AHU Load Calculation

05/03/2011 10:39 AM

Room Size: 168 m3, Air change/Hr: 20, CFM: 1975, Outside Temp:104 F, Room Required temp: 71 F, Outside RH: 85%, Expected RH: 22%, system required 20 % fresh air and 80 % return air.

So, Sensible Heat: 1.085X1975X(104-71)/12000 = 5.87 Ton
& Latent Heat: 4.840X1975X (139 - 31.43)/12000 = 86 Ton,

if I overlook other heating load, then total load = 91.87 Ton, but I don't think so, its too much for 168 m3 room, what was my problem with the calculation? Please help?

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#1

Re: AHU Load Calculation

05/03/2011 11:58 PM

FIRST-

You stated that the system required 20% fresh air but you calculated 100% outside air load- both sensible and enthalpy (NOT Latent)

SECOND-

You calculated BOTH the SENSIBLE and the ENTHALPY loads- and you calculated the enthalpy load incorrectly- the "constant" for Imperial (I-P) calculations is 4.50, not 4.840 AND you calculated ONLY the delta enthalpy between fresh air and room air- NOT the discharge air temperature from the cooling coil- which must be low enough to meet the internal sensible loads (that you did not calculate) OR the temperature needed to adequately remove moisture to maintain the 22% RH you specified.

THIRD-

You did not calculate ANY internal sensible loads (lights, equipment, people, etc.) and you did not calculate ANY internal latent loads (processes, people, etc.). The coil leaving air temperature must also be low enough to satisfy that sensible load at 1975 CFM supply.

Assuming that your fresh air and internal air enthalpy values are correct, your load (enthalpy-based) is 4.5 x (((1975 x 0.2 x 139) + (1975 x 0.8 x 31.43)) - (enthalpy of the coil leaving air conditions)) / 12000.

Finish your internal load calculations and try again.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#2
In reply to #1

Re: AHU Load Calculation

05/04/2011 1:26 AM

This is in addition to Energygod's comments. Use proper form E20 and correct method as listed in ASHRAE or carrier handbooks to carry out cooling load calculation .Plot the process in P-s chart. Now days many software's are available to reduce manual calculation

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#7
In reply to #1

Re: AHU Load Calculation

05/04/2011 11:36 AM

For the benefit of those readers who do not have detailed psychometric background the "4.50" constant is 0.075 Lbs per CuFt for "standard" air times 60 minutes per hour to convert CFM into Pounds per hour which is then multiplied times the differential in enthalpy (heat content of air in BTU per Pound) to get BTUs per hour heat exchange load. That value, divided by 12,000 BTU/hr (value of one "ton" of cooling) yields cooling load in tons.

By the way- since we are in the "training" mode- a "ton" of cooling is based on way back when ice was used for air conditioning. A ton of water (2,000 Lbs) melting from ice at 32F to water at 32F absorbs 144 BTU per pound (the heat of fusion for water). So- 2000 x 144 = 288,000 BTU. If you divide that by 24 hours in a day, you get 12,000 BTU per hour- or one ton of cooling effect

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Participant

Join Date: Jan 2015
Posts: 1
#29
In reply to #1

Re: AHU Load Calculation

01/11/2015 2:42 PM

Hi Mr. Energygod,

Thanks for the valuable information.

Can you please let me know how & what exactly does the values 139 & 31.43 refers to?

I believe this must be the enthalpy at 104F/85% & 71F/22%. Am I assuming it as it actually is?.

Thanks.

Register to Reply
Anonymous Poster #1
#30
In reply to #1

Re: AHU Load Calculation

01/22/2016 7:23 AM

Sir,

I am naive to this after reviewing your discussion i felt very enthusiastic nad have joined in this site.pls explain me the formulae for calculation of ahu heat load. what is that "139" and "31.43" values??

And also kindly tell me the software for this calculation.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#31
In reply to #30

Re: AHU Load Calculation

01/22/2016 9:33 AM

This reply is also to Mohsinrkhan86 since I somehow missed your post.

The values "139" and "31.43" are enthalpy (given as BTU per pound of air in "I-P" units) differences between the outdoor (ambient) air which was defined by the original post.

I did not calculate the values BUT they seem reasonable.

The outdoor air was given as 104F and 80% RH- VERY hot and humid, so very high thermal content. The indoor air was given as 71F and 20% RH- "normal" BUT very dry so relatively low heat content.

As I stated in one of my responses, the one "missing" value was the actual supply air temperature AND its corresponding enthalpy. In order to have a space with that low of a RH, the supply air (which is usually close to 100% RH at the supply temperature) would have had to be VERY cold (to remove the moisture required) and then likely had reheat supplied to avoid comfort issues due to the low supply temp.

Relative humidity (RH) is by definition the amount of moisture in the air compared to how much moisture the air (at that temperature) could contain at saturation (100% RH). Without getting specific, and ONLY for this discussion, if we were to assume that air at 71F could "hold" 0.1 pounds of water for every pound of air then the defined air would have "held" 0.02 pounds of water (20% of the maximum possible) in every pound of air.

IF the space was totally "vapor-tight" so that NO additional moisture could enter the space, the supply air would also have contained 0.02 pounds of water per pound of air but it would have been "saturated" (~100% RH). BUT- it is very likely that "outside" moisture will enter the conditioned space (especially because the "very dry" air acts like a sponge for any available water vapor). SO- the actual supply air would have had to have had even lower water content- maybe 0.005 pounds of water per pound of air- to allow for the "outside" moisture that would infiltrate and mix with the space air. That means that the supply air would have been "saturated" (100% RH) with 0.005 pounds of water per pound of air. That condition would have required VERY cold air that would require reheat for the comfort mentioned earlier. AFTER the reheat, the supply air would STILL only have 0.005 pounds of water per pound of air BUT the RH of the reheated supply air would likely have been 40-50%.

AS the supply air was "diluted" by the incoming water vapor, and heated by the space conditions, the resulting ROOM air would have been 71F and 20% RH since RH falls as air temperature increases- given no more added moisture.

Back to the issue of the "missing" supply air enthalpy- It would have been very low- maybe 12-15- because of the low temperature AND moisture content. Since water vapor is able to "hold" much more heat than "dry" air, moisture content is the biggest factor in determining the enthalpy value of the air.

Hope this extended discussion helps you to understand the complexities of the original post.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: AHU Load Calculation

05/04/2011 1:57 AM

I haven't checked it yet, but I'm not sure the original calculation takes into account the specific heat and density of air. The 86 tons of latent cooling seems inordinately high.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: AHU Load Calculation

05/04/2011 7:20 AM

1800 sq ft and 90 tons of capacity. You may have overshot your sizing X10. You really need to rework your calculations. 20 air changes per hour??? What is this room for? Most medical buildings only require 4-6 (it can really vary) but 20??

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#5
In reply to #4

Re: AHU Load Calculation

05/04/2011 8:47 AM

Its a pharmaceuticals plant, and 20 ACR/Hr is requirement for clean room where all of the process work continue.

The problem is quite clear to me but need not fully.......!

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #5

Re: AHU Load Calculation

05/04/2011 9:05 AM

I've worked in some pretty big clean rooms before for catheter and angioplasty balloon production, hard drive manufacturing, the Henkel laboratory for final customer product production, etc. I've never seen such a high requirement.

The air change requirement is like a 4 bedroom home having complete air changed every 3 minutes! That's incredible.

You might want to include floor to ceiling height and get total cubic volume, not just sq meter of floor space.

Does the entire room need this many air changes? Can you vent directly over specific areas and achieve the margins specified? Are you using powered Hepa's to charge the room and getting a positive room pressure?

Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#8
In reply to #6

Re: AHU Load Calculation

05/04/2011 10:26 PM

As per FDA requirement minimum requirement for clean room is 20 ACR/Hr, We have different filter including HEPA and need to control room pressure. Basically its a big system and we have 5 other AHU.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9
In reply to #8

Re: AHU Load Calculation

05/05/2011 8:22 AM

I looked it up, you're right. 20 is actually a minimum for that class of room. The air changes are achieved by how many feet per minute are forced through the hepa's. So you need hepa area and airflow rates across them to determine changes per hour.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#10
In reply to #9

Re: AHU Load Calculation

05/05/2011 10:14 PM

The problem is we are still in the problem........ no one provide me the solution.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#11
In reply to #10

Re: AHU Load Calculation

05/05/2011 11:09 PM

Your initial post was filled with errors and indicated that you did not truly understand "your problem".

My initial post (#1) and MRSWAMY's post (#2) have given you all you need to know to "solve" your problem.

NO ONE here is going to do your calculations- we have given you all the tools you need to generate a working solution to your problem.

