BDV of Transformer Oil

04/07/2011 12:40 PM

I am having one confusion about BDV of transformer oil. Usually oil with BDV=28-29 KV is considered ok. But my question is if the transformer rating is 132KV/66KV in that case also BDV value = 29KV is ok or is there any IE rule for BDV of transformer with different KV rating???

__________________
Thanks
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: BDV of transformer oil

04/07/2011 1:09 PM

There's no confusion here. Just use the correct oil. Unless........

is acceptable?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: BDV of transformer oil

04/07/2011 3:12 PM

According to IEEE Std C57.106-2002, there are different breakdown voltage values depending on the voltage class of the oil-filled equipment. For a 132kV transformer, it falls smack in the middle of the range of 69kV-230kV, for which the minimum BDV is 28kV (ASTM D1816-97, with 1mm electrode gap). I would rate that oil acceptable if I were receiving the test results.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: BDV of transformer oil

04/08/2011 10:03 AM

BDV OF TRANSFORMER OIL (As per IS 6792:1992)

The oil sample is subjected to a steadily increasing alternating voltage until breakdown occurs in a BDV test kit. The breakdown voltage is the voltage reached at the time of the first spark appears between the electrodes. The test is carried out six times on the same cell filling and the electric strength of the oil is the arithmetic means of the six results obtained. The electrodes are mounted on a horizontal axis with a test spacing of 2.5 mm. The value should be:

Electric Strength (BDV)

Vide IS 1866:2000,

30kV - for Voltages upto 72.5kV

40kV - Above 72.5kV upto 170kV

50kV - Above 170kV up to 420kV

Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2009
Location: Mumbai
Posts: 73
#4
In reply to #3

Re: BDV of transformer oil

04/09/2011 11:44 AM

Dear Guru,

Thanks for providing a good answer.

But on 7th Apr why you have taken my question as a joke?

& replied perfectly on 8th Apr????

Anyway, thanks again

__________________
Thanks
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: BDV of transformer oil

04/09/2011 12:02 PM

Dear Sir, Please take a close look. On 7th it was not me, but M. Slack, who had answeredyour query. I answered your query first and only on 8th April. I do not play jokes on people who are sincere to learn.

Register to Reply Off Topic (Score 5)
Register to Reply 5 comments