Current Transformers Tests - Frequency 60 or 50 Hz?

03/23/2011 1:06 PM

Dear Sir,

My question below refers to the routine tests to be performed on current transformer [ characteristics : rated voltage 245 kV; frequency : 50 (fifty ) Hz ; rated current : 2.000 A] :


Suppose in the following situation : the current transformer with the characteristics above will be tested at a high voltage electrical laboratory which is configurated to perform test only in the frequency of 60 [ sixty ] hertz [ not in 50 Hz ].

In this case, what are the conditions, modifications , correction factors that I must consider for performing the routine tests below [ according to the IEC 60044 and/or IEEE C57.13 standard ] ? :

a) Power frequency withstand test ;

b) Parthial discharge;

c) Capacitance and dissipation factor;

d) Inter turn overvoltage test;

e) Accuracy test;

f) Excitation curve.


Note : The laboratory has only equipments and instruments for the frequency of 60 Hz, but the current transformer to be tested has 50 Hz frequency.

Thank you in advance

Cláudio Morais

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Mar 2011
Posts: 2
#1

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/23/2011 11:21 PM

If the test frequency is at power frequency, accordingly the voltage will change by a facor.50/60=0.83,may be lower to 0.83 test voltage comparing standard.If the frequecy is so high, no need to think about it.I'm not a expert of test.Just give some oppinion.Hope this could help and would be right.

Register to Reply
Member

Join Date: Mar 2011
Posts: 7
#5
In reply to #1

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/29/2011 12:35 PM

Dear Sir,

Thank you for your prompt reply.

Have a good week.

Cláudio Morais

Brazil

Register to Reply Off Topic (Score 5)
Active Contributor
India - Member - New Member

Join Date: Feb 2011
Posts: 14
#2

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/24/2011 1:20 AM

the capacitance as we know depends on frequency. and the dissipation factor or tan delta as popularly known also depends on frequency bearing the formula

dissipation factor = i/(wRC) where w = 2*pi*f where pi = 22/7 and f = frequency.

as can be inferred,

higher the frequency, lower the dissipation factor. the corresponding multiplication factor can be got by redistributing the terms on either side.

coming to the fact of excitation curve, it is a plot of the magnetising current and the voltage which is determined to find the knee point voltage or the voltage at which the core saturates. the magnetising current depends on frequency (may be proportional to the square of it). check out with an expert before coming to any conclusion. sometimes a higher frequency can cause overfluxing in the core.

Register to Reply
Member

Join Date: Mar 2011
Posts: 7
#6
In reply to #2

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/29/2011 12:37 PM

Dear Sis,

Thank you for your answer.

Have a good week.

Cláudio Morais from Brazil

Register to Reply Off Topic (Score 5)
Participant

Join Date: Nov 2009
Posts: 3
#3

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/24/2011 4:00 AM

To perform routine test on the 245 kV C.T., all test (except accuracy test) could be made at 60 Hz, without voltage correction. (For dielectric test in a C.T. there is not correction between 50 Hz and 60 Hz).

For accuracy test, the burden of the CT has to be increased in the proportion 60/50 (1.2), because, at 60 Hz, the section of the core for a given load is 1.2 times lower than at 50 Hz.

And to obtain the excitation curve, if you have the dimensions of the core, and the number of wires, you can obtain the relation B=f(H) without problem at 50Hz or 60 Hz. With the primary open, you only need to feed the secondary core and measure the voltage and current, and apply the approximate formula:

E = 2 * (f/50) * Ns * Bpeak * Sb *10^-6

where E: volts (rms)

f: frequency

Ns: secondary wires

Sb Section of the core [cm2]

Bpeak: induction [Gauss]

Ho*Lm = Ns*Io

where Ho: magnetic field strength [A/m]

Lm: midline of the core [cm]

Io: excitation Current [A]

Best Regards

Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2011
Posts: 7
#7
In reply to #3

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/29/2011 12:38 PM

Dear Sir,

Thank you for your prompt reply.

Have a good week

Best Regards

Cláudio Morais

Brazil

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#4

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/24/2011 9:58 AM

None of the standards provide formulas relating to changes of test values if the equipment is to be tested at a different frequency than the nameplate frequency.

You only alternative is to discuss the situation the situation with your client and come to an understanding. Generally speaking:

a. The power frequency withstand test should and would likely remain the same - at 50 or 60 Hz.

b. The same basically applies to the PD or FRI test - same test voltage for 50 or 60 Hz.

c. The same applies to the C&DF test, . . . same test voltage and the same expected DF/PF values regardless of test frequency - 50 - 60 Hz. NOTE the DF values of typical of GOOD oil-paper insulation remains basically the same at 25 / 50 / 100 Hz. NO, it can not be considered as a RC combination with obvious frequency corrections.

d. The induced test (inter turn test) can be carried out at a range of frequencies, . . typically second harmonic, third harmonic or 400 Hz. It is the TEST VOLTAGE that is critical and needs to be determined.

e. The accuracy test needs to be carried out at the specified frequency and specified burden. This does not require large amounts of power and could be powered from an electronic source. As an alternative, the client may accept a test using a >CT Tester<.

f. The excitation test needs to be carried out at the specified frequency. This test also does not require much power to conduct. Alternatively the test results from a >Relaying CT Tester< may be acceptable by the client. NOTE that the saturated voltage value from this test will determine the test voltage of the induced test.

Oleh

Register to Reply
Member

Join Date: Mar 2011
Posts: 7
#8
In reply to #4

Re: Current Transformers Tests - Frequency 60 or 50 Hz?

03/29/2011 12:40 PM

Dear Mr. Oleh,

Thank you for your prompt reply.

Have a good week.

Regards

Cláudio Morais

Brazil

Register to Reply Off Topic (Score 5)
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Cláudio Morais (4); cvsc (1); josmi38 (1); nanronan98 (1); olehwi (1)

Previous in Forum: Service Breaker Question   Next in Forum: Electrical Unbalanced Problem In Individual Equipments Terminal Box

Advertisement