3 Phase Heating Element Problem.

03/30/2011 8:14 AM

Hi Guys I have a question. I have a three phase heater 380v. It has 3 elements making up the heater all rated at 380v. Originally the heater was connected in star configuration with P=6kw and In=9.11A. I have recently recieved new elements and the drawing that came with them shows the connection in a delta configuration still with P=6kw and In= 9.11A. The company that sent them say this is the correct configuration for these elements. My question is what is the different about the new elements?. Thicker wiring for the elements to make more resistance?. I thought if you changed from a star to a delta configuration then you would draw three times more power and the elements would melt.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: 3 Phase Heating Element Problem.

03/30/2011 8:41 AM

Power = √3*Vline*Iline, irrespective whether it is Υ or Δ.

In Υ, Vline = √3*Vphase and Iline = Iphase

In Δ, Vline = Vphase and Iline = √3*Iphase

So, go by what the manufacturer says, don't worry.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#2

Re: 3 Phase Heating Element Problem.

03/30/2011 4:56 PM

As for the power consumption there would be no difference and the manufacturer's statement is correct however the situation is not the same in case one of the heaters breaks down.

In case of star connection with neutral conductor failure of one heater element does not effects the performance of the rest of the two good elements but please be aware that in case of delta configuration break in any one heater may burn the rest of the good elements.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: 3 Phase Heating Element Problem.

03/30/2011 11:03 PM

...please be aware that in case of delta configuration break in any one heater may burn the rest of the good elements.

Can you please elaborate on how the two remaining resistors can burn ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Mar 2011
Posts: 5
#5
In reply to #3

Re: 3 Phase Heating Element Problem.

03/30/2011 11:32 PM

I was under the impression that if I connected the elements they sent me in a star configuration that the current drawn would then only be around 3A as opposed to the rated 9.11A they are rated at and that elements would give off less heat. If so what is the difference between the original elements I have which were connected in star and the new ones connected in delta if both of them are rated for 9.11A. Surely then the actually elements are constructed differently.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#6
In reply to #5

Re: 3 Phase Heating Element Problem.

03/31/2011 1:20 AM

Yes it sounds like they are made differently to the orginal elements.

On a system where line to line is 380 Volts, line to neutral will be 220 Volts.

Your new elements sound like they are 220 Volt elements - hence the recommendation to connect them Star - each connected from line to neutral.

If you can see the wire they should look thicker as they are intended for lower voltage.

The 9.11 Amp rating is the line current on any 3 phase leg - which will remain the same for the same power rated elements.

If you measured the current through each element it would be higher (than the old ones) as they are intended to be fed by a lower voltage in Star configuration.

Crazy stuff 3 phase huh?

__________________
johny451
Register to Reply
Member

Join Date: Mar 2011
Posts: 5
#9
In reply to #6

Re: 3 Phase Heating Element Problem.

03/31/2011 2:20 AM

Your new elements sound like they are 220 Volt elements - hence the recommendation to connect them Star - each connected from line to neutral.

The new elements are 380v and they have asked me to connect in Delta.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#18
In reply to #9

Re: 3 Phase Heating Element Problem.

03/31/2011 6:22 PM

You know I re-read your orginal post several times when I was posting that - and I still got it wrong. Just ignore me. Post #8 looks helpful.

__________________
johny451
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #9

Re: 3 Phase Heating Element Problem.

08/29/2024 3:56 AM

Go for it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #5

Re: 3 Phase Heating Element Problem.

03/31/2011 1:42 AM

This should make it clearer. Please ask if something is still not clear...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#10
In reply to #8

Re: 3 Phase Heating Element Problem.

03/31/2011 2:39 AM

Kvsridhar,

If the elements are rated at 380 volts and at this voltage are 6kW

So V/I = R 380/9.11 = 41.7 Ohms

P = I x I x R So 9.11 x 9.11 x 41.7 = 3460 Watts

This does not make any sense it is supposed to be 6000 Watts

Now if the elements are 380 volt rated and they are 6kW

P = V x I so P / V = I 6000 / 380 = 15.78 amps This I believe is the correct current.

And if R = V / I 380 / 15.78 = 24.1 Ohms this I believe is the correct resistance.

If this is the case, and I am sure it is, let us now have a look at your drawings.

