Overload Setting

04/27/2011 3:48 PM

what is the appropriate current setting of an overload protector as a percentage of F.L.C

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Overload Setting

04/27/2011 4:12 PM

As stated many times in this forum... such things depend upon the codes in your jurisdiction.

In Canada... the following applies.

CEC rule 28-306 states...

125% for a motor with a service factor of 1.15 or greater

115% for a motor not marked as to service factor or with a service factor less then 1.15

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Overload Setting

04/27/2011 5:26 PM

Most overload relays on the market have the pick-up points already faqctored into their design. You set them for the motor nameplate FLC, nothing else. In the case of NEMA style OL relays with replaceable thermal elements, if you have a motor with a 1.0SF (or unmarked where you must assume as much) then you can select the next size LOWER heater element. That's because with the prevalence of motors having 1.15SF, the 125% is what is built-in to the relay design.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Overload Setting

04/27/2011 10:26 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #3

Re: Overload Setting

04/28/2011 1:22 AM

Most of answers are correct. But it also depends on the application. Some have to set the OL current to 175%.

I have read one manual which I found it was a good guidance especially for small motor application. You set the current at 125% then start up the motor, reduce the setting and restart the motor until it is tripped. Then, try to set it one level higher at the trip point.

By doing this, it will give us a higher safety margin for the motor against OL protection.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Overload Setting

04/28/2011 3:56 AM

OK if you can load the motor 100% for your trials. Not really a practical solution.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: Overload Setting

04/28/2011 8:20 AM

it really depends.... with the motors I use, I wait until the RC (running current) is settled then set the O/L to 115% of RC. However if your motor is 100% loaded you can either set it to 115% or 120% of the NPA (name plate amps).. again educated decision.

Remember the overload is there to protect the motor and equipment.. be careful when making these decisions.

__________________
The square root of nothing is what you make it!
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (1); hien.nguyenquoc (1); JRaef (1); msamad (1); North of 60 (1); TonyS (1)

Previous in Forum: Voltage Drop for Well Pump   Next in Forum: Inrush Current Issue

Advertisement