Service Breaker Question

03/23/2011 12:31 PM

Question for all my experts on CR4:

I was born and raised in the USA and every year I come to Peru to visit my in-laws and during this visit I have change the service breaker because they use an individual thermal heater to heat the water in the shower. When more than one person take a shower in the day for a long period of time the termal heater overheats and the service breaker blows. Maybe it is a mix of several things at once but the major culprit is this thermal heater.

The heater is a 230VAC, 15A single phase connected to the house wiring through a single pole 20A breaker and the breaker is wired to the light switch in the same room. All of this was connected by a local electrician. I have seen my things I think is not right and feel a need to correct but need expert CR4 opinion.

First, the wiring used is 7strand 16 gauge utility wire and should be 12 gauge single strand thermal coated. Second, I think there is too many 20A breakers in line(total of two, local and in the in-house service box). Three, it should be isolate on its on breaker directly to the the service box by eliminating one of the 20A breakers but the lights are also connected to the same breaker so I can´t eliminate the 20A in the in-house service box.

My Question is how would I run this line to the breaker box as an isolated plug with a shut off switch being placed in the bathroom? What wiring guage and is the double 20A breakers in-line a problem with burning up the main breaker to the apartment?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Service Breaker Question

03/23/2011 2:22 PM

There are probably local codes that you must follow and only someone familiar with those in Peru can address that. but from an engineering standpoint, 16ga wire is not in and of itself inadequate for a 15A load, but the total length of the circuit may be problematic. For sure increasing the wire gauge will help avoid voltage drop as a result of the heater draw, which may be that extra culprit. The heater causes a voltage drop, which all by itself doesn't harm the heater (just makes it take longer to heat the water), but when someone turns on something else on that circuit, especially anything with a motor, you get a current surge that blows the main breaker.

Also, that 16ga wire is too small to be protected by a 20A circuit breaker, at least it is here in the US. That right there would be a reason alone to upgrade to 12ga wire.

As to breakers in series, not a problem, except that each switching device in a series adds it's own small amount of resistance and thereby voltage drop, so too many can end up as a problem, but 2 in series in and of itself is not going to matter much. But it is a pain in the rear to troubleshoot because you don't know which one is going to trip. The installing electrician may have done it so that if the one closer to the shower trips, it keeps the person from having to go to the main breaker panel, but that's a fallacy. Just because it's closer doesn't mean it will trip first. if I had to guess, I'd say it was more likely that the original guy put in a 15A local breaker off of the 20A branch, then someone changed it to 20A because it was tripping too much. Bad idea, but that sort of thing happens all the time.

You are right to question it and if you can, fix it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#2

Re: Service Breaker Question

03/23/2011 7:22 PM

I can't tell you what to do and I don't want you to do it wrong, but it sounds to me like you are feeding the water heater with 120VAC.

If the breaker is 230VAC and it's going to a light switch, it would blow out the light bulbs.

The 230VAC water heater needs it's own dedicated circuit.

I'm not an electrician, so maybe somebody else can tell you exactly how to test and wire it properly.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3

Re: Service Breaker Question

03/23/2011 10:57 PM

tiger; I believe that Chile has adopted the U.S.A. national electrical code, NEC for wiring in the future, or now! American Wire Gage, AWG #12 wire can be solid, or stranded with THW, or THWN THHN nylon covering is normally rated 20 amps. If main service breaker is 20 amp @ 230 volt you have 4600 watts for use, the water heater rated @ 15 amps would be 3450 watts, leaving 1150 watts for general use, for lighting or ?? the water heater would not be any different in the morning or afternoon, same power used, the second breaker could be the disconnect in sight of the water heater. what brand of circuit breaker are used. perry

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#4

Re: Service Breaker Question

03/23/2011 11:04 PM

Do you know if the thermal heater did work acceptably ever? Or , has this problem been a recent development? I would first measure with amp meter how much current the heater is drawing during the period just before the service breaker blows. You said that the heater is rated at 15 amps. If it is drawing 15 amps or more, the thermal heater is probably bad, old and using more amps or perhaps some one repaired it and used a wrong element that may be for a larger heater. Also measure the voltage at the heater to ground to make sure it has the proper 230v. Low voltage will cause more current.

So if the amps and volts being measured at the heater are less than 14-15 amps and near 230v, then the wiring is the cause of the premature service breaker. I would also suggest that visual inspection of that small wire may have indications of heat from the excess current drawn.

Another thing about water heaters is that they tend to collect silt from the water in the bottom, even in city supplied water systems. Common practice here is to flush out the tank yearly. Removing built up silt will make the water heater work better (more hot water and reheat faster). It may also be the reason the heater has to work harder, drawing more current to heat the same amount of water. Trying running a large glass of cold, let it settle a minute and look at the clarity, then run the same glass full of the heated water, let it settle and see if the heated water is dirty compared to the cold, if so, the tank needs flushed.

__________________
For every action, there is an equal and opposite criticism.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#5

Re: Service Breaker Question

03/23/2011 11:27 PM

Uh, how many elements does the heater have? What's the rating on the heater label? Is there a toaster, oven, coffeepot, etc being used by the first person to shower while the second is using it? Is the heating element shorting to ground after a long expansion?

__________________
Align culture with nature...
Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#6

Re: Service Breaker Question

03/24/2011 4:29 AM

As someone else has pointed out, there must be a local electrical wiring code to follow. Common sense (and the UK code) suggest that a unit drawing 15A should be served by its own breaker. A 20A breaker is almost certainly too large for your lighting circuits.
The ultimate answer, therefore, is that there should be two separate breakers at the main board. If you really cannot run a second cable to the water heater, then I suggest you replace the breaker nearer the heater with a junction box (there is no point in having 2 breakers of the same rating in series). The junction is fed by the supply from the first breaker. From the junction box one feed goes directly to the heater, and another feed goes to a new lower-rated breaker which serves the lighting circuits.

