Anonymous Poster #1

Molded Case Switch And Circuit Breakers

04/03/2011 4:35 AM

Hello,

I just need to know please why it is recommended to have molded case switches (MCS) on the upstream level of the switchboard and after its main circuit breaker? Can it be replaced by a circuit breaker?

Another question is: why is the MCS rated as the next rating size of the breaker?

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Molded Case Switch And Circuit Breakers

04/03/2011 10:46 AM

A Molded Case Switch is an MCCB without the protective release. Just an on-load isolator. It is used to isolate certain circuits for maintenance. Protection is available in the MCCB anyway. Another way is to use a Plug-in CB, which can be withdrawn for (a) maintenance on itself and (b) isolation of the downstream circuit for maintenance. Such a CB will replace both the MCS and MCCB in this situation.

i did not know that the MCS is rated higher than the downstream MCCB. Possibly so that it will stay on when there is a short-circuit till the MCCB clears. Or maybe it is a code-related thing.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Molded Case Switch And Circuit Breakers

04/03/2011 4:51 PM

Your question doesn't make a lot of sense. Re difference in feeder protection against board protection. Quite normal in HV systems, but not in a situation where LV MCCB's would be used.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Molded Case Switch And Circuit Breakers

04/03/2011 6:44 PM

Even though an MCS is an MCCB "without the trip elements", it's not really true. They still have magnetic trips, they're just not adjustable; usually fixed at 10X the frame size rating of the breaker. This is in order to prevent the breaker from exceeding it's interrupt capacity and having someone try to open it manually in that occurrence. If a high magnetude fault occurs, the MCS will still open IF the fault is not interrupted at a lower level (closer to the fault). So if your purpose for having an MCS in a peice of switchgear is STRICTLY as an isolator for maintenance, to avoid confusion after an even, you size it one frame size ABOVE the main breaker so that in the case of a fault, it's the main breaker that trips, not the isolator.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Molded Case Switch And Circuit Breakers

04/03/2011 8:44 PM

Yes, the MCS does have high-set magnetic trips usually for self protection, no use to the customer though. That is why i ignored it. But your answer is more complete.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster #1
#6
In reply to #4

Re: Molded Case Switch And Circuit Breakers

04/04/2011 12:50 AM

Thank you. I really appreciate it.

Reply
Anonymous Poster #1
#5
In reply to #3

Re: Molded Case Switch And Circuit Breakers

04/04/2011 12:47 AM

Thank you. I reallay appreciate it.