Electrical Panel Inspection

04/11/2011 11:18 PM

Dear friend,

A new question regarding to panel wiring inspection, after we finish panel installation and wiring, we need to inspect them.

To do this, as I read from several standard books that we need to disconnect all the wiring from equipments to do the necessary tests.

Do you think it is suitable? Could you (electrical inspectors, gurus) let me know what you will do at this stage?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Apr 2011
Posts: 4
#1

Chain Sprocket Hobs

04/12/2011 1:16 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Electrical panel inspection

04/12/2011 4:49 AM

Should have done the tests before connecting then!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: Electrical Panel Inspection

04/12/2011 8:46 AM

Upon completion of a new panel install, the extent of our testing is verify conduit/connector bushings are in place, tightening torque of all conductor nuts/bolts, amp probe line and load conductors, conduct IR (Infrared) imaging of panel with loads energized (turned on), make sure panel schedule is accurate and complete, clean tub and replace cover.

Record all findings/results on customer supplied form or create your own.

I have never heard of disconnecting all wiring after installation to do necessary tests.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - Target Shooting - New Member

Join Date: Feb 2010
Location: Florida
Posts: 259
Good Answers: 29
#4

Re: Electrical Panel Inspection

04/12/2011 10:37 AM

Inspections should be ongoing throughout the fabrication process and may include any level or depth of inspection. The depth of inspection depends on how critical the panel's design function might be. If a failure might affect other equipment to the extent that it may be damaged or cause an unsafe condition, then the highest level of quality control should be employed. If the panel's only function is to provide circuit protection for lighting, then a simple visual inspection of component layout to match design drawings and checks for terminal tightness might be all that's necessary.

A more in-depth inspection might include verification that cable size and insulation type meet design input. Crimped and soldered connections are made correctly, and terminated on the correct lands. Switch, instrument, and indicators are the type and rating specified...etc.

__________________
Si vis pacem, para bellum
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Electrical Panel Inspection

04/12/2011 12:20 PM

I think first you need to clarify what you means by "electrical panel". Do you mean a circuit breaker panel, a residential load center, an industrial control panel, a panel that came on a piece of equipment, what? It makes a difference.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#6

Re: Electrical Panel Inspection

04/13/2011 9:18 AM

dear,

At the time of carrying out the H V Test , you need to disconnect all the control fuses, instrument supplies.

Rest you don't require to disconnect.

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7

Re: Electrical Panel Inspection

04/14/2011 2:31 PM

An inspection of the actual panel in an industrial or commercial setting would include short circuit, protective device coordination and arc flash testing. Available fault levels would need to be obtained. Fault levels would be used to determine the worst case fault level for main switchgear and all assocated panels and sub-panels.

Arc flash calculations would include magnitude, device clearing times, arc duration, arc boundaries, working distances, incident energy and PPE ratings for service.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!