Voltage Drop for Well Pump

04/27/2011 3:30 PM

I know voltage drop has been kicked around quite a lot, but I would like to get some views on this thought. I'm working on a 1/2 hp pump, 5 amp, single phase, 230v., three wire, 160 ft. in well. Power source is 3300 ft. from well. Just using simple voltage drop calculations and using 7000 ft. of run I figure a #4cu. would work. Now what if I used a couple of 2:1 transformers as a step up and then step down and the motor controller at the well head. The questions are: what size copper wire would work? how does voltage drop affect the primary voltage at the step up transformer? would reactance from the transformers affect the three wire motor controller? should I be looking at starting current instead of FLA, the motor will be starting with quite a load( would the motor ever start with say a #10 cu.) Is there anything else I'm overlooking? Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Voltage Drop for Well Pump

04/27/2011 4:22 PM

With respect to overlooking something... I would say so. The cost of doing what you propose is far greater over the long run then the cost in wire. The energy spent keeping the cores of both tansformers magnetized will eat up many many watts on a full time basis.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#4
In reply to #1

Re: Voltage Drop for Well Pump

04/27/2011 11:05 PM

North of 60,

Thanks for the reply, I left out that the control scheme will be such that the transformers are energized only when the pump is running, and being small transformers, (2kva or less) I believed that cost of electricity would be small compared to cost of copper.

thanks again,

corona

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #4

Re: Voltage Drop for Well Pump

04/27/2011 11:41 PM

Hey...

You mentioned putting the controller at the well head. As such, you would need to leave the circuit energized all the time. Or are you going to use a second starter at the source end that will energize the feeder to the transformer and then send the start signal to the pump? Sounds like this is getting overly complicated for naught.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: Voltage Drop for Well Pump

04/27/2011 5:43 PM

For that sort of distance on the sheep station, we'd run an aerial sub main using cheaper uninsulated conductors and have a switchboard at the pump head.

The once only install cost to "do it properly" (and without complication) by far outweighs the complexity of multiple transformers and such.

Have you considered a solar array or wind turbine with battery storage. I hear there are some pretty attractive subsidues in your part of the world at present for the alternatives.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Voltage Drop for Well Pump

04/27/2011 8:34 PM

"... 160 ft. in well. Power source is 3300 ft. from well. Just using simple voltage drop calculations and using 7000 ft. of run I figure a #4cu. would work...."

Just out of curiosity, how are you getting 7000' from this? Are you thinking you have to count the circuit as a line and return as separate runs? If so, not you don't. It's one drop from source to motor, 3460 feet. 5A at 3460 ft. still comes out as 4AWG for a 4.3% VD, I was just curious why you used 7000'.

10,400' #4 THHN, probably about $1 per foot, $10,400 cost, plus conduit etc.

If you stepped up to 480V 1 phase (because that transformer is easy to buy), you could drop down to 10AWG wire. Two transformers, 1500VA CPTs (easiest to implement and capable of high inrush), including fuses and fuse holders, figure around $250 each, $500. 10,400' #10AWG THHN, probably $0.40/ft, $4,160, plus transformers, $4,660 total.

Less than half the cost using transformers. But you gotta really want that well pump to spend even that much on powering it. I would consider solar for something like that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #3

Re: Voltage Drop for Well Pump

04/27/2011 11:32 PM

Hey there JR... you might want to rethink this. For the VD calc, 7000' is the value of interest. The VD has to be measured on the full circuit length, IE. from the source to the load then back again.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#7
In reply to #3

Re: Voltage Drop for Well Pump

04/28/2011 12:59 AM

JRaef:

I suppose the best way to explain why 7000ft. instead of 3460ft. would be to have you examine Kirchhoff's second law, however your final outcome coincides with my calculations. And your statement about really wanting that pump is also correct, the pump in question is in eastern Washington, dry arid conditions, sometimes water is rare. I haven't considered solar, and I will research this aspect.

Thanks, Corona88

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Voltage Drop for Well Pump

04/28/2011 1:05 AM

You're in great solar country, so that could be a good direction for further research.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: Voltage Drop for Well Pump

04/28/2011 4:05 AM

you are making a simple thing way to complex

I am going to assume(understand) that you have a supply 3000ft away from the switchboard/motor controller which is 230volts.

Look at it this way, look at the NPA (Name Plate Amps) for the motor, also the NPV (Name Plate Voltage). Decide what size of cable (CSA) you require for the NPA, then from a cable chart that will give you the voltage drop per 1000 feet for the cable you require at the NPA, add the NPV and cable voltage drop to give you the required voltage at the switchboard or where the main supply is.

Now if you have a step up or step down transformer, select the closest voltage to that which you have calculated, if you cannot get it exact use the tap setting higher than you require, be careful you do not set the voltage higher that 10% of NPV.

So if you have your supply at 3300 ft plus 160ft well depth. total cable length is 3460 feet, look at the cable chart, it should give you the volts drop per 1000ft at a certain current, in this case 5 amps.. for example 10 volts per 1000ft at 5amps = 32volts±, + NPV of 230 volts = 262 volts at the switch board

As for the motor controller power supply.. find a 0.5Kva multi-tap Primary Tx with 230Volts output for your control voltage

Please forget about the Tx reactance, as for the primary voltage effect on the Tx..you should ensure that the Tx CAN deliver the Kva for the motor you have and the primary supply voltage is beefy enough, that being said.. a 0.5 HP motor is not that heavy a load on a supply, your washing machine motor is probably bigger

AND after all the solutions you get from this forum.. and you are still not sure.. call in someone who knows what they are doing...better safe than sorry eh?

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#10

Re: Voltage Drop for Well Pump

04/28/2011 7:43 AM

I have learnt in past posts that pumps can be operated by remote control through mobile phones. I think that may work out as cheaper option.You may contact pump seller who can help you in this regard.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 3)
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#11
In reply to #10

Re: Voltage Drop for Well Pump

04/28/2011 7:47 AM

have you read the OP?

unless I'm missing the point, I don't think that remote starting of the pump is an issue.. I could be wrong!!

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#13
In reply to #11

Re: Voltage Drop for Well Pump

04/28/2011 8:16 AM

I have read somewhere may be in this forum or in some web site I do not remember. But it was proved to be possible. Some of our experts can through more light on this subject. I have been watching now a days advertisement on TV about Panasonic AC which is controlled from mobile phone, advantage is when reach home in summer it is already cool.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 6)
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#14
In reply to #13

Re: Voltage Drop for Well Pump

04/28/2011 8:24 AM

as you said

I have read somewhere may be in this forum or in some web site I do not remember. But it was proved to be possible. Some of our experts can through more light on this subject.

but this topic is about "voltage drop for well pumps" and NOT "Remote starting of pumps using you cell phone"

Are we clear what the topic is now??

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#16
In reply to #14

Re: Voltage Drop for Well Pump

04/28/2011 9:21 AM

OP is asking for cable size for connecting the pump with starter, I assume that he has not yet installed the pump with long cabling. I have suggested alternative arrangement without using cables. That is the reason I have responded.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#18
In reply to #16

Re: Voltage Drop for Well Pump

04/28/2011 10:02 AM

What the main point of this thread is about is getting power to the pump. Yes, the OP may also want to turn it on and off, but:

  1. the pump may be set up to start and stop automatically based on level in a pond or tank
  2. your suggestion of remote control through mobile phones will not solve the major problem, which is getting power to the pump (you will not get power to the pump through a mobile phone)
  3. he hasn't asked about that (yet)

Once a means of getting power to the pump is established (fairly large long cables, microwave power transmission ;-), local solar or wind generation), the problem of starting and stopping the pumps will be relatively minor. (With large long cables, you can simply power / de-power them at the supply end.)

Register to Reply Off Topic (Score 5)
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#22
In reply to #16

Re: Voltage Drop for Well Pump

04/28/2011 11:22 AM

OP is asking for cable size for connecting the pump with starter, I assume that he has not yet installed the pump with long cabling. I have suggested alternative arrangement without using cables.

so if I understand you.. mobile phones can now POWER submersible pumps from anywhere in the world.

The OP is asking what size cable to supply the pump... not how to control it, that is switch it on and off. So what is your answer to the question.. and to repeat the question.. here it is again..

OP is asking for cable size for connecting the pump with starter.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15
In reply to #13

Re: Voltage Drop for Well Pump

04/28/2011 8:28 AM

hi suresh.. the topic you have mentioned, remote starting of pumps, I have worked closely on for many years and yes, in several topics within CR4 it has been mentioned and we all know it works, but why are you talking about it in this particular forum??

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#17
In reply to #15

Re: Voltage Drop for Well Pump

04/28/2011 9:24 AM

Hi Brich,

Please read my reply above. Can you remember when this topic was discussed in this forum and your experience in this application.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12

Re: Voltage Drop for Well Pump

04/28/2011 7:50 AM

Just curious. Is there any elevation change from the well head to your end use for the water?

Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#19
In reply to #12

Re: Voltage Drop for Well Pump

04/28/2011 10:32 AM

Fredski,

Thanks for viewing and commenting my thread. Yes there is an elevation change, from the well head to the water destination, (which is also the power source) is 3300 ft. run and uphill 80 ft. So from the pump (which is already installed and being run via generator) approx. 240 ft. of head. The system will pump into a cistrern and float switches will control on/off functions.

Thanks again for the look.

Corona

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#20
In reply to #19

Re: Voltage Drop for Well Pump

04/28/2011 11:03 AM

You're really putting this little .5HP motor to work. I'm not completely familiar with your neck of the woods. I was concerned for the possibility of freezing a line that travels over a half mile. I wondered if it was subterranean or surface. I know a lot of people use solar and a storage tank close to the well head. They store 200-300 gallons (make use of the solar when you can even if your home storage is full) and use gravity or a second pump to transport the water to its end point.

I know if this was my project my last choice would be running a 3000' electrical service. I almost certainly would go solar/reservoir. I think once you cost it all out (including service life of your conduit and all the possible scenarios of it being damaged by cars, trucks, vandals, wayward missiles, etc). That's quite a long run! A lot could go wrong.

Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#21
In reply to #20

Re: Voltage Drop for Well Pump

04/28/2011 11:17 AM

and all the possible scenarios of it being damaged by cars, trucks, vandals, wayward missiles, etc).

you have got to be so careful these days.. NATO drop bombs on any damn thing, instead of aiming at Gaddiff!!

Register to Reply Off Topic (Score 5)
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (2); corona88 (3); Fredski (2); JRaef (1); Just an Engineer (1); North of 60 (3); rhkramer (1); suresh sharma (4); thccontrols (4); Tornado (1)