Motors

04/30/2011 9:21 AM

why we use delta connection in motors first

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: motors

04/30/2011 10:06 AM
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Motors

04/30/2011 11:46 AM

We don't - unless we want to blow the fuses. Star first, then delta.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Motors

05/01/2011 1:31 PM

We do when the supply is good. Simple straight forward DOL starting.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Motors

05/02/2011 2:15 AM

Elementary! In delta connection, for the same line current, the windings would carry only the phase current (i.e.) 1/root3 times the line current and hence the heat in the windings would reduce by 3 times (square of the current, i.e. square of root 3). Heat management would be easier.

But, behold! This is true only in case of Low Voltage Motors. In HV Motors, even though the same theory can be applied, the cost of insulation, in case of Delta winding would be much higher. So, in HV motors, the windings are connected is Star.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2010
Posts: 13
#5
In reply to #4

Re: Motors

05/02/2011 5:01 AM

sir i want to say that as we knows the supply comes to us in star usally in pakistan then why we use star-delta starter.if the motor just operate on star then what the effect on system.

Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Motors

05/02/2011 5:55 AM

Well! You need to be explained the whole motor starting theory, indeed! At least are you aware that a motor's starting current is much more than its rated current, when started direct-on-line - typically 6 to 8 times its rated full load current? Now, how do you avoid this high starting current? In delta connected motors, when full line voltage is applied to the motor at the time of starting itself, this full line voltage is also the phase voltage (as it is delta connected) & this full line voltage is the one available to the motor's phase windings. As the applied voltage is high, so also will be the current. There could be problems to the motor as well as to the installation, due to this high starting current. One of the easier ways to reduce this high starting current is to reduce the voltage applied to the windings during starting. In star-delta starter, you do exactly the same thing. That is, when you initially connect the windings in star, the voltage seen by the phase winding of the motor is the phase voltage and not the line voltage. So, as the voltage is reduced so also will be the starting current. But, as the motor picks up its rated speed, it would start delivering Horse Power and please recall that HP or kW = Root3 x V x I x Cos Phi. Now, if you still kepp the motor windings connected in star itself, even after the motor has accelerated to its rated speed, then if the horse power demanded by the load is as per the rating, then as the voltage is only about 57%, going by the above formula, the motor would draw, 1.732 times more current to deliver the required HP. It would overheat & possibly fail. To avoid this, once the motor has picked up speed, the winding connections are changed to delta, wherein the voltage is the line voltage now and thus the 'running' current would be within limits.

Wait! Let me take a deep breath!

Register to Reply Good Answer (Score 2)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); JohnDG (1); lyn (1); rao rizwan (1); TonyS (1)

Previous in Forum: Motor Used In Fans   Next in Forum: Too Many RPM Not Enough Torque...
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement