Inrush Current Issue

04/28/2011 12:57 AM

Hi all,

We have project 4 sets 4 x 1250 kVA/380VAC parallel and all come into a MV Trafo 5000 kVA/400-4,1 kV/star-delta. The issue is when the load is very small eg. 100 kVA, so only 1 set need to run, many consultant ask about inrush current that will happend when the set come online and take a load.

Thank you in advance

__________________
One system
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Inrush current issue

04/28/2011 3:59 AM

? ? ? ? ? ? ?

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#2
In reply to #1

Re: Inrush current issue

04/28/2011 5:12 AM

From your experience, if inrush current occur how big is the current effect on system and set ? and how to solve ?

__________________
One system
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3
In reply to #2

Re: Inrush current issue

04/28/2011 5:40 AM

Why you want to connect 4 sets of 1250kvA transformers in parallel to one 5000kVA transformer? Is that your homework or imagination?

How you can start a project where you cannot use correctly the transformer terminologies?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#4
In reply to #3

Re: Inrush current issue

04/28/2011 6:01 AM

Hi Hien,

4 x 1250 sets are parallel with others and main outgoing sets breaker connected to MV trafo (detail above), in case of customer out of production they just need to run 1 set to cover light and data center. With do respect on you, I did not imagine or doing home work. If you have an experience or deep analyze you could share. Im only technician, have not good knowledge as you and other. But I'd like to learn from you the expert. OK

Thanks 4 ur respond anyway

__________________
One system
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#5
In reply to #4

Re: Inrush current issue

04/28/2011 6:42 AM

Sorry, I still cannot understand this application.

"4 x 1250 sets are parallel with others and main outgoing sets breaker connected to MV trafo." Does trafo mean transformer? I still don't understand why you connect 4 in parallel then their outgoing is connected to one 5000 kVA transformer? It means you have 5 transformers (1 connects in series with 4)?

So, you will have 4 separated incoming breakers for those transformer?

Thank you if you could enlighten me.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6
In reply to #5

Re: Inrush current issue

04/28/2011 7:05 AM

The purpose of transformer parallel connection, is to increase the loading capacity while replacing the existing transformer is impossible.

Operating-in-parallel means that these transformer shall operate at the same time. With one breaker at the outgoing, you will not be able to eliminate one or two transformer to save the operation cost? You kow why?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Jun 2010
Location: zaria nigeria
Posts: 12
#22
In reply to #5

Re: Inrush current issue

04/29/2011 5:33 PM

Sorry this application is very clear: 4no. 1250 KVA generators with individual outputs of 380 volts are connected in parallel and the output from the load transfer breaker (switch) is fed to a 5MVA MV step up trafo (transformer) with primary input of 380V and secondary output of 4.1KV .As you can see, there is only one trafo and four gen-sets NOT 5 transformers!

__________________
r4roty
Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#23
In reply to #22

Re: Inrush current issue

04/30/2011 2:28 AM

Hi Roty.

If you stop and look at the diagram you will understand it is not clear at all. For example there are 3 gensets, not 4.

The secondary output is 20kV not 4.1kV.

The ATS is across the 20kV side thus RAM, Hien and I suspect this is where the issue is.

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#7

Re: Inrush Current Issue

04/28/2011 9:30 AM

Are the "4 sets 4 x 1250 kVA/380VAC" in parallel transformers or generators?

At what point do you want to know the inrush current?

Register to Reply
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#8

Re: Inrush Current Issue

04/28/2011 10:19 AM

I think a clear explanation (or a single-line diagram!) of your system would help the discussion. What I have been able to guess from your description is you have a 5000kVA transformer (4.1kV - 400V?) feeding four distribution transformers of 1250kVA each at 380V. Only one of these operates continuously, for lights & data, at about 100kVA load. The others are only turned on when customer production equipment operation demand it. Someone is concerned what inrush current will do when one of the additional loads is turned on. Is that a fair description?

I don't think you have any problem here. The 5000kVA should be able to carry the combined continuous load of the 4 x 1250kVA transformers. Transformer inrush current is up to 10x or so full load amps (FLA), but that only lasts about 0.1 second. There may be minor heating of the conductors, but that will dissipate. You need to make sure any overcurrent relay or circuit breaker trip unit settings are set to ride out the inrush. The other consideration is that the distribution feeders are not coming on at full load, but rather are switched on and then their loads are turned on. That gradually brings in the continuous loads.

In the event of 3 units running and the 4th coming on line, unless the first 3 are all fully loaded at 1250kVA (and most installations are not such), you won't be loading the main transformer to its nameplate anyway.

Hope that helps. Good luck!

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 3)
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Inrush Current Issue

04/28/2011 12:24 PM

As I understand it, OP has four generator sets all tied to a single bus that feeds plant loads through a single transformer. His question is basically can a single generator pick up suddenly applied high inrush current loads when the generator is lightly loaded. The answer is that it depends on the nature of the loads. If they're chosen wisely and sequenced properly then no problem, but if it's possible that they can be applied all at once or at random then the inrush currents can far exceed a single generator's short term rating, then no way. Designing an isolated system requires more than just having switchgear and generator sets.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #9

Re: Inrush Current Issue

04/28/2011 9:22 PM

Thank you for your cue, Ram. This now comes out as an interesting question.

So, the customer wants to save fuel of gensets when there are only light loads switched on.

I don't know much about how the inrush current will affect to genset in this application but to mitigate the inrush current in this case, I think, we should switch on one breaker to this 5MVA transformer prior to starting up genset. This operation will reduce dramatically the inrush current since the genset takes time to build up the voltage.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13
In reply to #10

Re: Inrush Current Issue

04/29/2011 12:02 AM

The nature of the loads creating the inrush current is the real problem. Not only does the type of motor (synchronous, induction) matter so does the nature of the load being driven (high torque, low torque, pulsing, non-linear, etc.) along with any speed control, starting control, etc. Closing the breaker and waiting for the generator to build up voltage can cause problems like motors going subsynchronous and never reaching full speed and/or drawing excessive currents during speed ramp up.

Best bet would be to bring the diesel up to speed and voltage then close the breaker, letting the governor and AVR correct for the inrush.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#12
In reply to #9

Re: Inrush Current Issue

04/28/2011 11:09 PM

Hi RAM,

Yes, the load will be randomly. I ve experience like this case too but haven't solve yet and now facing same project. From last of my experience, we've manage the load, so when black start happen, the sets not suddenly take all the load but arrange sequentially but then this way wasn't solve the problem, the main breaker at outgoing trafo keep tripping

__________________
One system
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#11

Re: Inrush Current Issue

04/28/2011 10:54 PM

Hi All,

Thanks for your responds, here I provide you snapshot of single diagram.

__________________
One system
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14
In reply to #11

Re: Inrush Current Issue

04/29/2011 12:16 AM

Thanks! I assume that you have some form of synchronization and interconnected speed and voltage control to ensure proper load balancing and var control as well.

As far as the breaker tripping I suspect one of your loads is an across the line synchronous motor driving a high starting torque load whose running kw is more than 25-50% of a single diesel's rating. Please let us know.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#15
In reply to #14

Re: Inrush Current Issue

04/29/2011 2:51 AM

Ram, it should be asynchronous rather then synchronous, am I correct?

For the main outgoing breaker tripping, when you bring the generator online, it should be sure that the phase is synchronized with each other in term of frequency and phase and the main incoming switchgear to tranfo shall be the appropriate one which can handle this out-of-phase current.

For the SLD, looking for the genset side, there is small issue that the configuration should be 0.4/29kV instead.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#20
In reply to #15

Re: Inrush Current Issue

04/29/2011 10:38 AM

Hien, We're talking two different things (types of motors vs. how to connect to a grid) but you bring up an interesting point which OP didn't mention, that there is an external connection on the other side of the transformer. Unfortunately I could not read the fine print on the SLD. Using the recent comments from others it appears that there is a connection to another source of generation. Judging from what I've read so far it appears that there is no attempt at synchronizing the local generation to the utility, just close the generator bus breaker and of course watch the transformer trip out on the huge currents from out of phase/mismatched voltage synchronization. Op is one lucky guy that the only thing that happened was the breaker tripped.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#17
In reply to #11

Re: Inrush Current Issue

04/29/2011 4:56 AM

Hi Loadshare,

So we all understand this better, can you show us the diagram of the ATS please.

It looks like the ATS has PLN (Indonesian Power) incoming to ATS @ 20kV then you have another 20kV travo on the client side. Is this correct?

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#18
In reply to #17

Re: Inrush Current Issue

04/29/2011 6:03 AM

Hi Tamu,

Correct, another trafo at distribution.

__________________
One system
Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#19
In reply to #18

Re: Inrush Current Issue

04/29/2011 6:10 AM

Can we please see the diagram of the complete ATS system?

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#16

Re: Inrush Current Issue

04/29/2011 3:24 AM

Hi,

RAM, we already try to isolated the load. Vendor of trafo said cause of tripping breaker is inrush current present on system, solution is the sets all run together till main generator breaker closed and load, then one by one manually switch off the set. here is good link for calculating IC http://www.bambangdjaja.com/index.php?option=com_content&task=view&id=22&Itemid=34 , but again im still curious. Does IC happen only on power source trafo or sum with distribution trafo ?

__________________
One system
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#21
In reply to #16

Re: Inrush Current Issue

04/29/2011 11:04 AM

Hi, Please read my earlier post to Hien, where I explained that I'm getting the feeling that you're trying to simply close the generator breaker into the transformer when the high side is energized by another source. Please tell me I'm wrong and that if you are doing that you are synchronizing properly.

Assuming I'm wrong above and that you are indeed operating an isolated system, then the strategy of having all generation online and operating through some form of load-sharing/VAR-sharing master controller should allow you to randomly apply load, but, and it's a big but, if too many really big high inertia loads just happen to start simultaneously, you are going to trip the breaker because your prime movers lack sufficient inertia to overcome the loads and/or your excitation system lacks sufficient field forcing capability to maintain the terminal voltage at the motors, either of which has the potential to lead to high currents through the breaker as the motors start too slowly and/or fail to come up to speed before the current dies down below the breaker trip level.

One more thing, you still haven't revealed the nature of your loads, that would help everybody tremendously...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
3
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#24

Re: Inrush Current Issue

04/30/2011 2:42 PM

Hi loadshare, after you read this response to your post, go to the link and read the paper on this issue that we put out years ago. You might also find it helpful to register with ASCOapu.com, go to the menu tab INSIGHTS, and then to ASCO facts. Good info on switching and gens to be had there. We've been at this over 100 years.
http://www.ascoapu.com/pods/asco/vids/ASCO_Facts-Switching_Transformers-4032.pdf

By your description here of your system, assuming there are no actual faults, design errors, or smoke getting free, it is very likely you are experiencing transformer magnetizing inrush. This actually is a very common issue but it can be a bit frustrating. Magnetizing current can be 8x to 12x of FLA. It doesn't matter how long that 5MVA xfmr is de-energized, a minute or a month, it will experience a magnetizing inrush to overcome the residual core magnetism and it isn't just that xfmr, it's all of them between the source and the loads. We usually can get past this by simply making sure the breakers aren't using instantaneous trip and then be smart about the short delay settings. How stiff the source is can also be a factor.
I've lost track of how many times I've had this discussion with consulting engineers when they've installed a simple 400amp ATS with a 75kva xfmr on it. The feeder breaker trips on transfer and they are frustrated and wanting to blame something. I've even had guys arguing that the in-phase monitor has to have failed, even as they are watching a meter swing to zero. Also note that very lightly loaded transformers or ones with no load definitely hit harder.

In your system you also have an issue with the fact that the transformers could potentially slam individual generators. The total VA can exceed a single units capacity and with systems like this, depending on how tight the protective scheme is and the type of regulators, can even cause a gen to fault because of the wicked reactive starting current. This is usually made even worse by the way we do gen control systems. Typically in standby parallel controls, the first gen to make the threshold for volt and speed closes to the bus and is actually still spinning up when that big reactive inrush hits it. The next closest gen that has grabbed the sync line can actually close in during this hit and they both blow off-line. This is also one of those 'been there - seen that' things. 99% of the time the easiest ways to deal with this at the gens is to modify the control scheme so that the outgoing switchgear main breaker is opened until your gens are on and paralleled, and then close all gens to the load in order to have capacity to take the hit. You have not said whether you are under any regulations covering time-to-restore power but if the gens are in good shape and the controls are adjusted properly it is very easy to meet the 10sec life safety code like this. After closing the main then one uses a simple load scheme to control stopping of generators down to whatever capacity you need. This, coupled with smart choices in circuit breaker trip units and settings, is really about all you can do.

Rest assured your issue is actually quite common but the only thing anyone in a forum of this nature can offer is a bit of experience and insight. There are some very experienced people here though that like to help. Please come back on this and let us all know how you make out, since we're all here because we really enjoy this sort of thing and it's cool when we get some follow up.

Good luck

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#25
In reply to #24

Re: Inrush Current Issue

04/30/2011 2:50 PM

Loadshare,

Another thought to add to this... at your ATS you can add a second or two of delay to transfer to the gen bus. This will allow the gens to take the inrush hit of that 5MVA transformer, delay for few cycles to let them to settle in and then roll over and energize the downstream loads.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#26
In reply to #25

Re: Inrush Current Issue

04/30/2011 9:57 PM

Actually, this application is clear in term of concept. But the OP, same as many others, still has not described enough what he has been looking for and dealing with.

All the thing here is just to focus on inrush current and it seems that this is the only challenge from the consultant.

I think that, one again, this application is popular and the best way is to consult the supplier of genset. Until now, we also don't know why his consultants said about the inrush current?

The problem, for nothing, possibly, may be not just inrush current.

This is just my curiosity, what does Loadshare mean?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#27

Re: Inrush Current Issue

05/03/2011 10:15 PM

Hi All,

Thank for you respond and explanation, I do appreciate.

On start discussion, I made a simple example which similar to the actual in order to make easier to understand.

@Hien: Purpose I ask about inrush current, because the distributor of transformer said no inrush current then I remember on my previous project, it exist even at no load. And I'm looking for advise from this forum regarding this. Also this is AMF/TS

@RAM: Yes, sets synchronizing and close its CB and step up to the transformer, its simple

@Switchman: you mentioned to make sure the breaker doesnt use instantenous trip. So in my head there will be a LBS but I think its dangerous because no protection or could you please advise me what kind of breaker that doesnt use IT ?.

@Tamu: OK, I will provide you the missing part of diagram

So, at temperory result, if Im not wrong:

Transformer step up 0,4/20 kV 5000 kVA In primary = 7217 amps (possibility I inrush = 10 x 7217 amps)

The sets 400 VAC, 3 x 1406 kVA Ig Total = 6088 amps, Protection over current at set 125 % (t 1 sec) = 1,25 x 6088

Main sets CB In = 6300 Instatenous trip can be set to = 86.000 amp (t 80 ms) and 100 kA for ST

Please, correct me

Thanks

__________________
One system
Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: