing all 110Volts Items with 220 volts Items, then what could be the possible reason of not working?

Make sure that you have replaced all the items those were supplied by 110Volts,

Register to Reply
Active Contributor

Join Date: Sep 2010
Location: Hyderabad
Posts: 11
Good Answers: 1
#16
In reply to #1

Re: Electrical Engineering

03/23/2011 11:38 PM

If you replace with all 110Volts Items with 220 volts Items, it may not work(due to low potential) its purely depends on construction of particular items.

__________________
"Everything you can imagine is real." -- Pablo Picasso
Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: Electrical Engineering

03/19/2011 9:45 AM

You should first respect the idea that a competent engineer designed your machine. (Obviously this is not always true but one should start here.) The engineer designed this machine to work from two different power sources for a reason. Figure out this reason before you switch any power supplies or motors so that you could operate off of only one power source. Possibly the drives produce too much electric noise on the power line that the computer tends to lockup if they are connected to the same source. Maybe the drives tend to overdraw current during startup and thus have often tripped external circuit breakers. The added boot time or lack of history recording of the computer during these power losses was deemed a bad idea. You don't provide enough information to hazard a guess why the designer of this machine choose to use two power sources.

I admit that if it was obvious why two power sources were needed you probably wouldn't be asking us for help. But to modify anybodies design in a responsible fashion you should first try to figure out why they did it that way in the first place.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Electrical Engineering

03/19/2011 10:07 AM

GA redfred

Listen to the voice of reason, uniq_engineers. When i was young, i also made this mistake of thinking that i am smarter than the original designer. Only once, and fortunately, caught myself at the drawing board stage

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Oct 2009
Location: Istanbul. European side
Posts: 151
Good Answers: 4
#7
In reply to #3

Re: Electrical Engineering

03/20/2011 6:26 AM

This is the smarter reply I ever heard in the forum. "When i was young, i also made this mistake of thinking that i am smarter than the original designer.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: Electrical Engineering

03/20/2011 6:28 AM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Electrical Engineering

03/19/2011 2:56 PM

I am going to have to go against the competent engineer design concept and toss in incompetent bean counters who override good engineering designs to save a few pennies on multi thousand dollar devices.

Too often the multi volt inputs simply came down to the device having multiple sub components designed by independent contractors and not one individual company department.

Some where along the way sub contractor A decided to add the capability for dual voltage to their component but the final stage assemblers at stage Z where told to still use the lower voltage setup since thats what the original design had and that doing a input voltage change on the redesigned sub component would take a bout 20 seconds more and thats too much cost over run for a some bean counter to accept for his theoretical time Vs production graph and charts.

That doesn't mean that I think I know more than engineers, I might know more than some, but certainly I know far more about proper engineering than any typical bean counter does!

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#5
In reply to #4

Re: Electrical Engineering

03/19/2011 11:51 PM

I'm with you...

It is generally frowned upon to have more than one power source

it is needlessly complicated & not as safe!

If the PLC blips from sharing power with the drives, it's a bad design

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Electrical Engineering

03/20/2011 3:47 AM

Dear Uniq Engineers,

You should not use 220 Volt Supply in a 110 Volts system, since the components will get damaged. Either way you should not use undervoltage also.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: May 2009
Location: West Eaton , New York
Posts: 17
Good Answers: 1
#9

Re: Electrical Engineering

03/20/2011 10:21 AM

Hello all ,

I have been in manufacturing for many years and have run across this very same scenario many times. We have several European and Japanese injection presses that require dual voltage power sources. Case in point , just last week we purchased a JSW 120ELII all electric press. The specs that were faxed to me from the plant we purchased it from only stated that the requirements of the machine were 200V @ 30Kw. So automatically assumed it was a EU power requuirement of 50 Hz , when all I have at my plant is either 480V 3phase or 240V 3 phase. The press did come with the appropriate transformer though.

As it ended up after the press arrived and I removed the covers and READ the prints and manual, that the press required two power sources , (1) @ 480V 3ph no neutral , and also a 208V 3ph with neutral .

Therefore after carefully inspecting machine and prints it was clear why this was done.

The heater bands for the press and a few aux. equipment recepticles mounted on the cover panels require the 480 @ 50A aprox. .

The 208v @ 28.1 KW aprox for the servo motors and computers.

So by bringing only one 480 Vac 125 A service to the tranformer input ( the H ) side of coils. I was able to put double lead lugs ont the input and single on the output 208, I achieved all the requirements of the original design.

If you look into the equipment I believe you will find that there are several smaller transformers in there for specific purposes that each require a different input voltage dependent upon there usage and output designs.

I hope this helps JCD

Register to Reply
Power-User

Join Date: Oct 2009
Location: Hydro, Oklahoma
Posts: 184
Good Answers: 2
#10

Re: Electrical Engineering

03/20/2011 10:28 AM

Define the machine a bit better, seems the reason for the lower voltage feed for the computer and the cooling source may be for a safe guard if the heavy load fed by the higher voltage failed for some reason. The computer's timers and sensors could remain running until the unit was safe and removed from service. You really answered your own question. My suggestion is to read the material supplied by the engieer and find the reason for the two sources of power. "know" and leave "think" aside. The ole adage it's better to be safe than sorry. You could burn a building or ruin a valuable machine..

__________________
Jim
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#11

Re: Electrical Engineering

03/20/2011 6:49 PM

When you have a machine with the manufacturer's data,first respect and operate the machine with the data specifications.

If on the other hand you don't have 110v ac supply and you cant lay hands on the sizable step-down transformer,if you have to use 220v ac supply,then make sure the panel components for the 110v ac supply conforms with the 220v ac you tend to replace,since you have the computer and coolant pump of 220v ac inputs.

You should try to find out first why the manufacturer has adopted the 110v ac input,why not 220v input.Read the manual and check the panel component ratings if they conform with 220v ac,else change the components to conform with 220v ac input.

__________________
Patrick Whowha
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#12

Re: Electrical Engineering

03/20/2011 7:13 PM

In some cases,you find out that the higher the voltage,the higher the speed or performance of the machine,and the lower the current consumption.

It could be that the purpose of the 110v ac input to the coolant pump is to enable the pump performance or speed in such a way as to meet up with proper cooling of the machine,but if 220v ac is applied to a 220v ac coolant pump,it may not cool the machine properly as designed.

__________________
Patrick Whowha
Register to Reply
Member

Join Date: Jul 2010
Posts: 7
#15
In reply to #12

Re: Electrical Engineering

03/23/2011 10:56 PM

Generally speaking, 1 and 3 phase asynchronous and synchronous AC motors' speed is not dependent to voltage. Only the supply frequency and the pole count determines the speed. Therefore "the higher the voltage the higher the speed" rule does not apply to AC motors. It can be applied somehow to DC motors.

Regards

Steve_y

Register to Reply
Active Contributor

Join Date: Sep 2010
Location: Hyderabad
Posts: 11
Good Answers: 1
#13

Re: Electrical Engineering

03/20/2011 10:48 PM

No problem you can go head

__________________
"Everything you can imagine is real." -- Pablo Picasso
Register to Reply
Member

Join Date: Feb 2011
Location: India
Posts: 9
#14

Re: Electrical Engineering

03/21/2011 1:47 AM

Dear All,

First of all I am really thankful to you guys for giving me so much detailed explanation on how the stuff works with the electrics and I didn't knew this as I am a mechanical guy and am learning with the electronics.

Also I respect the designers off-course who have designed this machine as this is really a great concept and achievement in its class for all those looking for small size VMCs. You guys can check out my website www.uniqengineers.com for more details of the TORMACH PCNC1100.

The question of mine was related to this machine only. They have provided two different power supplies, one for running the machine and the other for running its accessories. I really appreciate that stuff now after I have conducted the trial of using both the power supply after reading the electrics of the machine. I used both the inputs of 220V only and it really worked very well without any problem. Then I came to a conclusion of the design that they have done. The secondary power supply that was to be 110V is used just for the auto use of the computer and the coolant pump as they have given the power switch to operate both of this from the machines panel. I mean to tell that if we give the input of 110v then it will send forward the same i.e. 110v and if I use 220v then it will send 220v. Just you need to take care of the accessories that you are attaching are of the respected power supply that are inputted. I hope that you can understand what I am trying to explain.

Once again thank you for your answers and also hope that my lesson can help you guys also in future.

__________________
CNC Solution Provider
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Ayyavaru (2); dhayanandhan (1); Garthh (1); JCDeGoski (1); jtd405 (1); kvsridhar (2); nezihozfirat (1); Patrick Whowha (2); rakesh_semwal (1); redfred (1); steve__y (1); tcmtech (1); uniq_engineers (1)