Hold On and Drop Down Characteristics of DOL Starter

04/03/2011 9:54 PM

Can anybody explain me the hold on and drop down characteristics of 3 phase DOL starter?

I performed an experiment in Lab to find out the characteristics. And Instructor asked me to note hold on and hold off voltage of the DOL starter. It is a basic DOL starter with thermal overload relay.

Please explain me hold on and hold off voltage also.

With regards

__________________
A.Classy.Lass
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Hold on and Drop Down characteristics Of DOl starter

04/03/2011 10:05 PM

You will get some excellent information from the Cutler-Hammer training modules here

Look at Module 19 which is for starters and contactors.

The pick-up, hold on and drop off characteristics are for the electromagnetic contactor. So, you need to understand the functioning of the contactor and the parameters that govern its performance. In IEC standards, the pick-up should be <85% of the rated control voltage, and the drop-off should be between 70 and 35%. Usually happens at about 45% with AC coils. The only thing i can think of as a "Hold-on characteristic" is the consumption, usually expressed in VA (it is a low pf circuit). In AC coils, the hold-on VA is usually 10% of the pickup VA.

Hope this is of some help. Good luck.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 4)
2
Member

Join Date: Aug 2010
Posts: 5
Good Answers: 1
#2

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 1:40 AM

A solenoid coil used for starters/ contactors has definite pick up, hold on & drop off values.

If a variable supply is connected to such coil & voltage ia gradually increased, it will be found that at some value V1 the coil is able to latch the contactor i.e. pulls up the magnetic core. This is called pick up value.

If now the voltage is gradually lowered it will be found that at certain value V2 the coil is unable to hold the magnetic core & it drops thereby delatching the contactor. This is called drop off value.

V2 is always < V1 Since V1 has to take care of the Inertia of Rest of the Magnetic Core.

Any value of voltage between V1 & V2 is called the hold on Voltage i.e. the voltage at which the Coil can sustain latching.

Hope this will clarify the doubts.

Regards

Debasis Nandy

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#3
In reply to #2

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 3:58 AM

This is simular to the logic of a PLC, between 0 and 1 there is always a grey area on the inputs.

The energy required to pull the relay on is greater than the energy required to hold the relay, once the relay has made contact with it's corresponding contact surface the current will be lower if we are talking about an AC Coil contactor, this is due to back EMF.

Cheers

Joe

Register to Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#5
In reply to #3

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 11:59 AM

Back emf.......

What a load of Crock.

C'mon.

Are we professionals here. or what.

Cheers

Mark N.

PS. 'spose it could have been Eddy currents.....!...////...!

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #5

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 11:18 PM

Excuse me Markone, but Joe is right i think ... there is a back-emf which makes the hold-in current far less than the pick-up current. Mainly due to the high inductance of the 'sealed' magnet. There are plenty of references on the web about this, here is a video also http://techtv.mit.edu/tags/1969-spark/videos/880-mit-physics-demo----back-emf-in-a-large-solenoid

Eddy currents have nothing to do with this. Designers strive to reduce eddy current and hysteresis losses in AC solenoids.

Anyway, we are now in the age of the microprocessor-controlled coils, which use pulse-width modulation to give just enough power to the moving system so that the contacts close with minimal bounce, and the consumption is extremely low.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#12
In reply to #9

Re: Hold On and Drop Down Characteristics of DOL Starter

04/07/2011 5:21 AM

Hi Kvsridar, Thanks for your support My Freind.

You and I know that we are both right.

Mark is wrong, and is giving wrong advise to the forum. If you look at previous threads that he has been involved in,the also make no sence.

Kvsridar, I have a a lot of respect for you and your reply in my defence!

But all of this has not answered the question that was asked directly, I will have a go at thying to answer this tomorrow.

Best Regaeds

Joe

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#10
In reply to #5

Re: Hold On and Drop Down Characteristics of DOL Starter

04/06/2011 12:50 AM

For some reason Markone, I dont like your attidude.

Of course Back EMF is a factor, why do you think coils burn out. A lot of the time a contactor coil can burn out if if the armiture and the base have not made a good contact, this can be caused by some foreign material being trapped between the contact surfaces.

