Power Factor & Generator...

04/23/2011 12:50 AM

Dear friends,

I have one small doubt..,

Power factor depends on type of load used, correct..?

If correct, why manufacturer of A.C generators mention power output in Watts....?

With regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#1

Re: power factor & generator...

04/23/2011 5:49 AM

Then they will also provide power factor and efficiency for customer's estimation.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#2
In reply to #1

Re: power factor & generator...

04/23/2011 6:11 AM

Normally rating of power supply source is expressed in KVA. If someone expresses in KW then he must also express that what power factor should be to get that power.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#3

Re: power factor & generator...

04/23/2011 6:12 AM

There is actual load and indicated load. generators are rated at actual capability.

Regards JD.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#4

Re: power factor & generator...

04/23/2011 7:06 AM

dear,

Function of Generator is to provide 2 out puts - (1) Voltage & Current - By alternator

(2) Electrical Energy / power - i.e. KW

by Engine - mechanical energy in to electrical enegy by engine.

Function (1) is expressed in KVA, where Power factor is mentioned @ KW

Function (2) is expressed in KW as usal

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#5

Re: Power Factor & Generator...

04/23/2011 10:20 AM

Re: Power factor depends on type of load used, correct..?

Yes

Re: If correct, why manufacturer of A.C generators mention power output in Watts....?

I think most consumers are more used to and capable of considering the load they have to power in terms of watts.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: Power Factor & Generator...

04/23/2011 5:34 PM

Dear friend ,

Your answer is already available in your question. They specify the KW to choose the correct KW capacity generator depending up on the actual power factor of your load. To make it more clear the designer should consider the actual power factor of the load to select the correct KW and KVA rating of the generator

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Power Factor & Generator...

04/25/2011 7:10 AM

So that you don't overload the prime mover - which is always rated at HP or Watts.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2011
Posts: 99
#8

Re: Power Factor & Generator...

04/27/2011 4:24 AM

http://www.generatorguide.net/watt-acpower.html

I am not a big expert but KVA would be more accurate and fair if you ask me. I can see most of the manufacturers use KVA on their new products instead of simple KW as before. KW refers only for a linear loads while KVA is more "dynamic" and includes power factor in the math. Simply, if the Power Factor φ=1 → KW=KVA. I hope the explanation above will help.

regards

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); harry potter (1); hien.nguyenquoc (1); jdretired (1); Mishel (1); rhkramer (1); Signode (1); V.I.Abraham (1)