Lightning Arrestor Rating

04/05/2011 12:32 AM

Can't i use a 198 kv lightning arrestor for a 33kv system? If no, why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Lightning Arrestor Rating

04/05/2011 8:23 AM

You can, if you don't care that lightning or other surges will damage or destroy your electrical equipment and system. But if you want protection from lightning, you need to have a properly rated arrester, so that it diverts the surge to ground at a voltage level below the limits of what your equipment can withstand. Hire a qualified engineer to evaluate your system and specify the correct arrester rating for your needs.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Lightning Arrestor Rating

04/05/2011 3:40 PM

If no, why?

Would you protect a 10A circuit with a 100A fuse? Best to get the correctly-rated surge arrestor otherwise it won't provide the protection required.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Lightning Arrestor Rating

04/06/2011 5:56 AM

Are you filthily wealthy? Why then would you use a costly 198kV arrestor for a 33kV system?

Register to Reply
Member

Join Date: Feb 2011
Posts: 6
#4

Re: Lightning Arrestor Rating

04/06/2011 1:12 PM

Dear All,

Let me put it this way. I have a 220KV/33KV transformer for the power distribution within my plant. However, the 33KV CICO panel which I've ordered shall take some more time and so I'd to plan for an alternative. So, we have decided to use one 220KV outdoor spare bay for my 33KV side protection. It includes a 220KV breaker, a 198KV LA and the CTs rated for my LV current suitably. Now pls tell me whether I can use my 198KV LA for my purpose or I need to arrange specifically for an LA of suitable rating?

Pls answer with the technical drawbacks of using my 198KV LA for the purpose.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #4

Re: Lightning Arrestor Rating

04/07/2011 12:24 PM

Using a spare 220kV bay to temporarily feed a 33kV circuit is an inventive idea, and should work for you. However, as I said before, the 198kV LA will NOT protect your 33kV rated equipment. You should temporarily install properly rated arresters for the duration of your temporary feed. You could even leave the 198kV units in place too - they won't hurt anything, but they won't help. The "technical drawbacks" of not having the right rating LAs: If you get a lightning strike or other transient high-energy surge, your cables could fail, your downstream transformer could go "boom!" or damage to other 33kV rated equipment can and will take place. It's your risk!

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Lightning Arrestor Rating

04/07/2011 1:23 PM

<...Pls answer with the technical drawbacks of using my 198KV LA for the purpose....>

Simples: It won't 'king work properly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

dhanshyam (1); electricalexpert65 (1); jack of all trades (1); PeterT (2); PWSlack (1)

Previous in Forum: HV Termination in a Hazardous Area   Next in Forum: 11 kV Cabling
You might be interested in: Lightning Protection Systems, Antennas, Chip Antennas

Advertisement