N2 for Transformer

03/30/2011 7:41 AM

What is the specification of N2 to use it as gas space

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: N2 for Transformer

03/30/2011 8:38 AM

Nitrogen for oil-filled transformer blanketing should meet ASTM D-1933 Type III, with -59C dewpoint, as specified in IEEE C-57.12.00-1993, paragraph 6.6.3. See the following good reference regarding transformer maintenance:

http://www.usbr.gov/power/data/fist/fist3_30/fist3_30.pdf

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2011
Posts: 9
#2

Re: N2 for Transformer

04/02/2011 5:14 AM

Thanks for your reply.

ASTM D1933, Type III.

Type III

Nitrogen and rare gases, min,

volume %

99.993

Hydrogen, max, volume % 0.005

Oxygen, max, volume % 0.002

Dew point, max, °C −59

Register to Reply Off Topic (Score 5)