05/14/2011 1:21 AM

why is the capacitor voltage greater than incoming supply voltage in a capacitor bank....i saw a capacitor bank in which the incoming voltage was 400V ac but the capacitor selected for this panel was 440V ac delta connected

also why the reactance connected in series with the capacitor bank always has a detuned factor of 0.7.

also can you guys provide me some good links for the study of the capacitor banks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Jun 2010
Posts: 38
Good Answers: 2
#1

Re: capacitor bank voltage

05/14/2011 3:09 AM

hope this helps

XXXX://store/gedigitalenergy.com/faq/documents/general/shunt.pdf

Just change the "X"'s to the usual intertube stuffs.

__________________
" Is it plugged in ? " ... " Are you SURE it's plugged in ? " ... " Is it plugged into an outlet that is on a switch ? "
Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#2
In reply to #1

Re: capacitor bank voltage

05/14/2011 6:37 AM

That link did not work for me, even after changing the xxxx to http, and changing the / between store and gedigitalenergy to a period.

This link seems to work.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Capacitor Bank Voltage

05/14/2011 9:11 AM

I think you'll find knowing how to use the Laplace impedance of a capacitor Xc=1/(sC) will be very helpful. Oliver Heaviside was working on transmission line effects when he re-invented the Laplace transform.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: Capacitor Bank Voltage

05/14/2011 11:14 PM

a good amount of information in capacitor selection, de-tuning and related application notes is available from some reputed manufacturers - a brief list is shared here:

already shared here before - http://tinyurl.com/gepfnotes

and :

http://tinyurl.com/moreelectroniconpfnotes

http://tinyurl.com/schneiderpfnotes

if you need to know something beyond the links listed then do ask . . . i promise to try to help . . .

Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: Capacitor Bank Voltage

05/15/2011 5:49 AM

Simply put, the voltage marked on the capacitors is the highest SAFE voltage that the capacitor should ever see. More than this may cause it to explode.....

It is always best to use an actual voltage lower than the marking.

I used to work on heavy printers where the 50 volt caps had 48 volts on them, they did occasionally explode, but had a metal cage to contain the pieces......I was in the same room one day (30 meters away) and only one exploded in a bank, but it was louder than a hand grenade at 30 meters!!!! Probably being in a room amplified the effect to a degree......

So don't be unsafe with the voltages you apply to any caps, you could lose an eye or worse......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#6
In reply to #5

Re: Capacitor Bank Voltage

05/15/2011 8:54 AM

GA. I gave you a GA because I believe that someone who actually answers a question deserves more credit than someone who provides a Wiki-reference. Think about selecting a fuse rating. In most circumstances you would select a current rating somewhat higher than the maximum expected current. Capacitor voltage rating selection is analogous. As the voltage rating of a capacitor is exceeded, its reliability is reduced and the risk of dielectric breakdown (explosion) increases.

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#15
In reply to #5

Re: Capacitor Bank Voltage

05/15/2011 2:20 PM

We should not lose sight of the fact that the voltage rating is also a function a function of the reactance and the VAr of the capacitor in question. It is in effect the main determinant of the capacitance value in farads or micro farads. Moreso, a capacitor is expected to have a leading PF which makes it imperative for it to have a higher voltage than the system voltage. It's actually a fixed voltage and frequency synchronous machine and it is expected to do the PF correction within the safe values of it's rated voltage. The higher voltage of the capacitor is purposely allowed to enable capacitors achieve the desired result of PF improvement. Just as synchronous generators will maintain steady frequency and voltage at all loads to maintain a close unity PF, capacitors have fixed voltages and at times frequency that is above the system voltage.

__________________
There is peace in silence and achievement in plans.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Capacitor Bank Voltage

05/15/2011 10:13 AM

Your doubts would be clarified if you attend to our training programme on Reactive Power Management.

Reply Score 1 for Off Topic
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#8

Re: Capacitor Bank Voltage

05/15/2011 10:35 AM

Dear Friend,

The Capacitor will have a LEADING CURRENT and hence LEADING POWER FACTOR and the Impedence Voltage will add to the LINE VOLTAGE known as TERMINAL VOLTAGE, and hence always HIGHER than the LINE VOLTAGE.

CAPACITORS in series is EQUIVALENT or SIMILAR TO THAT OF RESISTANCES added in PARALLEL in which the RESULTANT RESISTACE WILL BE LESS.

