Repeated Shoot-Out on Red Phase of a 33kV Single Core PLWS Armoured Cable

04/13/2011 1:08 PM

Hi all, i need your urgent advice/solution to this problem. Firstly this cable (3no) is terminated to the primary side of a 2.5mva trafo feeding a 50mld water treatment plant. During operations the feeder tripped on over-current. Fault investigated and found out that the j&p fuse dropped on the red phase, Amoured cable terminated to the red phase on trafo primary side had a blow-out on the Raychem termination,also the out-going 11kv cable from the end box of the fused extension of the rmu was also burnt.Cable injection tests were carried out and results ok despite the fact that water was found between the steel wire Armour and the outer pvc of the Armoured cable,insulation readings are in the tetra range! Cable ends re-terminated using raychem kits,a set of new 50A fuses were fused on the j&p,system put on potential and ok.

Secondly,after 4 days the problem re-occurred and the blow-out was on the red phase of trafo primary! However, no fuse dropped- only tripping of the 33kv feeder at the transmitting station thus isolating our feeder.

What could cause this re-occurrence? Is this cable bad? or is there something we are not seeing? Ambient temp. at location is 37degC,Nominal plant loading is 1.4mva,rmu over-current setting is 100A.

Thanks in advance. R4ROTY

__________________
r4roty
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Repeated Shoot-Out on Red Phase of a 33kV Single Core PLWS Armoured Cable

04/13/2011 2:15 PM

Have you done a HIPot test or equal to verify the cable is not testing bad?

Register to Reply
Active Contributor

Join Date: Jun 2010
Location: zaria nigeria
Posts: 12
#3
In reply to #1

Re: Repeated Shoot-Out on Red Phase of a 33kV Single Core PLWS Armoured Cable

04/14/2011 3:40 PM

Yes HIpot test was conducted using a 60kv/m generator, cable passed. fault localized to the termination kit first used.A superior kit from a different manufacturer was used.We are back in operation about 2hrs ago.Thanks for your comment.

__________________
r4roty
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#2

Re: Repeated Shoot-Out on Red Phase of a 33kV Single Core PLWS Armoured Cable

04/14/2011 1:56 AM

Perform a DC hi-Pot test immediately for the R phase.