Cool Capacity (Btu/hr) vs Actual Size (ton)

04/06/2011 4:53 AM

I have just bought an airconditioner with cool capacity of 45,000Btu/hr and power source of 4500watt. I understand that 12,000=1ton but the manufacturer wrote 5ton on it. with the Btu on it, i calculated 4ton.

what is the correct conversion rate of btu to ton?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: cool capacity(Btu/hr) vs actual size(ton)

04/06/2011 5:24 AM

As you stated, 12,000 Btu/h = 1 ton of refrigeration; 45,000 Btu/h = 3.75 tons.

(There may be a higher precision number such as ~12,050; but 12,000 is most commonly used.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2011
Posts: 7
#2
In reply to #1

Re: cool capacity(Btu/hr) vs actual size(ton)

04/06/2011 11:09 AM

Thanks tornado for the reply, its a confirmation I really needed cos of the confusing spec on the a/c.

Would you also know the conversion rate from the input to ton?

the input on the a/c is 4,500w.

once again thank you.

Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/06/2011 3:40 PM

This from Wikipedia:

"Historically, one Ton of Refrigeration was defined as the energy removal rate that will freeze one short ton of water at 0 °C (32 °F) in one day. This was very important because many early refrigeration systems were in ice houses. The simple unit allowed owners of these refrigeration systems measure a days output of ice against energy consumption and compare their plant to one down the street. While ice houses make up a much smaller part of the refrigeration industry than they once did the unit of Tons of Refrigeration has remained in North America. The unit's value as historically defined is approximately 11,958 BTU/hr (3.505 kW) has been redefined to be exactly 12,000 BTU/hr (3.517 kW)."

Register to Reply Good Answer (Score 2)
Member

Join Date: Apr 2011
Posts: 7
#7
In reply to #3

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 2:35 AM

Hi Lyn,

This is really revealing for me and got me learned.

Now I know why the cooling capacity is in tons.

Thanks

Seun

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/06/2011 6:41 PM

The watts needed to produce x tons of refrigeration depends on the evaporation and condensing pressures, the refrigerant, the ambient temperature, and the efficiency of the system components. Larger surface area of heat exchangers yields higher efficiencies. For air conditioning, too large an evaporator leads to too high humidity, so a main determinant of system efficiency is the condenser area. Your 4500 watt (electrical input) unit should be easily capable of producing 45,000 Btu/h of cooling, unless the ambient temperature is really hot.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2011
Posts: 7
#8
In reply to #4

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 2:39 AM

Tornado,

Thanks for your wealth of info.

Am in Africa and the temperature we are experiencing in the last one month has been very high sometimes its just 43degree perpetually.

Am beginning to understand why the a/c may not be achieving the kind of cooling, i really need-ambient temperature is very hot.

Thanks alot

Seun

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#11
In reply to #8

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 8:21 AM

As Tornado was saying, the capacity is function of evaporating and condensing pressure. The same unit, accepting that outside temperature remain constant, has different capacities at different evaporating pressures. Depending of refrigerant, the capacity the unit has when evaporating pressure is tuned up for +5 deg. C is almost double then when is tuned up for -10 deg C. You can increase the capacity by raising the evaporating pressure (if it has expansion valve you can tune it up), however the power absorbed by the compressor will increase too. Another way to increase the capacity is to lower the condensing pressure, and that can be done by spraying water over the condenser (careful with electric motors) . That helps a lot the unit, mainly in the hottest part of the day.Standard ton is with evaporating pressure for 5 deg. F and condensing pressure for 86 deg. F.

Register to Reply
Member

Join Date: Apr 2011
Posts: 7
#14
In reply to #11

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/08/2011 2:27 AM

Hi Jerybaciu,

Am interested in the expansion valve tuning. I tried opening it up all I see are gas pipes and some panel.

Could you write how it look?

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#15
In reply to #14

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/08/2011 9:22 AM

The expansion valve you find it on the evaporator, (that in inside the house) at the end of the smaller pipe that comes from outside unit. If you see something resembling the picture, then that is it. Do not worry if you do not see it, in this days they make the units much cheaper, replacing it whit capillary tube, that is a very thin pipe. In the last case, you can not adjust the pressure in good way. You need specialised tools (gauges, hoses) to adjust the pressure, and is done (after you hook up the gouges, so you know what you are doing) by opening the cap (that in picture above is in the left side near the bulb (silver), the bulb is attached to the bigger pipe that comes out) and turn the screw clockwise to lower the evaporating pressure, or the other way to increase it. You have to put a amp meter on the compressor to, as the power drown by it will increase. Be careful, the amps have to be lower then that at which the compressor is rated.

Register to Reply
Active Contributor

Join Date: Feb 2011
Location: GTA Canada
Posts: 15
Good Answers: 2
#16
In reply to #14

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

05/25/2011 11:22 PM

This unit has an electronic expansion valve.

Register to Reply
Active Contributor

Join Date: Feb 2011
Location: GTA Canada
Posts: 15
Good Answers: 2
#5

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 12:22 AM

Can you give the specific model number and manufacutre?

Register to Reply
Member

Join Date: Apr 2011
Posts: 7
#6
In reply to #5

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 2:32 AM

Johnsonr1,

Thanks for asking.

The model no on the indoor unit is cu-45ffh while the model no on the outdoor is cs-c45ffh and its panasonic.

I tried checking it out on their page , apparently it appeared that they have not updated their site.

Thanks once again

Seun

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#9

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 4:38 AM

12000 btu/hr = 1 TOR .Refrigeration capacity is evaporator capacity. Air cooled condensers are 25% higher than evaporator capacity . Heat rejection ratio.

Register to Reply
Power-User

Join Date: Apr 2011
Posts: 188
Good Answers: 6
#10
In reply to #9

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 8:13 AM

You can help just a little with a very fine occasional water mist on the condensor and by keeping the condensor in the shade if it's very hot.....

Register to Reply
2
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/07/2011 8:38 AM

As it has been mentioned before, this is not a 5 ton unit definitely!

Also, the power input of 4500W will only give at best 40,000 BTU/h in your climate. An this is stretched fine. The general ratio is 2.5 to 1 whic comes to ~ 38,000 BTU/h, again I stress that the unit will be working at its optimum design criteria, Which is never achieved on site and in particular in your climatic conditions. Your mentioned unit will give on average 3 Ton cooling.

Register to Reply Good Answer (Score 2)
Member

Join Date: Apr 2011
Posts: 7
#13
In reply to #12

Re: Cool Capacity (Btu/hr) vs Actual Size (ton)

04/08/2011 2:21 AM

Thanks Lucke,

From your analysis and the notes have checked too, the a/c is definitely 38,000Btu/h against the 45,000Btu/h pasted on it.

Figured I had been short changed. But now am very knowledgeable about this.

Thanks

Seun

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

corbinstein (1); jerybaciu (2); johnsonr1 (2); LAA_Lucke (1); lyn (1); mrswamy (1); seun (6); Tornado (2)

Previous in Forum: Making Sheet Metal Slitting Cutters   Next in Forum: Us of Bolt Tension for Nuts Loosening

Advertisement