Lightning Arrestors

04/19/2011 12:30 AM

hi all,

jus wanted to know if provision of lightning arrestors for fuel oil storage tanks is neccesssary or not??? i've gone through the codes like OISD, The Pertoleum Rules but there is no indication of the same in any. if the provision of the same is mus pls indicate the code or relevant reference too. any help will be appreciated...

__________________
Varun Passi
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#1

Re: Lightning Arrestors

04/20/2011 11:36 AM

I am sure that provision of lightning protection for aboveground oil tank is a must. Try API RP 545 (American Petroleum Institute) for more details.

You can also have a look at this. Note that some of other standards are also recommended at end of the report.

http://ws9.iee.usp.br/sipdax/papersix/sessao12/12.9.pdf

__________________
Anything that can go wrong, will go wrong
Register to Reply
Commentator
India - Member - Mechanical Engineer Engineering Fields - Petroleum Engineering - Mechanical Engineer

Join Date: Jun 2009
Location: Chennai (India)
Posts: 92
Good Answers: 2
#2
In reply to #1

Re: Lightning Arrestors

04/21/2011 1:01 AM

thanks a lit for the link. it was very informative. but i have not seen any storage tanks havin arrestors over the roof may be the provision is at the walls of the dyke farm area. anyways thanks again.

__________________
Varun Passi
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3
In reply to #2

Re: Lightning Arrestors

04/21/2011 1:10 AM

You then will need to have a chat with the lightning protection vendors especially in oil and gas field to have a clearer view on this.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #3

Re: Lightning Arrestors

04/21/2011 2:14 AM

The whole structure can be used as a lightning arrestor as we did with Cold Box. But if the tank has the instruments mounted around on it wall. It should have an arrestor.

Your second comment reminds me about the answer of my question. If we drop a lit cigarette into a bowl of petrol, the petrol will distinguish it. But if it lights the vapor before it hits the liquid...

Does it light up something?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Commentator
India - Member - Mechanical Engineer Engineering Fields - Petroleum Engineering - Mechanical Engineer

Join Date: Jun 2009
Location: Chennai (India)
Posts: 92
Good Answers: 2
#5
In reply to #4

Re: Lightning Arrestors

04/21/2011 5:12 AM

i do accpet the provision to be compulsory, as there are codes which describes the designing n other aspects like NFPA 780, but none of the storage tank design codes indicate the need and the location of these arrestors. this makes it very difficult for us to ask the vendor with out any proper basis. anyways thanks for the info.

__________________
Varun Passi
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#8
In reply to #5

Re: Lightning Arrestors

04/21/2011 10:33 AM

Several standards will just focus on materials or on how to erect the tank correctly because it is availabe other standards for protection. You should have a look at some additional standards like API RP 545 (Recommended Practice for Lightning Protection of Aboveground Storage Tanks for Flammable or Combustible Liquids) which will tell us how to protect the tank after we installed it.

If you have never seen any arrester on the top of tank, it is OK because it depends on what method of lightning protection being used.

We used to have problem with Cold box (CB) lightning protection, the CB was about 25m high and when we asked the supplier if it needs lightning protection? They said, no because the CB itself was an arrester. But month later, it was struck by the lightning. Yes, the CB is Ok but all the instrumentation was broken. Now, who can we blame? The designer said it is ok but the instrument manual said the instruments need protection.

Just go back and ask the tank maker or designer for this. I am sure that they will have the answer.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#6
In reply to #3

Re: Lightning Arrestors

04/21/2011 9:46 AM

deleted--comment made to the wrong post

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#7
In reply to #1

Re: Lightning Arrestors

04/21/2011 9:57 AM

As hien.nguyenquoc says, the tank will need lightning protection. It may be provided by means other than commercial lightning arrestors, but you may need lightning arrestors to protect instrumentation on the tank.

If you need to buy commercial lightning arrestors, review the following posts and avoid the products mentioned:

  • http://cr4.globalspec.com/comment/709103
  • http://cr4.globalspec.com/comment/667868
  • http://cr4.globalspec.com/comment/676167
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#9
In reply to #7

Re: Lightning Arrestors

04/21/2011 12:51 PM

Well, finally, this is what APR RP 545 says:

1. Install submerged shunts between the roof and shell every three meters around the roof perimeter, and remove any existing above-seal shunts.

2. Electrically insulate all seal assembly components (including springs, scissor assemblies and seal membranes) and all gauge and guide poles, from the tank roof.

This is submerged shunt:

__________________
Anything that can go wrong, will go wrong