HV Termination in a Hazardous Area

04/04/2011 10:54 PM

Morning,

we are to connect a 3.3Kv cable in a type IIC hazardous area and we are required to use a barrier gland. To complete the barrier gland you need to brake out the cable to the individual conductors to allow the compound to be installed but to install the HV termination boot you require the inner sheath to still be on the cable which is removed fo the barrier gland.

If we form the 3 conductors back into a circular shape using some product (?) to allow the HV boot to seal properly will this effect the HV termination?

or is there another way of terminating this install

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: HV Termination in a Hazardous Area

04/04/2011 11:59 PM

Not sure about HV cables, but are you not able to get an a suitable barrier gland that also allows you to terminate the cable screen to the gland body.

I cannot quite picture what you mean by the HV cable boot (do you simply mean a heat shrink 3 way breakout boot, but then I don't see the problem).

Do you have pictures/part numbers/specs of the cable and HV boot you could post for clarity?

__________________
jack of all trades
Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#2
In reply to #1

Re: HV Termination in a Hazardous Area

04/05/2011 12:44 AM

Thanks jack,

yes by a 'HV Boot' I do just mean the 3 way break out.

By removing the inner sheath and sealing this to the material we use to form the replacement sheath do we comprimise the integrity of the HV termination kit.

And does having the conductors broken out without the heat shrink inside the barrier gland after the 'boot' cause any additional problems? I do not think this is a drama but would like your opinion

Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#3
In reply to #2

Re: HV Termination in a Hazardous Area

04/05/2011 5:27 AM

Sorry I should also add that it is a lead sheathed steel wired armoured cable we are required to use.

Register to Reply
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #2

Re: HV Termination in a Hazardous Area

04/05/2011 3:07 PM

By removing the inner sheath and sealing this to the material we use to form the replacement sheath do we comprimise the integrity of the HV termination kit.

It depends on the barrier gland you use. You should be able to find information on the barrier gland supplier's website regarding barrier glands suitable for use with steel wire armoured cable. I have no experience with HV barrier glands but the principle should be the same.

And does having the conductors broken out without the heat shrink inside the barrier gland after the 'boot' cause any additional problems?

It shouldn't as the main purpose of these boots is to weather seal the cable end (which should already be accomplished by a suitable barrier gland).

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#5

Re: HV Termination in a Hazardous Area

04/06/2011 7:50 AM

If you have not been properly trained, you should not perform the task. If not done correctly the 3.3kV line will fail causing an arc flash which will ignite the hazardous atmosphere resulting in an explosion that will destroy the surrounding area and any personnel nearby. Bad news any way you look at it.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2011
Posts: 4
#6
In reply to #5

Re: HV Termination in a Hazardous Area

04/06/2011 5:41 PM

couldnt agree more gazu,

I am trained as a HV terminator although one of our contrctors will be performing the task.

our usual method for this install would be to run individual XLPE but the client has specified the multicore

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!