Access the suggested manuals, or hire a competent HVAC engineer, to get to where you want to be.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#12
In reply to #9

Re: AHU Load Calculation

05/06/2011 8:53 AM

I'm not the OP, but I want to ask two related questions:

First: How do I interpret / reconcile the 20 air changes per hour with the requirement for (only) 20% fresh outside air? (I'm not stating this very well, but hopefully someone will understand my misunderstanding--if you make an air change with 20% outside air (and 80% recycled air), does that count as an air change? Or must you increase the amount of air circulated so that in one hour you get the equivalent of 20 air changes at 100% outside air, which, if I calculate correctly, means 100 air changes per hour (times 20% fresh air per change, gives you 20 air changes of fresh outside air)? (I assume / hope that is not the requirement.)

Second, is that really more than is required? I mean, I'm sure there are regulations somewhere that require that, but is that really the best way to create and maintain a clean atmosphere in the room--wouldn't fewer air changes and "better" filtering do a better job of keeping the room clean, and also use less energy, which should be a valid design criteria these days? Or is it "effluvium" generated by the process and personnel in the room that you're trying to get rid of by using so many air changes?

Finally (oops, sorry, this is the third question)--presumably this is not a--well, I don't know the right name, but one of those labs where some very dangerous biological is processed that would be a problem if it escacped, right? Because, if it was, you would also have to very carefully filter and process the exhaust air from the process, and the more there is, the more has to be processed?

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#13
In reply to #12

Re: AHU Load Calculation

05/06/2011 10:46 AM

All reasonable questions-

First- the 20 A/C per hour is an industry standard to assure essentially equal temperatures and humidity throughout the facility- virtually no chance of stagnant air. The 20 A/C per hour is TOTAL air circulation- for the same reasons as noted earlier. The 20% "fresh" air is likely due to either the exhaust make-up, personnel fresh air requirements and/or pressurization of the space.

Second- PROBABLY, but lots of "rules" get made because "they seem to work". A well qualified HVAC designer can easily lay out an air distribution system that will provide FULL circulation with as little as 3 A/C per hour or less- BUT over 50% of the designers out there don't meet that qualification. SO- by requiring massive air circulation, the job gets done. Regarding energy usage- AGAIN, because energy USED TO be relatively cheap, the "tried and true" method of sub-cooling and reheating massive amounts of air continues to be used, even though it wastes huge amounts of energy. The end-users are making SO MUCH money that it just doesn't "hurt" that much. Systems are available- my company makes one- that can allow the high air flows AND control energy use (and the related environmental impacts- CO2 and NOx) but we are just getting started marketing our systems and potential end-users do not know about it- or other options- yet.

Third- ANY lab that handles bio-hazards or other toxic products has very defined protocols for their use, and highly effective exhaust hoods for working with those products that discharge into HEPA filters before the air is truly "discharged" into the atmosphere. The air being circulated is also likely being sent through the same type of HEPA filters before it is sent back into the space to protect the room employees from any accidental out-of-hood releases. By the way- that is also another reason for the high air change rate- any accidental releases are very quickly "diluted" below their toxic levels before they are later captured in the high grade filters.

Hope this helps.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#14
In reply to #13

Re: AHU Load Calculation

05/06/2011 10:53 AM

Re: Hope this helps.

Yes, it does--thanks very much!

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15
In reply to #14

Re: AHU Load Calculation

05/06/2011 11:22 AM

you are welcome-

by the way- you accidentally clicked the "off-topic" button. If you ask them, the moderators will cancel that click. (I did it once myself).

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#16
In reply to #15

Re: AHU Load Calculation

05/06/2011 12:13 PM

Actually, if you're referring to my last post, I clicked that off topic intentionally--I figure that thanking you, although a nice thing to do, is really off topic.

If you're referring to some other post, I don't think I marked any others on this thread OT.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#17
In reply to #16

Re: AHU Load Calculation

05/06/2011 12:17 PM

If you think back at some of the recent threads- A LOT of comments that are truly OT still get posted- at least yours was about the theme of the initial post.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#18
In reply to #17

Re: AHU Load Calculation

05/06/2011 2:58 PM

Yup!

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#20
In reply to #15

Re: AHU Load Calculation

05/08/2011 5:08 AM

I would say, that was truly amusing......

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#19
In reply to #12

Re: AHU Load Calculation

05/08/2011 5:00 AM

20 air change is one of the requirements not all.

G4, F7, F9, and terminal HEPA filter is required for clean room with room DP, dust collector, room exhaust, etc....... their are lots of requirements.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#21
In reply to #19

Re: AHU Load Calculation

05/08/2011 10:36 PM

I understand and TOTALLY agree, BUT my post was in response to a question regarding WHY certain protocols were in place and whether it was possible to satisfy those primary criteria WITHOUT using the "tried and true" approach that is normally applied.