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#7
In reply to #6

Re: Service Breaker Question

03/24/2011 7:53 AM

That scenario does not increase supply current to the water heater.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#9
In reply to #7

Re: Service Breaker Question

03/24/2011 2:35 PM

If you look at the OP's scenario, an under-supply of current was not an issue. The heater was over-heating. My concern was to avoid the lights going out every time the heater misbehaved. I had already pointed out that running a cable for the heater alone (which would avoid overloading the cable) was an even better solution.

Register to Reply
Member

Join Date: Oct 2009
Posts: 5
#14
In reply to #6

Re: Service Breaker Question

03/28/2011 3:51 PM

PHPH001,

Unlike europe, here in Peru is 220VAC at the source. Everything in domestic electronics, large or small, is 220VAC whether it be the lights or the washer and dryer. Here you have to look at the amp load and the watts. The pole source is 380VAC coming to the house and 220VAC sourced by two wires throughout the entire house. The only ground here is at the pole itself. We are taking built in the early fiftyish so as far as codes for this place its better for the poor people to pay under the table than to have the government to throw them in the street.

I am helping freely to correct this problem without having to out weigh the source of income availiable to pay for the entire house to be rewired. I personally know this situation is entirely miswired but like I said the money is not there. I appreciate all of the comments and opinions and will read them very carefully and use what sounds correct to me. Yes, I am following the local electric codes, what few exist for the area in which the house is located. And, by the way, its not a tank its a heating element encased in a plastic mold of a shower head and the water runs directly over the element to heat the water.

Thanks to all for your opinions, Louis(oceantiger)

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#8

Re: Service Breaker Question

03/24/2011 9:24 AM

I have travelled to a number of different countries, so here is my suggestion:

1.- First check the local codes to make sure that you will not be in violation of any.

2.- Change out the cable not to 12 ga. but rather to 10 ga. The reason is that in Peru like many Latin Countries the line voltages tend to fluctuate quite a bit both above and below the preset voltages. So this way you will avoid overheating of the cables due to the line variations.

3.- The change of the cable size will also help if the installation is in a hot tropical area.

4.- Try to have only one breaker between the main switch box and the heater, and this one try to get a GFCI type unit, that can trip on short circuits due to overheating of the cable, ground faults, etc. Helps protect the person taking a shower.

Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2009
Posts: 5
#13
In reply to #8

Re: Service Breaker Question

03/28/2011 3:24 PM

Thanks for the understanding of this problem and you are correct when you say the electric here is nothing like any where else. The lights here run on 220vac just like everything else and the building I am living in is older than most apartments in New Orleans. I was born and raised in Biloxi, MS and have visited just about all Latino countries and the older cities have the same configuration but the heater is a single heating element encased in plastic mold that the water runs over the element and through the shower head, it is not a tank at all. I will try what you are telling me and see if it works.

Sorry it took so long to reply but if you have been to any Latino country you would know the satellite system for phone, internet and tv are run together and its hard to get somewhere to get an internet signal.

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#10

Re: Service Breaker Question

03/24/2011 4:38 PM

In the process of heating the water, if the water temperature is high enough, on the heating element are forming calcium deposits that greatly decrease the heat transfer, causing the element to overheat. Same as the electric kettle or the steam iron. The quantity of deposits depends on the water hardness, temperature, the time in use, etc. In the kettle you can clean it by boiling vinegar solution. If possible, try to inspect the heating element and if is covered with calcium, clean it up with sandpaper, but be gentle.

Register to Reply
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#11

Re: Service Breaker Question

03/24/2011 7:35 PM

Does this picture appear like the one you are having trouble with?

__________________
For every action, there is an equal and opposite criticism.
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#12

Re: Service Breaker Question

03/25/2011 11:22 AM

If the breakers are ELCB ( earth leakage core ballance ) type putting two in series is known to cause nuisance tripping.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2009
Posts: 5
#15

Re: Service Breaker Question

03/28/2011 4:02 PM

For Merph

Yes, sorry, always read them first time asking for help. All the years reading this forum I have never posted a question because someone usually posted an excellent answer or a perfect question. But thanks for letting know and it wont happen in the future..

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#16

Re: Service Breaker Question

03/28/2011 7:06 PM

After re reading, I wonder if in Peru 230VAC single pole is standard for a 20 amp circuit. That's what I wish it were here. In that case a lightbulb or fixture, even incandescent, would pull less than 1 amp, and adding the fifteen amp water heater for 16 total would still not be very problematic on one circuit. If you have voltage spikes and poor power quality, it could cause tripping, but there is nothing too dangerous in this scenario. I would correct wire to 12Gauge, even 10 would be worth it, if you are pulling new. My guess is you have a breaker trip when you have amperage spikes up with voltage spikes down., not because the unit is overheating. I agree with the other posters, increase wire size. The resistance element in that shower head is not in danger of damage, it's pretty robust. I would use a GFCI breaker if you can find one, if you decide to replace it.

Your last question does not make sense to me. The breakers won't care what is happening to your main, which is I'm guessing is a 100 amp, or maybe a 50.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Beenaround (2); jerybaciu (1); JIMRAT (1); JRaef (1); kramarat (1); OceanTiger (3); ormondotvos (1); perry (1); PFR (2); phph001 (2); vargaalex (1)

Previous in Forum: Yokogawa Exaquantum Server   Next in Forum: Current Transformers Tests - Frequency 60 or 50 Hz?

Advertisement