Flow Transmitter Not Giving Proper Reading

05/13/2011 1:52 PM

I have DP type flow transmitter (venturi) that has a cal range 0-1250 mmH2O & flow range display is 0-13000 kg/h , it's showing 330 kg/h after many times o trimming it's not going to '0' so any solution? I want to know how to calculate flow at DCS side? What is the equation probably used to do it? I know may be it's silly question but I need simple understanding so asking

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: May 2011
Posts: 3
#1

Re: Flow Transmitter Not Giving Proper Reading

05/13/2011 2:37 PM

your reading at the DCS is 330 kg/hr even at zero flow condition because for your transmitter sensing the Delta P of just 0.805 mmH2O which is nearly zero but because of the impulse leg variation it is sensing and showing some flow of 330kg/hr.

To avoid this, normally LOW CUT OFF is configured in the DCS and below which when flow goes it will indicate zero flow to avoid impulse line error in actual zero flow condition.

I.E. if 500 kg/hr is kept at lowcutoff then the flow reading goes below 500 kg/hr it will show zero on the DCS. Usually 5% of the flow range is kept as a lowcutoff.

for DCS calculation flow reading = SQT(DP%)*10 %of flow range

in your range if the dp is 312.5 mmh20 means 25% then the flow reading will be:

flow reading = SQT(25)*10 % of 13000

=(5)*10 %of 13000

=50% of 13000

= 6500 kg/hr

Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#2
In reply to #1

Re: Flow Transmitter Not Giving Proper Reading

05/13/2011 2:49 PM

One small note: Some flow transmitters do the square root function themselves, so there is no need to do that in the DCS. He will have to check the manual and setup on the flowmeter.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Active Contributor

Join Date: Oct 2010
Posts: 16
#4
In reply to #1

Re: Flow Transmitter Not Giving Proper Reading

05/16/2011 2:42 PM

the pressure range is 0 to 500 mbar how to calcurate ma for 25 ,50 ,75and 100 percentage

Register to Reply
Associate

Join Date: Jul 2008
Location: India, Kuwait
Posts: 31
#3

Re: Flow Transmitter Not Giving Proper Reading

05/14/2011 12:50 AM

Check your transmitter catalogue and see if there a parameter called "Low Flow Cut in" on your transmitter. This value might be fixed at 330, the reason why ur instrument is not indicating zero.

Register to Reply