110v From a 220v Line

05/09/2011 3:03 AM

I have a shallow well pump located approx. 125' from the breaker box, so I hooked it up as 220v rather than 110v. I have a buried power line with 3 braided wires including the ground. I'm uncertain of the gauge, I'm guessing it's 12 gauge.

I would like to have a 110v outlet located near the pump. can I come off one of one of the lead wires and run a neutral wire to a ground rod? or run it back threw the ground wire?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 110v from a 220v line

05/09/2011 3:46 AM

Given that the cables now installed. I would use the core that is being used as the earth as neutral. Use the braid as earth with the addition of the ground spike at the remote point. It may not be up to regulations but it will work.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 110v From a 220v Line

05/09/2011 9:33 AM

If in doubt, consult a qualified electrician locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
4
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#3

Re: 110v From a 220v Line

05/09/2011 11:12 AM

Umm...no...you should not run the neutral to a ground rod. That setup would not be safe. That type of setup is specifically forbidden in most electrical codes, specifically anything the IEEE or NFPA publishes.

If your well pump is 110v why did you run 220v? I didn't really catch that from your original post. I would connect the line as 110v. Run the hot neutral and ground on the three wires. Put a ground rod at the pump and connect that to ground. Put in a GFCI breaker at the panel board.

It really isn't a good idea from a safety perspective to mix neutral and ground beyond the panel board. That can result in a nasty shock anywhere along the ground path which could be any convenient connection. This is especially important in your case.

If there were a fault in the pump, this could put current into the water supply, water being an excellent conductor. Without a proper path back to the panel board, the breaker may not trip if a better path to ground is found through a person using a spigot somewhere. There are too many scenarios to cover here.

The basic information I would want to impart would be to not mix neutral and ground and to properly power, ground and protect the new location.

Reply Good Answer (Score 4)
Anonymous Poster #1
#6
In reply to #3

Re: 110v From a 220v Line

05/09/2011 4:15 PM

i decided to run it on 220v because of the long run. "125'" though 12 gauge braided wire may be able to run the pump on 110v. i don't know enough about voltage loss to make a good decidition, so i thought i'ld go the safe waqy.

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#10
In reply to #6

Re: 110v From a 220v Line

05/09/2011 7:50 PM

There is no appreciable voltage loss. AC equipment is designed to run on 110/208/220/240, whatever. Connecting a 110 device to 220 is not good and would require some creative wiring which would let the magic smoke out, no doubt.

If you don't deliver the proper phase/neutral/ground to a 110 outlet, you will find out in short order there is no voltage loss and may in fact kill you.

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#17
In reply to #6

Re: 110v From a 220v Line

05/10/2011 4:09 AM

Good gradulations, you have answered your own question. Yes you are right you dont know enough!

10 points for asking the question, dont attempt this installation.

Seek professional help.

Best Regards

Joe

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: 110v From a 220v Line

05/09/2011 12:37 PM

As a clarification.

Given that the cables now installed. I would disconnect and reuse the core that is being used as the earth as a neutral. Use the braid as the earth with the addition of a ground spike connected to the braid at the remote point.

It may not be up to regulations but it will work.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #4

Re: 110v From a 220v Line

05/09/2011 12:50 PM

Okay, that sounds right. I don't think I caught the original intent. If the braided portion is grounded at the distribution panel and at a ground rod at the pump it is within NEC. Other codes, not sure. GFCI would be necessary for the circuit to work effectively, and would be required or an exterior (wet) location, such as the outlet he was suggesting. Plus, the pump itself is in that wet location.

Reply Score 1 for Good Answer
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#8
In reply to #5

Re: 110v From a 220v Line

05/09/2011 4:32 PM

i like the iidea of a ground fault. the pump is in a 32" manhole with no room to work let alone get away from an electrical shock. where should the ground fault breaker be located?

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#11
In reply to #8

Re: 110v From a 220v Line

05/09/2011 7:51 PM

The GFCI breaker would be located in the service panel/breaker box.

Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#7
In reply to #4

Re: 110v From a 220v Line

05/09/2011 4:23 PM

i'm not sure if you understand that all three wires are 12 gauge? they are enclosed in a weather proof jacket

Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#9

Re: 110v From a 220v Line

05/09/2011 4:38 PM

can i run a 1/2hp pump at 110v with 12 gauge braided wire over a distance of 125' without any voltage drop?

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#12
In reply to #9

Re: 110v From a 220v Line

05/09/2011 7:58 PM

Check the mfr label for the voltage and current draw. This is how you will size the wiring servicing the equipment. Reference the NEC for determining the length of service allowed for the gauge of wire and load requirements. Again, voltage drop is not what you wil consider here...current draw is what you need to be concerned with.

You don't oversize the voltage to make up for "voltage drop". Providing two phase (split phase) power to a 110vac device is not going to work. 110vac devices require single phase and neutral, totally different.

Reply
Active Contributor

Join Date: Sep 2010
Location: Indianapolis
Posts: 10
#20
In reply to #9

Re: 110v From a 220v Line

05/10/2011 7:15 AM

To answer your question, though, the nominal current draw for a 1/2 HP 110V single phase motor is 9.8 amps. 12 gauge wire has a resistance of about 1.62 ohms/1000', so your voltage drop is 9.8A x (250' [there and back] x 1.62ohms/1000') = 3.97V (give or take). Your pump is rated 110V because it assumes up to a 10V loss from the initial 120V at the breaker panel, so voltage loss for your installation actually wouldn't be an issue. Also, the ampacity of 12 gauge wire is 25 amps, and you're well below that.

__________________
"We have met the enemy, and he is us." -- Walt Kelly
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30
In reply to #9

Re: 110v From a 220v Line

09/28/2023 7:37 AM

<...without any voltage drop...>

As no commonly-used circuit conductor is usually a superconductor, there will always be a <...voltage drop...>. It is within the domain of the qualified Electrician to ensure that the cable selected provides a <...voltage drop...> that complies with the local electrical code once installed. The conductor size, the length of the cable, the full-load-current to be carried and the method of installation all have a bearing on this assessment. At the end of the installation, a signed record of it would remain with the user. One doesn't get these things during a homebrew one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#13

Re: 110v From a 220v Line

05/09/2011 10:32 PM

This is not magic. It's a formula and an extensive set of regulations designed to keep people from shocking someone to death, or burning down their house. Would you try using English muffins with honey as brake pads cause they are sticky?

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#14

Re: 110v From a 220v Line

05/09/2011 10:39 PM

I got the impression your pump gave you a choice of 110 or 220 volt wiring, and you wired it 220v to minimize line losses, and preserve the motor. Then you decided you wanted a 110 outlet at the pump house. If you're not going to draw much current from the outlet WHILE the pump is running, I'd just tap off one leg and the neutral. You can also wire each 110 outlet of a duplex off a different leg, remembering to break off the connecting link on the side of the back of the duplex outlet.

If you're going to run an electric lawn mower, turn off the pump at the pump house. You DO have a double pole double throw switch there, eh? Then you have your choice of pump or outlet.

__________________
Align culture with nature...
Reply
Commentator

Join Date: Feb 2011
Location: Perth, Western Australia.
Posts: 72
Good Answers: 1
#15

Re: 110v From a 220v Line

05/09/2011 11:20 PM

It amazes me how many people play around with things that can be extremely dangerous even lethal. As for your wanting to hook your pump up as 220v rather than 110v - is it a 'slect the voltage' you want pump? I may be wrong but it may not run correctly if it is expecting 220v.

In my opinion from what I have read in regards your questions and comments I would urge you to get in a qualified electrician. (here in Aus we have to, as it is illegal not to do so.)

.......by the by if you let the smoke of the (electrical) system it creates a lot more problems....

__________________
'Nunc est bibendum'
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16

Re: 110v From a 220v Line

05/10/2011 2:21 AM

buy an industrial 220v to 110v transformer....Home Depot have them.. in all sizes!!

__________________
The square root of nothing is what you make it!
Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#23
In reply to #16

Re: 110v From a 220v Line

05/10/2011 8:37 AM

i agree. the safer the better. anyways, it wont cost a lot than taking a risk compare to the saving you gain by splitting the 220v, line to ground connection. buy a transformer.

Reply
2
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#18

Re: 110v From a 220v Line

05/10/2011 7:04 AM

This is a very simple matter but, as you have demonstrated, dangerous if you have not some theoretical background as well as knowledge of installation requirements as set out in the local code.

But obviously you are going to do it anyway so lets get it right.

What I understand from your confused post is that you have a half horsepower pump motor that can be wired either for 220 volts of alternating current or 110 volts of alternating current.

As well you have a buried cable which appears from your back and forth to be 12 gauge, three wire, plus ground, i.e., the metal braid.

You want to power the pump as well as an 110 volt outlet. You have wired the pump as 220 volts.

That means that you have used the two colored wires of the cable, usually red and black here in the states, to the appropriate terminals on the motor.

It seems you have used the third, white wire, as a ground and also the braid as a ground.

Provided that you have properly attached the braided grounding wire to ground at both ends, you can use the white wire as the neutral for a 110 volt outlet, disconnecting it of course from any grounding purpose it now serves although back at the panel the neutral and ground are bonded.

As redundancy, because wet areas are so hazardous, I would drive an eight foot ground rod next to the pump, bonding it both to the braid and to the pump body and any other parts that in case of a short could be electrified. You should as a matter of course have a ground fault interrupter in the breaker panel.

Perhaps it is useful to point out that wet areas are dangerous, not because of some mystical property of water and electricity but rather because the earth itself is used in the electrical transmission system as one leg of the circuit and the wetting characteristics of water provide a good and dangerous connection to the earth and the system.

You can now use the white neutral along with one leg of the 220 feed, usually the black wire, for your 110 volt outlet. Again, although redundant, I would install a duplex ground fault interrupter for the 110 volt outlet. It should go without saying that you should not use any appliance in that outlet that in combination with the pump exceeds the GFCI breaker values in the panel box but if you do the panel breaker will let you know. Of course installing a GFCI duplex for the 110 volt outlet will require bonding to the grounding rod.

If, on the other hand, your underground cable is only two wires, black and white, and a braided conductor, then there is no reason with a half horse motor not to change it back to 110 volt arrangement and then, in parallel, wire the 110 volt GFCI across it. The braided ground continues as your safety ground both on the motor and the outlet. Again, especially because in this hook-up the single phase draw of the motor goes up, do not overload the line by connecting to that outlet some humongous draw, for instance in cold realms, a heater to keep the pump and pressure tank from freezing.

I think that covers it but if not someone, I am sure, will correct me.

j.

Reply Good Answer (Score 2)
Anonymous Poster #2
#24
In reply to #18

Re: 110v From a 220v Line

05/10/2011 9:21 AM

Do NOT drive a ground rod at the pump, unless you connect it to the ground in the panel. The National Electrical Code (NEC) requires that there be only one ground in a system. It forbids separate grounds on the same system.

BEST ADVICE. HIRE A LICENSED LOCAL ELECTRICIAN TO DO THIS WORK FOR YOU. He will follow ALL the NEC provisions and provide a safe installation.

The number of questions in this post tells me that no one really knows the complete situation. This is not a difficult installation for someone who is licensed and knows what he is doing. Anyone else is liable to kill someone.

Signed, A Registered Professional Electrical Engineer

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#19

Re: 110v From a 220v Line

05/10/2011 7:10 AM

Not a good idea.

Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#21

Re: 110v From a 220v Line

05/10/2011 8:11 AM

Just run it back through the ground wire...USA National Electrical Code now requires ground and neutral to be bonded together inside your electrical panel.

Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#22

Re: 110v From a 220v Line

05/10/2011 8:27 AM

Use a step-down or an auto transformer sized to the expected load. Check Allied Electronics or a similar supplier.

Reply
Power-User

Join Date: Nov 2005
Posts: 173
Good Answers: 3
#25

Re: 110v From a 220v Line

05/10/2011 9:34 AM

To simplify your installation, first dou you plan on installing a quick disconnect at the pump location? NEC requires a service disconnect if your equipement is out of sight from the distribution panel box. Second, is your pump in a pump house or some sort of shelter? Meaning is there a place to add a sub panel to have a GFCI located near the pump. If not, the NEC requires to have a quick disconnect with 10' or eye sight of the equipement, being a safety measure for maintenance functions. It really doesn't matter what plan on hooking up, if the pump can be wired for 220, then take advantage of the effort. You do not see any voltage drop until after 150' from the source, this is when you start to see it and you never force more then 80% load factor onto your service drop. Being, if your pump draws 9.8amps on a continuous function, then a 20amp breaker is all you need and 12AWG is a standard size wire.

This being said, when you wire up the pump, since it is in a wet location, you will use PVC sealtight flex conduit to hook up your pump. On your disconnect, you have the options to use fast blow fuses at the site, I would recommend this effort and your fuses would be sized to 125% of the name plate rating of the motor. It might seem odd, but her is the big picture, you know this unit only draws 9.8Amps onc it is up and running. We feed the circuit to the disconnect with the 20Amp circuit. This 20Amp circuit is designed to protect the wire feeding your equipement to the disconnect. Next, with the fusable disconnect you will size the fuse to protect the pump itself, 125% of 9.8Amps is 12.25Amps, so would round it down to 12Amp fuses on the disconnect. By code, section 680 covers pools, spas, and other wet locations and similar settings, you will need to actually go over the requirements, its really too long to rewrite the book for you. If you do have a location to mount a sub panel, do it. Then you can branch out to your outlet and also have the means to safely configure your disconnect to your pump. Also I would recommend using a motor starter, push button type on/off set up to make this as neat as possible. There are several ways to wire it up, but so many veriables to make it all go wrong and get someone killed.

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#26
In reply to #25

Re: 110v From a 220v Line

05/10/2011 10:08 AM

Great information. You went a bit further than I. Hopefully the OP will get an electrician or at least a good inspection afterwards before putting this into operation.

I would hate to hear of someone getting zapped over what is really a simple installation (as long as the rules are adhered to).

Reply
Associate

Join Date: Jun 2009
Location: Estacada, OR
Posts: 29
#27

Re: 110v From a 220v Line

05/10/2011 11:21 AM

Mr. Simple chiming in. Perhaps, as you have provided enough for a 100 AMP (I'm somewhat certain that is what #12 can feed, would have to 'look it up' to be sure) panel near your pump. Get a small 100 AMP panel at your local Bog Box Store and provide proper over current protection and voltage for whatever you're going to locate near your well.

Just a thought.

__________________
General Note: Design subject to The Laws of Physics....
Reply Score 2 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#29

Re: 110v From a 220v Line

07/12/2012 3:15 AM

can't you find a 22o to 110 V transformer with one of its secondary terminals grounded?.

__________________
pnaban
Reply
Reply to Forum Thread 30 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); Anonymous Poster (2); brich (1); crashcol (1); cuba_pete (6); DaveFuller (1); erlo (1); Flaxfield (1); Fredski (1); Garthh (1); Jack Jersawitz (1); jlstitt (3); Joe Sparky (1); LordMaximo (1); lrsheldon (1); ormondotvos (1); PFR (1); pnaban (1); PWSlack (2); TonyS (2)

Previous in Forum: Phasing Out Procedure   Next in Forum: What is the Relative Permeability of Silicon Steel - 3%, 3.5%, 4%

Advertisement