Shielding and Grounding of 24 VDC Signals

05/09/2011 5:07 AM

Would it be necessary to consider shielding for cables carrying 24 VDC signals from field instruments to a PLC-based process control system? Also, please let me know if there is a need for a Y/G earth wire alongside the cable, to be as part of the cable, carrying a.m. 24 VDC signal?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Shielding and grounding of 24 VDC signals

05/09/2011 5:09 AM

Just earth the 0V line at the power supply. Everything will be just fine.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#2

Re: Shielding and grounding of 24 VDC signals

05/09/2011 8:21 AM

Yap, surge from EMI or lightning happens anytime, might as well conform to standard protocols for communication system.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Commentator

Join Date: Feb 2011
Location: Perth, Western Australia.
Posts: 72
Good Answers: 1
#3

Re: Shielding and Grounding of 24 VDC Signals

05/10/2011 12:14 AM

Only need shielding if you have got other sources that may interfere. As for runnnig and earth wire..Why? it won't do any thing except cost time and money and if you've got money to waste I can always assist in 'looking' after it.

__________________
'Nunc est bibendum'
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4

Re: Shielding and Grounding of 24 VDC Signals

05/10/2011 6:04 AM

What exactly is the signal being carried? Based on your use of "24 VDC signals" I'm jumping to the possibly wrong conclusion that they are DI and DO signals (digital input and digital output signals), which often don't need to be shielded.

However, if they are carrying something more sensitive (signals to an A/D converter, for example) they do need to be shielded.

Register to Reply
Participant

Join Date: May 2011
Posts: 4
#7
In reply to #4

Re: Shielding and Grounding of 24 VDC Signals

05/22/2011 3:52 AM

Sorry for the delay and many thanks for your reply. You jumped to exactly the right conclusion. the cables carrying DI and Do signals to a PLC-based control system. If these need to be shielded, considering the fact that noise may hardly distort the 24 VDC signal, why shielding might be necessary?

Register to Reply
3
Active Contributor

Join Date: Mar 2011
Location: Lexington, Kentucky, United States of America
Posts: 20
Good Answers: 1
#5

Re: Shielding and Grounding of 24 VDC Signals

05/10/2011 9:27 AM

Unless you have 1000 miles of this cable, the extra cost of the shielding is negligible and as has been pointed out, EMI is about everywhere today. Lightning alone and stray currents are justification enough. Sensitive signals like 4-20 AI and AO lines do require shielding. DI & DO not so much, but it's still a good idea. If you do use shielded, be certain that it is only grounded at the source/PLC end, though. You will get problems that are hard to find if you have ground loops.

__________________
John 11:25
Register to Reply Good Answer (Score 3)
Participant

Join Date: May 2011
Posts: 4
#6

Re: Shielding and Grounding of 24 VDC Signals

05/11/2011 4:05 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments