Circuit Breaker in Switchgear Panels

04/21/2011 3:33 AM

why only one trip coil in switchgear panels is present in their circuit breaker??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Apr 2011
Location: Abu Dhabi, UAE
Posts: 25
Good Answers: 2
#1

Re: circuit breaker in switchgear panels

04/21/2011 6:05 AM

You can connect all the trip commands in parallel and activate one trip coil. if your application demands additional trip coil to improve the reliability, contact the manufacturer. Additional trip coil can be mounted on the breaker upon ordering.

Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#2

Re: circuit breaker in switchgear panels

04/21/2011 8:00 AM

for the reliablity pupose you can use AC & DC trip coil . which is depends upon the user.

__________________
Knowledge Sharing
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: circuit breaker in switchgear panels

04/21/2011 11:09 AM

Strange thing is you'll find a lot of manufacturers will fit rectifiers to AC trip circuits and use DC coils.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Circuit Breaker in Switchgear Panels

04/21/2011 11:39 AM

why only one trip coil in switchgear panels is present in their circuit breaker??

(1) There are many switchboards with one main incomer CB and many outgoing CBs. Each CB will have its own protection scheme, depending on the kind of discrimination system preferred.

(2) There are mainly three kinds of trip coils: Shunt trip coils and undervoltage releases, and the trip coil of the protective relay if it is built into the CB. The trend nowadays is to use microprocessor based relays with their own low-energy trip coil (self-powered and not dependent on aux power). In most CBs, all three are provided in my experience.

However, as pravinba says, one can parallel all trip commands and use one coil only. Makes one dependant on aux supply.

DC is generally used since in critical power stations, battery banks are provided for reliable aux supply.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Circuit Breaker in Switchgear Panels

04/25/2011 7:38 AM

Elementary, Dr. Watson! Economy! There is nothing wrong in going for 100% redundancy, in breaker trip coils, if the application is critical. I have come across two trip coils PER POLE in all EHT Circuit Breakers that I have commissioned. The trip supplies, the cables, the cable routes - all will be seperate & different.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers: