Transmitter indication problem

04/19/2011 12:45 PM

I am working on a Dp transmitter, have checked the under pressure zero their was a difference of +2" H2O but when depressurized it, found -2" H2O. Apply zero Trim, but when checked the under pressure zero that was 9" H2O. Checked the static pressure of transmitter while it is depressurized it was Reading 4 PSi, any One can tell me what could be the reason of it and what should i do to resolve this problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Transmitter indication problem

04/19/2011 3:44 PM

What position are the isolation and bleed valves in?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#2

Re: Transmitter indication problem

04/22/2011 9:06 PM

Hi, MKashi

to resolve your issue, need this details

What is the range of the dp xtmrs, elevation, and the type of measurement is it dp level, dp flow, dp pressure.

Regard's

Register to Reply
Participant

Join Date: Apr 2011
Posts: 3
#3
In reply to #2

Re: Transmitter indication problem

04/22/2011 11:17 PM

transmitter is measuring flow of syn Gas and its range is

0-200"wc

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#4

Re: Transmitter indication problem

04/23/2011 11:53 AM

>have checked the under pressure zero their was a difference of +2" H2O

What does "the under pressure zero" mean ? What state are your various valves in to get zero pressure?

How could there be zero pressure at both ports if you have not yet blocked both line valves and opened the equalizer valve, (which appears to be your next step)?

>but when depressurized it, found -2" H2O.

The 3 valve manifolds typically used with DP transmitters do not 'depressurize'. The equalizer valve equalizes the pressure between the high side and the low side so that there is no differential pressure, hence the zero (under those conditions) should be 0.00" differential. There might well be static pressure on both ports at that time.

When you say 'depressurize', is some port open to atmosphere, or is 'depressureize' your word for 'equalized' pressure?

>Apply zero Trim, but when checked the under pressure zero that was 9" H2O.

That sounds like you used a HART or keypad function to correct the -2" H2O to 0.0" H2O.

What isn't clear is what state the transmitter and valves are in when you 'checked the under pressure zero'. What steps do you take to achieve conditions of 'under pressure zero'?

>Checked the static pressure of transmitter while it is depressurized it was Reading 4 PSi.

It is somewhat disconcerting to change engineering units from inches water column to PSI. Are you re-configuring the transmitter to read its local display in two different eng units? Or how does it work to get both inches water and PSI ?

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#5

Re: Transmitter indication problem

04/24/2011 5:00 PM

do a calibration on the transmitter, by following your cal. procedure you will understand your transmitter better and hopefully you can fix your problem

Register to Reply
Register to Reply 5 comments