10 comments
Rate Comments: Nested
Active Contributor

Join Date: Jun 2010
Location: zaria nigeria
Posts: 12

1083KVA Generator Speed & Freq. Problem

04/25/2011 1:35 PM

Hi All,

We have two newly installed Perkins dg each rated at 1083 kva. The problem is they failed to run at rated speed of 1500rpm and of course rated frequency of 49-52 hz.(name plate declarations) The variable potentiometer for speed adjust on the Gen was varied to increase speed to 1500 but the max. attained with a digital tachometer was 1320rpm and freq reading was 41hz for both Gen-sets.The Gen-sets were to be paralleled using a µprocessor controlled GENSYS synchronizing/load transfer panel already installed with one Gen as master and the other as slave.The load transfer breaker trips immediately any motor is started (even as small as a 5.5kw induction motor) except for lighting loads.We have motors ranging from 750w to 400kw.

Question:Why is the shaft speed less than 1500rpm?

:what could be holding down the speed command signal thus making

the speed adjust pot on gen AVR panel useless?

:expectation is that shaft speed could be raised/lowered with genset

independent of the load xfer panel, Right?

:could it be a defect from manufacturer?

All these problems cropped up during commissioning. Looking forward to

solutions. Thanks

__________________
r4roty
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: 1083KVA GENERATOR SPEED & FREQ. PROBLEM.

04/25/2011 2:12 PM

Sounds like dirty fuel or filter, a constriction in the fuel supply piping, or the governor system took a nasty hit somewhere in transit and the linkage has jammed. If the symptoms are identical on both units then you have to look at things that are common to both; i.e., the fuel system and/or the synchronizing system. Since they're brand new it's time to get the supplier/manufacturer involved.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#2

Re: 1083KVA Generator Speed & Freq. Problem

04/25/2011 11:27 PM

You seem to have neglected the initial primming requirements the same should have been clear to you if you had thoroughly read the commissioning manual from the manufacturer.

Initially you have to turn open the bleed valves located at different points in the fuel piping at the engine in order to release the air in the fuel piping so that diesel occupies all the space.

For the engine lube oil to run through you will have to crank the engine by using a screw driver at two of the starter motor terminals specified by the manufacturer.

Re-work following the commissioning instructions from the manufacturer.

Register to Reply
Active Contributor

Join Date: Jun 2010
Location: zaria nigeria
Posts: 12
#5
In reply to #2

Re: 1083KVA Generator Speed & Freq. Problem

04/26/2011 10:20 AM

"you will have to crank the engine by using a screw driver at two of the starter motor terminals"

I read your comments, but the engine can be cranked by pressing the start button on the GENSYS panel.Since there are two starter motors for the engine,it might be a difficult procedure which in the end could damage the starter in the process!thanks your comment is noted.

__________________
r4roty
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#7
In reply to #5

Re: 1083KVA Generator Speed & Freq. Problem

04/26/2011 11:31 PM

Don't dismiss the they may just need proper bleeding part of the comment, just because of a fairly common 'bush mechanics' practice - when lacking a helper or a remote switch.

But as they do run, you can bleed at the injectors (at idle), which with some fuel systems, is about the only way to get all the air out.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #2

Re: 1083KVA Generator Speed & Freq. Problem

04/26/2011 1:17 PM

I could think of better ways of ruining a screwdriver.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: 1083KVA Generator Speed & Freq. Problem

04/26/2011 1:47 AM

Why did you accept the generators when they didn't come up to design specification? Get the commissioning team back.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Apr 2011
Location: Abu Dhabi, UAE
Posts: 25
Good Answers: 2
#4

Re: 1083KVA Generator Speed & Freq. Problem

04/26/2011 4:36 AM

DG set Governor has " maximum speed set point " by mechanical means. May be your DG sets have been commissioned during testing using a defective Tachometer. They should have cross checked the tachometer reading with the frequency meter.

since both the DG sets have the same problem, it could be a wrongly set " max speed "

Check the fuel filters as pointed out by many experts. It seems that your generators do not have under- frequency protection.

Try to find out by what means the speed is adjusted by varying the potentiometer. There can be some mis-match in the mechanism involved.

Register to Reply
Participant

Join Date: Mar 2011
Posts: 4
#8

Re: 1083KVA Generator Speed & Freq. Problem

04/27/2011 7:17 AM

hey,

first of all check both dg sets one by one idle condition by disconnecting all signals between them (like as synchronouzing & load sharing etc) and lets check the RPM condition @ idle mode, then put on load and lets see what will happen.

Register to Reply
Active Contributor

Join Date: Jun 2010
Location: zaria nigeria
Posts: 12
#9
In reply to #8

Re: 1083KVA Generator Speed & Freq. Problem

04/27/2011 7:46 AM

We checked all these at pre commisioning stage, the generated outputs were less than 400V. We believe if we can get the speed to 1500 every essential parameters will fall in place. At the moment, we are re-working the commissioning procedures taking into cognizance all suggestions by respondents to this thread. Thanks for your inputs

__________________
r4roty
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#10
In reply to #9

Re: 1083KVA Generator Speed & Freq. Problem

05/10/2011 1:09 AM

Hi,

Simplify the problem, the engine or electrical. On engine you may check fuel system fuel line, pump and injector. assume no problem on your fuel line, may be on electrical actuator inside pump, could be dirty, stuck, high impendance, try to compare the data you checked with the manual. In electrical, may be you have different read between on controller and actual, this sometime happend on new set, you could callibrate the reading on it...pls get back if this result ok in your set

__________________
One system
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); A.A.Khi (1); loadshare (1); pravinba (1); r4roty (2); RAMConsult (1); SUKKR (1); TonyS (2)