You call yourself a professional, so why did you get out of your trade couldn't you handle it. I think that you went into sales because you were washed up as a electrician. With the attidude you have I think that the best carrer move that you have done was to retire!!!!!

Best Regards

Joe

Register to Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#11
In reply to #10

Re: Hold On and Drop Down Characteristics of DOL Starter

04/06/2011 1:31 AM

Yeh, well I suppose, if you lead with your chin, we will have someone hit us.

Fair Comment.!

But, Joe, don't presume, that which you don't know, as I, also, shall not presume anything of, or in life.

And, you have proved my point.......! "sometimes Good Electricians, don't see the Volts for the Amps."

We, all of us, aren"t perfect, in particular...Me...!

Cheers.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #2

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 8:18 PM

I tried it on an electro-magnetic contactor 3 times in succession and got different results,why?.

__________________
pnaban
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 9:39 PM

If you are doing it on an AC coil, it could be due to the point-on-wave when you give the closing command. Or when you reduce the voltage and hunt for the drop-off point. Then there are mechanical contributors...friction, spring forces... Even with DC coil, unless it is a battery supply, the ripple of rectified DC will give different results.

In any case, if you study the gate limits of IEC, they are pretty wide. The pick-up and drop-off values are not expected to be precise.

However, your query is aimed at Debasis, so he will respond too i hope.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#4

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 11:50 AM

I reckon that the control voltage you are using is DC.

You haven't stated as such in your enquiry post.

I am not going to advise of the math in the equation, but to suck it in, is a lot more than, to hold it.

Common answer to a large contactor coil, for a 100 amp contactor and above is to actually have a Dc coil, to pull him in.. Most cases the DC bit is done in the coil, ie 240vac, bridge rectifier in the coil, and so on.

The main reason, is that most control devices, timers, relays, pressure switches, etc are only rated at 10amp ac ac1, whereas to suck in a, say 400amp ac3 contactor, say using a 110vac coil:- will actually need another smally type contactor to do the "Sucking".

You really have to sit back and see what is going on.

I am an electrician, not an Author or a Teacher, but if you can understand that which I am trying to say here, will help

  1. Answer your Question
  2. Save you a lot heartache later on in life.

I have worked as a sales Engineer most of my life, and to acquire a solution to this problem is as hard as...................I have nearly wanted to kill..............

Normal sane electricians ( that I would Pin my Life on) have said to me, the coil pulls 20amps, and burns out the contacts in the timer, Your contactor is Faulty. I have shown them the coil operating data for the opposition stuff, and they all pull about the same current, but.......no...it was my gear that was the problem........

We sometimes don't see the Amps for the Volts. Bit Cryptic, but I hope you can understand this problem. Learn, from your Instructor......he has more than likely been Bit, B4

All the Best Cheers............Learn.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#6
In reply to #4

Re: Hold On and Drop Down Characteristics of DOL Starter

04/05/2011 12:06 PM

Sorry fellas...................

Please reply personally what makes my reply '''Off Topic""

Fair Dinkum, I really want to know??????

Cheers.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply Off Topic (Score 5)
Associate
India - Member - New Member

Join Date: Feb 2011
Posts: 45
#13

Re: Hold On and Drop Down Characteristics of DOL Starter

04/07/2011 9:27 AM

@ kvsridhar

Yeah! i daily see all comments. My concept is clear now .

You rock buddy..

Module 19 is really helpfull.

__________________
A.Classy.Lass
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #13

Re: Hold On and Drop Down Characteristics of DOL Starter

04/07/2011 9:34 AM

Oh, sorry. Should have occurred to me that you may not have time to respond. We usually see some mails from the OPs, asking for clarifications, more info etc, so no mail from you made me say this. Glad to have been of some help. Please feel free to ask for more if you need, maybe some of us can help. Good luck.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Associate
India - Member - New Member

Join Date: Feb 2011
Posts: 45
#15
In reply to #14

Re: Hold On and Drop Down Characteristics of DOL Starter

04/07/2011 9:39 AM

@kvsridhar

Surely !

Thanks :)

__________________
A.Classy.Lass
Register to Reply Off Topic (Score 5)
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: