Transformer Vector Group Selection

05/14/2011 2:57 AM

Dear All,

I want to know.

why GT of power plant vector group is DY1? please Explain.

generally we used Dy11. if we use GT as DY11. wat happen??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Transformer Vector group selection

05/14/2011 5:06 AM

I want to know.

why GT of power plant vector group is DY1? please Explain.

generally we used Dy11. if we use GT as DY11. wat happen??

I dint do it, honest, please sir ! Don't hit me

Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: Transformer Vector Group Selection

05/14/2011 8:59 AM

The vector group DY1 or DY11 is not valid. The letter(s) for high voltage side is upper case (Y, D, N, Z) but the letter(s) for low voltage side is lower case (y, d, n, z). So, your question is not valid as well.

See this link: http://www.transformerworld.co.uk/vector.htm

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Transformer Vector Group Selection

05/15/2011 10:10 AM

GT is Yd1 or Dy1?

Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#4

Re: Transformer Vector Group Selection

05/16/2011 10:31 AM

Generally for export only transformer, generator side is connected in delta and load side is connected in star. For export import transformers star star connection may be preferred by some since this avoids a grounding transformer on generator side and perhaps save on neutral insulation.I am not sure how correct this practice is but so many systems are running in this configuration.Perhaps it may be felt to be less harmful than operating delta system incorrectly. Yd or Dy connection is standard for all unit connected generators.

The main reasons for connecting generator side winding in delta are:

1)to facilitate grounding of generator system with higher impedance and the load system with lower impedance.

2)To break The zero sequence circuit for the system at the transformer.This ensures the load side zero sequence currents do not come to the generator system.

3)IIIrd and similar harmonics will circulate in delta and will not come to generator system.

The trafo vector group will be Dy if load voltage is lower and Yd if load side voltage is higher.

Dy1,5,7 or 11 selection depends on requirement for load synchronizing ,standardizing or ready trafo availability. All vector groups are functionally similar.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); Jans (1); msamad (1)

Previous in Forum: Capacitor Bank Voltage   Next in Forum: Temperature Remote Control

Advertisement