5 comments
Rate Comments: Nested
Participant

Join Date: Mar 2011
Posts: 2

Fuel Island Control Contactors

03/30/2011 3:56 PM

I have a fuel island that loses power and has to be manually reset each time the complex generator fires up weekly under load to ensure power works properly.

Am looking for ways to have this fuel island power automatically reset after generator usage.

The emergency shutoff at the island controls a relay, which then controls the contactor coils providing fuel island power. When power is lost, or when generator power comes on under load to test the power system, or also when the emergency shutoff at the fuel island is pressed, the relay will power down all power to the fuel island. Under all the above conditions, power can only be restored manually by depressing a button.

Is there a way I could set up this control so that when power is lost and then restored, this relay would restore power to itself which would in turn restore power back to the fuel island (all the while maintaining that if someone depressed the emergency stop button, power could only be restored by manual reset?)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Fuel Island Control Contactors

03/30/2011 4:14 PM

I believe that the system is designed to NOT be automatically reset especially when the e-stop has been pressed. Bypassing the hand reset could create a dangerous and/or deadly situation. Your insurance carrier would also have an issue with bypassing this safety feature.

As far as when the generator does its weekly exercise, you should be able to incorporate a UPS into the system behind the transfer switch on the branch leg that powers the fuel island.

I suspect you are getting the fuel island shut down during generator exercise because of a momentary loss of power when the transfer switch switches from normal to em power.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2011
Posts: 2
#2
In reply to #1

Re: Fuel Island Control Contactors

03/30/2011 4:33 PM

The fuel island was just rewired a few months ago, and never had this problem before the rewire.

The electrical outfit that installed the new system said it was possible to do what I had suggested above, but said since we never questioned at the time, they put in the manually reset contactors and relay.

So if there is a manual reset required only when e-stop is pushed, what can be done to maintain power during power glitches like the power lag waiting for a generator to start up or shut off?

Would some sort of a latching relay work in conjunction with the other relay?

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3
In reply to #2

Re: Fuel Island Control Contactors

03/30/2011 4:41 PM

Like I previously posted, install a UPS system behind the ATS on the leg that supplies power to the fuel island.

In my local, by passing a fuel island manual re-set is illegal.

Safest way to avoid gen start up/island shut down without altering the system control wiring is to install a UPS.

Good Luck

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#4

Re: Fuel Island Control Contactors

03/30/2011 7:48 PM

FYI - UPS = Uninterrupted Power Supply (basically an expensive AC battery bank) Available in many sizes/shapes/power ranges and available from many manufactures. This is the best solution to your problem, and deserves a GA.

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5
In reply to #4

Re: Fuel Island Control Contactors

03/31/2011 9:27 AM

Thanks RVZ!!

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bradleyquinton (1); KJK/USA (3); RVZ717 (1)