Whether it is POSSIBLE to meet certain Operating criteria dose not negate the primary DESIGN criteria when certain protocols are mandated by the current state of the art in Good Manufacturing Practices or other Operational Criteria.

When DESIGN criteria call for certain procedures, those procedures MUST be met. However, it is still possible to operate a facility requiring those procedures at much lower energy usage levels IF some "out of the box" solutions are used that allow meeting ALL of the OPERATIONAL criteria with some non-standard, creative solutions that allow BOTH the operational requirements to be met AND reduced energy usage.

My firm HAS developed one such solution that we will be bringing to the market place very shortly which provides ALL of the operating criteria mentioned earlier AND cuts total energy usage by 70% to 75% compared to "standard" HVAC systems serving spaces like this- plus it provides 100% sterile air.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#22

Re: AHU Load Calculation

06/25/2011 8:24 PM

Dear BASHIR1219,

In you posting a portion of which reads as " So, Sensible Heat: 1.085X1975X(104-71)/12000 = 5.87 Ton & Latent Heat: 4.840X1975X (139 - 31.43)/12000 = 86 Ton," and 12000 at the denominator appears to be low (I am not sure)

what is the basis.?

Thanks,

rajeswari

Register to Reply
2
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#23
In reply to #22

Re: AHU Load Calculation

06/26/2011 12:22 AM

rajeswari-

In English units, one "ton" of cooling is defined to be 12,000 British Thermal Units (BTUs)

That value came from the energy required to melt one English ton (2,000 Lbs) of water in the form of ice to liquid water.

Every pound of water has a latent energy of fusion of 144 BTUs. In other words, 144 BTUs of heat must be removed from one pound of water at 32F to turn it into ice at 32F OR 144 BTUs of heat must be added to one pound of ice at 32F in order to melt it into one pound of water at 32F. In the cooling process, heat is removed from one media and transferred to a second media. The heat removal process is called "cooling".

Since there are 2,000 pounds of water in an English "ton", the total amount of latent fusion energy required to totally change state from ice to water is 2,000 X 144 BTUs or 288,000 BTUs.

288,000 BTUs divided by 24 hours in a day = 12,000 BTUs per hour. Hence, the use of 12,000 BTUs per hour to define a "ton" of cooling capacity.

By the way- if you look at the first post following the initial question, you will see the "true" process of determining the actual cooling load for the condition that prompted the initial post.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#24
In reply to #23

Re: AHU Load Calculation

06/26/2011 1:28 AM

Interesting.

Refrigeration tons is not something I'm familiar with, but the Imperial ton is 2240 lbs. US short ton is 2000 lbs.

Please enlighten.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#25
In reply to #24

Re: AHU Load Calculation

06/26/2011 2:13 AM

All "normal"- not SI- calculations are based on "short" tons- 2,000 Lbs per "ton". The "imperial" ton is basically a metric ton in English units.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#26
In reply to #24

Re: AHU Load Calculation

06/26/2011 2:22 AM

There is also a JRT (Japan ton of refrigeration), based on a metric ton rather than short Imperial ton (12,000 x 2240/2000 = 13,440 Btu/h).

As a historical note, I think 12,000 is a conventional value; I have heard but not verified that a "real" ton of refrigeration is something like 12,051 Btu/h. This does not matter in a world of approximate calculations.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#28
In reply to #26

Re: AHU Load Calculation

06/27/2011 6:18 AM

Cool - pardon pun - so it's a conventional approximation - so the actual conversions aren't of great importance, hence the 'dogs breakfast' in naming of units - which is what triggered my curiosity in the first inst.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#27
In reply to #23

Re: AHU Load Calculation

06/26/2011 2:40 AM

Dear Mr. EnergyGod,

Thank you very much for your detailed explanation and easily understandable.

rajeswari

Register to Reply
Participant

Join Date: Dec 2016
Posts: 1
#32

Re: AHU Load Calculation

12/02/2016 9:42 PM

sir

i am present job is clean room hvac draughtsman

but i don't any thing about heat load calculation,ahu & fcu ,fillers,coils,blowers chillers ,diffusers,ducting size selection process

i am have great interest so i kindly requesting for provide the clean room selection process pdf & heat,pressure load calculation excels of the u done project & also the diagram of the clean room

so plz forward (any person) to my Email id konderu999@gmail.com

plzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzz

thank you

Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: