Rating Current for Switch & Cable

05/02/2011 4:37 AM

1. Ampe rating on switch shows: 16A.

2. Ampe rating on 1.5mm2 cable catalog shows: 19A for underground installation, single core.

My question is:

1. Can I connect this switch to 40x72W fluorescent lamps? Or can I connect to 02x250W sodium lamps?

2. Can I use this cable this for 40x72W florescent lamps? Or just need to keep the voltage drop stayed within the limit?

I mean not to overheat the switch and cable? Is that correct when we can use up to the limit of current stated on switches and sockets? This question seems so stupid but I found several switches were overheated. Is there any tips from the gurus?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Rating current for switch & cable

05/02/2011 5:42 AM

@ 12.5A yes, but with a big BUT. The striking current when 40 lamps turn on at the same time will be X1.8 load. The cable is undersized so you will get appreciable volt drop making starting the lamps worse.

Time for a rethink.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#2
In reply to #1

Re: Rating current for switch & cable

05/02/2011 5:57 AM

So, when the contractor comes to me with an 16A overheated switch which is used for one 250W sodium lamp and said: "This is caused by overload. We must replace the other switching method for lamp".

"You bought the fake one or recheck your connection since the rating showed 16A and how much current will be made by that lamp"? Impossible for that switch to be overheated by the lamp. Correct?

Ok, this is my off-topic.

__________________
Anything that can go wrong, will go wrong
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Rating Current for Switch & Cable

05/02/2011 12:02 PM

The key factor you've omitted is the nominal voltage and phases of your power grid that this switch and cable will be handling. The fluorescent lamps will be drawing nearly 3kW of power. (At a nominal 80 lumen per watt you're at almost a total of 1/4 million lumen. That's a lot of light.) If you have a 120 VAC single phase grid this is an inadequate switch and cable. If the grid is 480 VAC three phase then you will not have to worry about in rush currents.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #3

Re: Rating Current for Switch & Cable

05/02/2011 12:11 PM

Yeah, I know lo of light. Voltage here is 220V.

Normally, we use this switch to control less than 10 sets of 72w lamp. But the reason I post the question here is I want to find the truth behind the current rating given by supplier especially commercial sockets and switches.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Rating Current for Switch & Cable

05/02/2011 1:07 PM

Why didn't you say so in the first place?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6
In reply to #5

Re: Rating Current for Switch & Cable

05/02/2011 8:48 PM

I've noticed that and will do it in the first place. Thank you very much for your suggestion.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Associate

Join Date: Dec 2009
Location: SOUTH AFRICA near the' Cradle of mankind'
Posts: 41
Good Answers: 3
#7

Re: Rating Current for Switch & Cable

05/03/2011 1:55 AM

The 16A switch rating is for a resistive load, but you will be switching a capacitive load which will result in very large inrush currents. This will cause arcing and may result in the switch contacts welding together. My experiance is to use these everyday commercial switchers at about 50% of their rating and this seems to work well.

__________________
The more I practice the luckier I get.(Player)
Register to Reply Score 1 for Good Answer
2
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#8

Re: Rating Current for Switch & Cable

05/03/2011 2:02 AM

Rating a switch at whatever current, is nearly meaningless, Without telling the whole story.

This is the reason why there are electricians, and there are people who know stuff.

The load in your case, with the fluros, is an AC3 load, capacative/inductive. If your switch is rated at 16amp AC3 duty at 240vac, then you are in with half a chance. If you switch the load off and on, say twice a day.

If this switch, say, is being switched off and on every 10 seconds, then please have a bucketfull of switches ready. Because the AC3 load is now doing it, at an AC4 duty.

There are a lot of features, built into a switch to do a particular job.

Even like a Star Delta starter, standard of the shelf, is nominally rated at 3 starts per hour. If you need a starter to start/stop 20 times per hour, then the starter must be redesigned to manage it.

Switches aint just switches.

Here in Australia, it is Illegal for someone not currently qualified, to install electrical equipment. But that does not stop people using 2pair telephone cable to connect a ceiling fan, some bloody electrician wants to charge me $$$$$$, to do the job. I know and did it for nothing, type idiots.

But as you are an electrician you should know all this.......

Cheers.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Rating Current for Switch & Cable

05/03/2011 7:05 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#10

Re: Rating Current for Switch & Cable

05/03/2011 6:32 PM

Just noted that these lights are being installed underground, as the cable rating you are using, indicates that it will not be in a roof space or in conduit above ground.

If the 1.5mm cable is being used as a control circuit to switch a contactor, rated at 16amp AC3, and your 40 lamps have been split into 3 groups, and wired with 2.5sqmm cable, then you are getting there.

Cheers.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Greg M (1); hien.nguyenquoc (3); Markone (2); PWSlack (1); redfred (1); TonyS (2)

Previous in Forum: Single and Multi-Core Cable   Next in Forum: Speed of Electricity
You might be interested in: Lamps, High Intensity Discharge Lamps, Halogen Lamps

Advertisement