DGA for Transformer

04/03/2011 4:36 AM

Here i will put examples for DGA test report for discussing the actions.

All other gasess not mentioned here are below limit and normal

1. TX#1 Conservator type 34.5/13.8 KV

Co2 Gas

25.02.2008

2717(PPM)

02.02.2009

2876(PPM)

02.01.2011

2881(PPM)

CO GAS

126

114

140

2.TX#2 Conservator type

Ethan C2H6 Gas

25.02.2008

115 (PPM)

02.02.2009

230 (PPM)

02.02.2009

221 (PPM)

03.10.2010

279

3.TX#3 Sealed type with N2 blanket 34.5/0.480 KV

Co2=256

H2=402

Co=70

CH4=3

C2H6<1

C2H4<1

C2H2<1

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: DGA for transformer

04/03/2011 5:04 AM

Is this a homework question? It looks like it

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: DGA for Transformer

04/03/2011 3:52 PM

If this isn't a homework question I am a little more worried about the calibre of our new distribution engineers.

There is not enough information supplied for any meaningful comments.

Jack - Actually works in the power industry.

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: DGA for Transformer

04/04/2011 10:57 AM

Based on evaluation metrics from ANSI/IEEE C57.104, I would give the following evaluations:

TX#1 - Gases are normal; no unusual conditions based on the data provided.

TX#2 - Ethane gas usually indicates localized overheating under the oil. These values are high enough to note, but not severe. It could be a bolted conductor connection (at a bushing, etc.) or a contact in the NLTC (No-Load Tap Changer) that hasn't made good contact pressure. Re-test in 3-6 months to see if it increases more, and investigate if it does. This will require internal inspection - what are ratings of this unit?

TX#3 - The only gas of concern here is the level of H2, which is somewhat high. That often indicates corona discharge under the oil. I would like to see historic data to know if it has been increasing, but if it is stable, then no major concerns. Another possible cause is if someone used a galvanized component (bolts, etc.) inside the TX - sometimes water in the oil will be catalyzed by the zinc to split into H2 and O2; that's not so common,but I have heard of it happening.

Didn't whoever analyzed the oil give you an evaluation, or are you trying to get a second opinion?

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Member

Join Date: Mar 2011
Posts: 9
#4
In reply to #3

Re: DGA for Transformer

04/05/2011 7:19 AM

Thanks for your answer

First i will start from last.

are you trying to get a second opinion?

Yes this is my goal when i put this question.

TX#1

I agree with you

TX#2

I agree with you

But what is the impact when C2H6 is kept without any oil treatment because to reach high level need years as per the history.

Tx#3

Also test for Passivator and corrosive sulphur at oil was done and found OK.

Electrical tests will be done for the transformer (is it will show something or need partial discharge test.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #4

Re: DGA for Transformer

04/05/2011 7:54 AM

Regarding TX#2, if Ethane is the only significant contributor to the total combustible gas (TCG), then I wouldn't worry a lot. Although it is increasing some, the rate is not severe. I would watch it through a few more test cycles, unless it starts to increase more rapidly. You can safely operate with several thousand ppm of combustible gases (except if it's acetylene) in the oil with little concern.

For TX#3, the inhibitor and corrosive sulfur tests only tell you about the quality of the oil, not what is happening in the transformer. A partial discharge test could show you if there is corona/discharge under the oil, or it may require an internal inspection to show the point of generation of the hydrogen (if it is a localized hotspot). At the level you have (~400ppm), I also would not be too worried yet. Since you didn't give historical info, I can't comment on a trend. If it isn't increasing, or not quickly, then I would consider just monitoring (annual or 6-month interval) testing until you see a change in rate.

Be wary of oil testing companies that try to sell vacuum reprocessing services to remove the gases from the oil. Yes the gases are removed, but it does not solve the problem that caused the gases, and it destroys your baseline values for trending. Instead, find a qualified service company that will help you investigate and correct the cause of the gases, then reprocess after the problem is fixed.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments