The last thread was getting pretty crowded so I'll start another, as I'm interested to know what you guys make of this.
This info and some photos of the setup can be found at http://urbangreenhouse.blogspot.com
I did two basic experiments.
1.
Filled the 20 litre drum (30 cm tall, deepest point 1.1 m, shallowest
80 cm, in dry sand over sandstone) with hot water. This was in the form
of 3 x 7 litres bought to boiling on the stove and poured into the tank
through the connector hose. Should've measured the water temp at start
and end of filling (took a minute or two to get it through the funnel)
but I'm going to assume it was about 90 C. The ground temp was around
24.5 C.
So:
First 7 L volume at 9.40 am, second at 9.57, third at 10.12. Measured
tank temp at 10.15 and was 77 C. This is a total of just on 5.75 mega
joules above the ground temp.
Full data:
time water temp (C)
10:15 77
10:30 74
10:50 70
11:05 67
11:20 65
11:30 64
11:45 63
12:00 60
12:15 59
12:35 57
12:45 56
13:00 56
13:40 53
14:00 52
14:30 50
15:00 48
15:35 46
16:35 43
17:00 43
17:45 41
18:45 39
20:00 38
21:00 36
23:20 34
00:15 33
08:20 29
11:25 28
13:15 28
14:00 28
16:00 27
17:15 27
18:30 27
23:35 26
08:45 25

And 2:
More relevant to the actual cooling system, I plugged the whole thing
together and ran it for about 8 hours. The setup was: air being sucked
from the top of the house through about 9 meters of 18mm garden hose
into the air pump housing, which was a vacuum cleaner pump and motor
inside a tupperware container with the attached electronics.
This meant the air was passed over the motor itself, which added a
lot of heat to it. Dumb for a proper installation, but good for fully
testing the system.
Air flow was about 2 litres / second, in that it took 20 seconds to fill a 40 litre bag.
The air then passed through 3 m of hose, bubbled through about 30 cm
vertical of water, and exited into the house through another 3 meters
hose.
............Air In....Air Out...Air House
11:15.......50......24...........30
11:30.......52......24.5........30
12:05.......54......24.5........31
12:40.......53.5....24..........32
13:25.......55.5....24..........29
14:40.......50......24.5........28
15:20.......49......24.5........27
16:20.......46......25...........26
17:05.......48......24.5........26
19:10.......45.5....24.5........25
'Air in' being the temp coming out of the hose from the pump, ie just
before it enters the tank. Pretty high due to the motor, the general
air temp was about 34-36.
Air out is the air coming directly out of the tank.
Air house is the what came out into the house. At about 13:00 I
wrapped the whole last length of hose in insulant and moved it out of
the sun. I was surprised by how much heat the air picked up through only
a couple meters of rubber hose, but there you go.

So I guess the two most striking things are that even with a
fairly basic interface between the air and water (vague attempt at a
diffuser, not really) the air dropped all it's heat, even at 55 C.
And that even with only 20 litres of water, which was only ever meant
as a quick test, the water temp didn't really come up over the ground
temp. True that 2 litres of air per second isn't much (I could've turned
the motor up a lot more, but didn't want to 'splode it) but at an
average of 50 C, the air was twice the temp above 24 that it would
probably usually be running, so is therefor the same energy as 37 C at 4
litres per second, which is quick enough to replace 50 cubic metes of
air in about 3.5 hours.
Which aint bad, frankly. It aint bad at all...
Thoughts?