in a pressure transmitter ,range is 0 to 25 bar, if I getting the 7 ma in series connection how I can calculate the pressure. Pls explain to me with example .
Re: transmitter calibration
04/16/2011 2:52 PM
0-25 bar=4-20mA.
0bar=4mA: 25 Bar=20 mA.
No examples.
04/16/2011 10:57 PM
Hi,
If you are working in calibration workshop, you may ask you superior/co worker they will help you more.
If this is homework then do research.
0~25 Bar = 4~20mA = 0~100%
0bar=4mA=0% : 25bar=20mA=100%
04/17/2011 4:48 AM
The relevant equation is y = mx +c, where m (bars per ma) and c are constants, x is ma and y is bars, y goes from 0 to 25, and x goes from 5 to 20. Now back to your coordinate geometry textbook.
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Re: Transmitter Calibration
04/18/2011 3:19 PM
25/16*(7-4)=4.6875
04/19/2011 8:43 AM
good formula for ya
Amount = %span + lower
7=%(16) + 4
3/16 = 18.8%
now to find out pressure at this current
Amount = 18.8%(25) + lower
Amount = 4.69 bar at 7ma