One for the Older Ones

04/13/2011 3:32 AM

This is one for the older ones on the board. Mining has always been an interest of mine (sorry J) since getting involved with an ill-fated limestone mine. (It was intentionally doomed to failure from the outset).

Can anyone tell me how / why all the main components of this set up have dual rating. Ex pit electricians I've spoken to have never come across a set up like this.

Extract from a report by
A. E. Crook, C.B.E.
H. M. Principal Inspector of Mechanical Engineering
on the causes of, and circumstances attending, the Overwind which occurred at Brookhouse Colliery, Beighton, Yorkshire, 4th March, 1958.

The drum is coupled directly to a D.C. winding motor that bears a name plate on which the following particulars are included: 1,200/2,040 h.p., 53.7 r.p.m., 425 volts, 2,260/4,000 amps. This motor is supplied with electrical energy by an induction-motor-driven Ward Leonard set with flywheel and slip regulator, which runs at a speed in the range of about 1,000 to 820 r.p.m. according to the magnitude and direction of the unbalanced load in the cages. The set includes a 900/1,700 kilowatt, 425 volt, D.C. generator, a flywheel weighing 11¼ tons and a 900/1,800 h.p., 3,300 volt, 3 phase, 50 cycles, slip-ring induction motor, which is controlled by a combined liquid starter and slip regulator.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: One for the Older Ones

04/13/2011 11:05 AM

Probably for infinitely variable speed control combined with smooth torque control. It's basically a high gain closed loop control system that was originally built before the advent of vacuum tubes and solid state devices. It's why elevators have such smooth transitions from starts to stops. Same for your mine winches. Here's more.... http://en.wikipedia.org/wiki/Ward_Leonard_control.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: One for the Older Ones

04/13/2011 12:53 PM

It's the dual rating for the components that confuses me.

I've worked on Ward Leonard systems for over 30 years but I've never found drives rated like this.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: One for the Older Ones

04/13/2011 3:05 PM

Thanks for the clarification. Having failed at my first attempt I'm going to venture the guess that this is some form of a "universal" or "multi-use" MG set that is wound with pairs of symmetrical windings that depending upon the application allows for running them either in series or parallel depending on the voltage available and/or the horsepower desired.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#4

Re: One for the Older Ones

04/13/2011 11:20 PM

This is an ole time rock crusher, still in service? Is it direct or pendulum?

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#5

Re: One for the Older Ones

04/14/2011 12:17 AM

On Winder motors in the Paper industry we often get NP ratings like:

300/300/300Hp 250/340/1200 RPM 652/480/480Amps 368/500/500VDC

O/L 200/200/100% 60 seconds

Field 20/20/3 Amps

The motor is run below base speed at 250 RPM, but is allowed a higher current to produce the 300 hp required. As the motor exceeds the base speed of 340 rpm the field is reduced to achieve the higher speed. But the current commutation is limited at week field and tapers to 100% NP at 1200rpm.

I do not have the data sheets for your motor, but would not be surprised if they have similar envelopes of operation defined. The NP's get pretty cryptic for some of the special applications.

Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#6

Re: One for the Older Ones

04/14/2011 12:32 AM

I was thinking Strong field / weak field, but on rereading the values I think it might be continuous rating / short time rating . Traction motors often have a short time rating far higher than their CMR. Are the motor and generator both compound wound, (the series component of of the generator may be in the form of busbars)?

Is the motor a slip ring induction motor or a synchronous motor? Synch motors are more common on MG sets. They can look a bit confusing with a large squirrel cage in the rotor too. The cage is the amortisseur winding which also doubles as a squirrel cage on DOL starting. The easy way to tell is a Synch motor will have 2 slip rings and wound rotor induction motor 3 rings.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#7

Re: One for the Older Ones

04/14/2011 1:46 AM

I would guess two speed and load settings. One for stuff and one for men.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #7

Re: One for the Older Ones

04/14/2011 4:06 AM

That makes sense for the generator and final drive, there were two speeds for men and coal. They weren't that different though. But I'm still puzzled why the generator set has a dual rating for the drive motor. The motor it's self is a weird set up, slip ring with a liquid slip controller so resistance was always in the rotor circuit and a flywheel. It's allowed to slip by 15% giving up power from the flywheel when accelerating the cage drum.

I'm gleaning a bit more from the accident report, but it's like wading through porridge, heavy going.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Jul 2010
Posts: 9
#8

Re: One for the Older Ones

04/14/2011 2:42 AM

Hi,

I am not entirely sure about this, but the Coal Board generally used reverse power braking on the coal skips and dynamic dc braking on personnel winders, with variable liquid resistance control. I think the rating must be due to the short term braking forces.

Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member Engineering Fields - Construction Engineering - Member Engineering Fields - Mining Engineering - Member United States - Member - Member Popular Science - Weaponology - Member Hobbies - Target Shooting - Member Hobbies - Car Customizing - Member

Join Date: May 2008
Location: Cary, NC, USA
Posts: 131
Good Answers: 7
#10

Re: One for the Older Ones

04/15/2011 7:50 AM

Most of these had dual operating ranges. One for materials and one for men.

__________________
You cannot escape the responsibility of tomorrow by evading it today - Abraham Lincoln
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#11
In reply to #10

Re: One for the Older Ones

04/15/2011 9:19 AM

Re: Most of these had dual operating ranges. One for materials and one for men.

Were these two different speeds? (I ask because the ratings on this motor both appear to be at the same speed (53.7 r.p.m).)

Or maybe it was for two different loads?

I'm not really arguing with you, I'm just puzzled. I guess I'm thinking that it had a lot to do with two different loads and the Ward Leonard control system. I'm guessing that the Ward Leonard system could put out anywhere between 2,260 and 4,000 amps, varying based on the load, and the motor could handle that same 2,260 and 4,000 amps, varying based on the load, maintaining the same speed with either load.

Maybe somebody has said this already, or at least in essence. I'm just trying to get my head around it. I guess I'm thinking it's sort of like a PID control loop, trying to maintain a constant speed (53.7 rpm) in the face of varying loads, and varying the current to do that.

???

It may be a little misleading to dual rate the motor that way, it seems like the rating on the motor might mention only the highest rating--just like any other motor, it uses less current at lower loads... It seems like the dual current rating would be more appropriate to the generator in the Ward Leonard m-g set.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#12
In reply to #11

Re: One for the Older Ones

04/15/2011 9:32 AM

RPM depends on the pole configuration. E.g. switched 3, 6, etc.

Men require longer 'ramping' than material, or lesser g rates. Materials 'up' higher torque. Materials 'down', higher breaking (regeneration).

It's not a simple 'star delta' system.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#13
In reply to #12

Re: One for the Older Ones

04/15/2011 9:56 AM

Yes, thanks, you're right about different acceleration rates required.

I still think thinking of it as something like a PID controller is useful and not far off the mark.

Considering acceleration, the Ward Leonard system is the (PID?) controller to achieve and maintain the required acceleration under the various conditions, by outputting a varying current.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#14

Re: One for the Older Ones

04/15/2011 10:13 AM

I am starting to recall in some instances the motors were given a 1 hour rating and an 8 hour rating. It also depended on the cooling supplied to the motor.

On some old mill motors we were even given a 5 minute rating. We could get extreme torques and currents for the short time, but then we had to have a cool down period. The alternative if the motor was going to be used continuosly then we had to have the rms current below the 8 hour level.

I suspect you have an 8 hour rms rating, and a short duty high load rating.

The manuals for the machine should spell it out. If it is a GE machine they will probably still be able to dig out the info from the serial #. The old Harland and Westinghouse machines may pose a bigger research problem.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15

Re: One for the Older Ones

04/16/2011 2:31 AM

If anyone wants to have a look at the report:

http://www.dmm-pitwork.org.uk/html/brookhouse.htm

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#16
In reply to #15

Re: One for the Older Ones

04/16/2011 6:06 PM

At the ship yards out here we have a lot of container cranes.

The report reminds me of an incident several years ago where I was asked to investigate why a container had dropped.

Sorting out the jurisdictions was an interesting case. Since the dock was on an ocean port it did not come under provincial jurisdiction but under federal. Federal has very little in the details of protection on these cranes. Provincial has rather up-to-date and stringent requirements, but it is outside there jurisdiction.

Bottom line, when the dust settled it became essentially a case of ensuring that ALL safety matters were addressed and before operation was resumed it had ALL jurisdiction safeties in place and it had been tested and signed off by a professional engineer.

I must admit I don't like being on those cranes. They are high, sway in the wind, and sway with every load. If the safeties screw up you can tip the crane into the ocean. One of the biggest issues in the ship yards is the longshoreman's union. Too many people are grandfathered, and talented electricians are hard to come by because they have to have seniority in the union to work on the cranes. Having people report to the union office every day to even find out if they are working is just silly.

Register to Reply Off Topic (Score 4)
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (2); Emjay4119 (1); GW (3); Jimh77 (1); Old Coal Man (1); Plugg (1); RAMConsult (2); rhkramer (2); TonyS (3)

Previous in Forum: Transistor   Next in Forum: Trifoil Cable

Advertisement