04/25/2011 1:35 PM
Hi All,
We have two newly installed Perkins dg each rated at 1083 kva. The problem is they failed to run at rated speed of 1500rpm and of course rated frequency of 49-52 hz.(name plate declarations) The variable potentiometer for speed adjust on the Gen was varied to increase speed to 1500 but the max. attained with a digital tachometer was 1320rpm and freq reading was 41hz for both Gen-sets.The Gen-sets were to be paralleled using a µprocessor controlled GENSYS synchronizing/load transfer panel already installed with one Gen as master and the other as slave.The load transfer breaker trips immediately any motor is started (even as small as a 5.5kw induction motor) except for lighting loads.We have motors ranging from 750w to 400kw.
Question:Why is the shaft speed less than 1500rpm?
:what could be holding down the speed command signal thus making
the speed adjust pot on gen AVR panel useless?
:expectation is that shaft speed could be raised/lowered with genset
independent of the load xfer panel, Right?
:could it be a defect from manufacturer?
All these problems cropped up during commissioning. Looking forward to
solutions. Thanks
r4roty
Good Answers: 445
Re: 1083KVA GENERATOR SPEED & FREQ. PROBLEM.
04/25/2011 2:12 PM
Sounds like dirty fuel or filter, a constriction in the fuel supply piping, or the governor system took a nasty hit somewhere in transit and the linkage has jammed. If the symptoms are identical on both units then you have to look at things that are common to both; i.e., the fuel system and/or the synchronizing system. Since they're brand new it's time to get the supplier/manufacturer involved.
Re: 1083KVA Generator Speed & Freq. Problem
04/25/2011 11:27 PM
You seem to have neglected the initial primming requirements the same should have been clear to you if you had thoroughly read the commissioning manual from the manufacturer.
Initially you have to turn open the bleed valves located at different points in the fuel piping at the engine in order to release the air in the fuel piping so that diesel occupies all the space.
For the engine lube oil to run through you will have to crank the engine by using a screw driver at two of the starter motor terminals specified by the manufacturer.
Re-work following the commissioning instructions from the manufacturer.
04/26/2011 10:20 AM
"you will have to crank the engine by using a screw driver at two of the starter motor terminals"
I read your comments, but the engine can be cranked by pressing the start button on the GENSYS panel.Since there are two starter motors for the engine,it might be a difficult procedure which in the end could damage the starter in the process!thanks your comment is noted.
r4roty
Good Answers: 130
04/26/2011 11:31 PM
Don't dismiss the they may just need proper bleeding part of the comment, just because of a fairly common 'bush mechanics' practice - when lacking a helper or a remote switch.
But as they do run, you can bleed at the injectors (at idle), which with some fuel systems, is about the only way to get all the air out.
Good Answers: 181
04/26/2011 1:17 PM
I could think of better ways of ruining a screwdriver.
Good Answers: 181
04/26/2011 1:47 AM
Why did you accept the generators when they didn't come up to design specification? Get the commissioning team back.
04/26/2011 4:36 AM
DG set Governor has " maximum speed set point " by mechanical means. May be your DG sets have been commissioned during testing using a defective Tachometer. They should have cross checked the tachometer reading with the frequency meter.
since both the DG sets have the same problem, it could be a wrongly set " max speed "
Check the fuel filters as pointed out by many experts. It seems that your generators do not have under- frequency protection.
Try to find out by what means the speed is adjusted by varying the potentiometer. There can be some mis-match in the mechanism involved.
04/27/2011 7:17 AM
hey,
first of all check both dg sets one by one idle condition by disconnecting all signals between them (like as synchronouzing & load sharing etc) and lets check the RPM condition @ idle mode, then put on load and lets see what will happen.
04/27/2011 7:46 AM
We checked all these at pre commisioning stage, the generated outputs were less than 400V. We believe if we can get the speed to 1500 every essential parameters will fall in place. At the moment, we are re-working the commissioning procedures taking into cognizance all suggestions by respondents to this thread. Thanks for your inputs
r4roty
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member
05/10/2011 1:09 AM
Hi,
Simplify the problem, the engine or electrical. On engine you may check fuel system fuel line, pump and injector. assume no problem on your fuel line, may be on electrical actuator inside pump, could be dirty, stuck, high impendance, try to compare the data you checked with the manual. In electrical, may be you have different read between on controller and actual, this sometime happend on new set, you could callibrate the reading on it...pls get back if this result ok in your set