If the electrical system having number of motor loads where protecting devices like MCB, Contactor and Overload relays are used for protecting purposes. In this case how to calculate kVA rating for control transformer(415/230V) which is used to supply a control voltage of 230v to lamps and push buttons. I need this information for designing in plc based mcc control panel.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: How to calculate kVA rating of control transformer

04/21/2011 12:33 PM

Find out the VA ratings of all devices that will be powered from the control transformer (PLC, computer, accessories; solenoids, relays; motor starter coils and other contactor coils; etc.) Add them all up and then multiply by a service/safety factor of 1.25 (or whatever the local code may dictate).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#7
In reply to #1

Re: How to calculate kVA rating of control transformer

04/25/2011 9:48 AM

Dear,

It is true that totalling the KVA ratings of all control devices may not be the same as total KVA load on the transformer. Since, it is the vectorial sum of KVA ( not a scalar quantity ) Infact, you need a smaller size of X'mer by about 0.83 times the total sum of all KVA

But, it is equally true that if you total the KVA of all devices, then, derating & safety factor is also considered in it, you may go very safely with the total sum of KVA to select the Control Transformer size.

__________________
Exploring the Science of Electricity
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: How to Calculate kVA Rating of Control Transformer

04/21/2011 4:54 PM

Sorry but have I got this right?
Your designing a PLC controlled MCC panel and yet have to ask the most basic question of total strangers on an internet site?

Pure fantasy!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#4
In reply to #2

Re: How to Calculate kVA Rating of Control Transformer

04/22/2011 12:38 AM

Tony, the mind boggles..

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: How to Calculate kVA Rating of Control Transformer

04/22/2011 12:08 AM

If the contactor coils are also supplied by the control transformer, the sizing is a more complex exercise due to high inrush VA. To get some idea of what is involved, please download and study this document : http://samplecode.rockwellautomation.com/idc/groups/literature/documents/wp/1497-wp001_-en-p.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#5

Re: How to Calculate kVA Rating of Control Transformer

04/22/2011 8:27 AM

You must be knowing voltage requirement and frequency for the circuit. Inrush current you have to findout for selecting the KVA rating.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: How to Calculate kVA Rating of Control Transformer

04/22/2011 4:45 PM

Maybe I'm overstating the obvious, but if you have 415/230V available, why would you need a control power transformer to get 230V control power? Why not just tap off of one phase with a fuse and connect the other side of your control circuits to Neutral?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**