In the Delta Con-fig P = V x I so 380 x 15.78 = 6kW

In the Star Con fig I = V / (Ra + Rb) 380 / 48.2 = 7.88 amps

So the power in the star con-fig is P = I x I x R 7.88 x 7.88 x 48.2 = 2992 Watts

So I think that your power calculation is incorrect

Sorry Mate, but you just cant get the same energy out of heating elements if you wire them is series, as I have shown.

To get full potential out of you heating you should follow the manufactures recommendation's and connect in delta if you line voltage is 380 volts

Cheers

Joe

Register to Reply Score 1 for Off Topic
4
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: 3 Phase Heating Element Problem.

03/31/2011 3:39 AM

Sorry Joe,

i am right.

Your assumption that the resistance = 380/9.11 is wrong. This is Delta connection, remember, so the current through the individual resistor is 9.11/√3=5.26A. So the resistance of each heater is 380/5.26 = 72.25 Ω. The LINE current is = (current through the resistor) X √3 = 9.11A, and the system power = √3*380*9.11 ≈ 6kW

Looking at it another way, each resistor, if connected to a single-phase 380V supply, will deliver (380/72.25)² X 72.25 ≈ 2kW. So three of them will deliver 3*2 = 6kW.

Best is for stoaty to check the resistor value. If each is 72 Ω, they should be connected in delta. If each is 24 Ω, they should be connected in star. QED.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 4)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#20
In reply to #11

Re: 3 Phase Heating Element Problem.

03/31/2011 11:54 PM

Ok, now to look again at the question,

"I have a three phase heater 380v. It has 3 elements making up the heater all rated at 380v. Originally the heater was connected in star configuration with P=6kw and In=9.11A

I was thinking that the elements were 6kW each, but I now am thinking that the elements are 2kW each making a total of 6kW.

I think that I have misinterpreted the question, "SORRY GUYS"

So if the elements were connected in delta format the line current would be 9.11 Amps but if the same elements were connected in Star each element would be working at a reduced voltage 220 Volts and have a reduced power output to about 3.5kW.

The next part of the question was;

" I have recently received new elements and the drawing that came with them shows the connection in a delta configuration still with P=6kw and In= 9.11A. The company that sent them say this is the correct configuration for these elements".

This is correct, obviously the elements that he had before were only rated for 220 Volts and that is why they were wired in the Star con-fig, the new elements are 380 Volt elements.

Conclusion; The line current would still be the same as the kW ratting is the same!

The new elements are rated at 380 Volts, the Old Elements are rated at 220 Volts, the new elements have a higher voltage ratting, do not try to mix the old and new elements together, or there will be problems.

"My question is what is the different about the new elements?. Thicker wiring for the elements to make more resistance?. I thought if you changed from a star to a delta configuration then you would draw three times more power and the elements would melt".

The new elements have a larger cross-section area and the resistance of the elements has changed.

Kvsridhar, "YES YOU ARE RIGHT" and you will get a GA from me, I hang my head in shame.

Best Regards, Kvsridhar

I Remain in Shame

Joe

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#21
In reply to #20

Re: 3 Phase Heating Element Problem.

04/01/2011 12:05 AM

Oh no, Joe, please do not embarrass me so much . Have i said anything that has offended you ? If so, sorry.

No need to feel ashamed. You should see some of the bloomers i have done, on CR4 too ! We have all misread some question and made mistakes, happens to the best of us.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#22
In reply to #21

Re: 3 Phase Heating Element Problem.

04/01/2011 12:25 AM

No offence was taken Kvsridhar, I made a mistake my friend.

The person that has not made a mistake has not done anything!

We all learn by our mistakes, that is what makes us better at what we do, we all hone and improve our skills every day, and what a place to think out problems (CR4)

We improve ourselves by helping others, lateral thinking, it keeps the mind tuned.

Any constructive criticism is positive.

Keep thinking mate

Cheers

Joe

All the best

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #2

Re: 3 Phase Heating Element Problem.

03/30/2011 11:24 PM

Why would the remaining elements burnout? Not because the voltage across each remaining element has changed, because it has not. Not because the current in each remaining element has changed, because it has not. The only effect will be a reduction in the power output of the heater. To think otherwise would mean that every system that serves single phase loads off of a three phase transformer has got it wrong. Of course if you are referring to a poorly regulated, weak or isolated system that serves only the heater then things might be different.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#7

Re: 3 Phase Heating Element Problem.

