Re: progressive casecade split range valve sequence
04/17/2011 3:23 AM
If a large valve is suddenly opened from a high pressure to a low pressure section of piping, there can be problems with surge or liquid hammer. To prevent this, a small valve and a larger valve can be installed in parallel. Opening the small one first allows the piping to equalize gently in pressure; then the larger valve can be opened to provide full flow. This is variously described as soft, staged, or cascaded valve operation. It is common in steam and refrigeration systems, among others.
Similarly, large modulating or regulating valves tend to overshoot (hunt) when controlling low flows. For better control at low flow, a smaller regulating valve can be paralleled with the larger one. When the larger valve is nearly closed, control is passed to the smaller valve.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Re: Progressive Casecade Split Range Valve Sequence
04/19/2011 3:48 PM
....it also happens in water distribution mains. The last thing that Mr. Brown at no.22 wants is the water main outside his house erupting as he is having a shave prior to going to work.