03/31/2011 1:33 AM

Stoaty, I won't answer the question, but I will advise you of a solution to get things going again. If you orignal elements were rated at 380 volts and the Line voltage is 380 volts, then you were operating the elements well below their current ratting. The elements would have been drawing far less than their optimun operating current.

Now if you want quicker heat recovery and the line voltage is 380 volts connect the elements in the delta config, and if you also want to monitor the condition of the elements to ensure that they are all operating ok, there is a simple way to do this, insert a thermal overload of the correct size to the contactor and use the N/O contacts of the overload to operate an indicator "Heating Element Fault", or you could use the N/C contacts to operate an indicator that the "Heating OK"

All of this is dependant on the Line voltage being 380 volts, but you indicator would probally have to be connected to a phase voltage circuit

Line Voltage is the voltage between any 2 Phases

Phase Voltage is the voltage between any Phase and Earth

Hope this is of help and you can sort out the answer to your question from here.

Cheers

Joe

Register to Reply
2
Participant

Join Date: Feb 2011
Posts: 4
Good Answers: 1
#12

Re: 3 Phase Heating Element Problem.

03/31/2011 10:34 AM

Dear Stoaty,

In both Star and Delta modes the total power is same (6KW). Hear specifications differ. In star mode each heater element is rated at 220V and has resistance of 24.15 ohms. In delta mode each heater element is rated at 380V and has 72.24 ohms. Therefore never connect heaters meant for star into delta. Heaters will melt. and never connect heaters of delta into star because that will not produce required heat. That is it produces only one third of what it is meant for.

A S Anand

Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: 3 Phase Heating Element Problem.

03/31/2011 11:22 AM

Thanks Anand. Glad to be vindicated

(i admit my faith was shaken for sometime there, after reading Joe's post)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Member

Join Date: Mar 2011
Posts: 5
#14
In reply to #12

Re: 3 Phase Heating Element Problem.

03/31/2011 11:27 AM

Thanks everyone for your help. I have one of the companys engineers coming out soon. So I will let him connect it up. Then he can melt this set of elements.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #14

Re: 3 Phase Heating Element Problem.

03/31/2011 11:40 AM

i would appreciate it if you could ask him about the resistance values... 72Ω or 24Ω.

To settle a bet

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Mar 2011
Posts: 5
#16
In reply to #15

Re: 3 Phase Heating Element Problem.

03/31/2011 11:44 AM

Sure no problem. This has been very interesting for me. Again thank you everyone that has posted.

Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#17
In reply to #15

Re: 3 Phase Heating Element Problem.

03/31/2011 4:15 PM

I don't believe doing a resistance test would show 72 ohms. I think it would be less. I believe the resistance will change with temperature. If the manufacturer says delta at 380 volts, thats the way to hook them up.

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#19
In reply to #17

Re: 3 Phase Heating Element Problem.

03/31/2011 8:11 PM

i expect the heater wire is Nichrome, whose temperature coefficient is 0.0004 per ºC. If it is operating at 400ºC for example, the cold resistance could be 16% less. Good point.

However, here we are looking at ballpark figures, 72 / 24 / 41 ...???

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#23

Re: 3 Phase Heating Element Problem.

04/01/2011 12:37 AM

This has been, (surprisingly to me), a good thread which made me redo my fundamentals. (Not to mention getting a couple deserved-or-not GAs )

Do you realise that the material content in the older, star-configured, heaters and that in the new delta-configured heaters are the same ? Check it out.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Participant

Join Date: Jan 2014
Posts: 1
#24

Re: 3 Phase Heating Element Problem.

01/20/2014 3:22 AM

If the heater is designed for delta connection then you can connect it in star connection, the only thing that happen is heating time will increased. Or if it is designed for star connection and you connect it in delta, your heater will meltout.

Register to Reply
Member

Join Date: Jun 2016
Posts: 8
#25

Re: 3 Phase Heating Element Problem.

06/05/2016 8:27 AM

Hey Guys i have somehow the similar problem, The factory has replaced 3 phase configuration with just single phase. can any body help me what is the disadvantage of this system? i mean the life time of elements and energy consumption.

Register to Reply
Register to Reply 26 comments