For example, If CAPPACITORS C1, C2, C3, connected in PARALLEL will add up like resistances are connected in series ( R1+R2+R3...) and NETT CAPACITANCE WILL BE 1/C1+1/C2+1/C3

If Capacitors are connected in SERIRIES nett CAPACITANCE will be C1+C2+C3.... like Resistances R1,R2, R3 as 1/R1+1/R2+1/R3=...

RAJESWARI.

Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #8

Re: Capacitor Bank Voltage

05/15/2011 10:42 AM

I am afraid the OP's question is not about the "very marginal" increase in bus voltage when the capacitive load exceeds the inductive load in the system. The OP's question is why should a capacitor used - in a 415V system - along with a 7% reactor, be rated for 440V.

Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#12
In reply to #10

Re: Capacitor Bank Voltage

05/15/2011 10:47 AM

So the 6 to 7% increase in voltage due to the 3rd and 5th harmonics (assuming post #9 is correct) is not relevant?

Why?

Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13
In reply to #12

Re: Capacitor Bank Voltage

05/15/2011 11:07 AM

Oh! I was only responding to Post 8. Post 9 is very relevant. But, the voltage rise is not due to the harmonics but due to the inductive reactance in series with the capacitor. There is a detailed formula for calculating the voltage rise for different tuning factors. Unfortunately, I cannot post them here. It is too long.

Reply Good Answer (Score 2)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#14
In reply to #13

Re: Capacitor Bank Voltage

05/15/2011 12:43 PM

Thanks for the clarification!

Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#18
In reply to #13

Re: Capacitor Bank Voltage

05/15/2011 5:18 PM

Finally a correct answer. GA Electricalexpert65!

Most of the answers given before yours are not correct. They are based on limited understanding of the real science. Who ever use the info in the previous posts above should beware and ask for advise from a competent engineer.

The interaction between a capacitor bank and the inductive feeder is complex. PF, harmonics attenuation, parallel resonances, and voltage drop/boost are affected by so many parameters that a simple answer is not enough.

I have seen many bad use of capacitor banks that were done by the sales guy that caused more problems than it solved.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#16
In reply to #8

Re: Capacitor Bank Voltage

05/15/2011 2:27 PM

In the Northern Hemisphere the opposite applies. Maby translation problem? S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #8

Re: Capacitor Bank Voltage

05/15/2011 2:29 PM

Excellent post, but you completely forgot the effects of parallel and series capacitor connection on the maximum working voltage then allowed!!

Will you add it or should one of us do it for you?

I feel its important as the original question was about voltages and caps.....don't you agree?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#19
In reply to #8

Re: Capacitor Bank Voltage

05/15/2011 5:23 PM

NO! Rajeswari you have it all wrong!

Capacitances in parallel is C1 + C2 + C3...

Capacitances in series is 1 / (1/C1 + 1/C2 + 1/C3...)

Don't give answers for concepts that you don't understand.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#26
In reply to #19

Re: Capacitor Bank Voltage

05/16/2011 11:49 AM

Thank You Mr. Marcot, for correcting the comment. I acknowledge your correction.

I express my regret to the cr4 Forum Members for giving wrong comment.

rajeswari.

Reply
Participant

Join Date: Apr 2011
Posts: 3
#9

Re: Capacitor Bank Voltage

05/15/2011 10:37 AM

There is a reactance in series with capacitor. Normally it's capacity is 6% of capacitor MVAR,. Due to this L-C series combination, voltage develop across capacitor is 6%( actually it depend on the rector value.) higher than the supply voltage.As voltage develop across inductor and capacitor is of opposite sign.Hence the 440V of a capacitor is a operating voltage for 400V system.

This 6 to 7% combination is actually a third and fifth harmonic filter circuit.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #9

Re: Capacitor Bank Voltage

05/15/2011 10:43 AM

7% de-tuned filter is used for filtering 5th and above and NOT 3rd.

For filtering 3rd harmonics onwards you need 14% filter.

Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#20

Re: Capacitor Bank Voltage

05/15/2011 6:25 PM

Ok. Simpli(mind)fying an answer. In an AC cirquit concisting from at least a capacitor C and inductor L, when AC frequency goes near it's resonant frequency (which is f=1/2pi*sqrt(L*C)) strange things happen. Voltage and current on L and C goes bananas. Thankfully there is always an added or parasitic R arround to keep things under control, but that's not something to rely on. So the sugestion is to keep the cirquit detuned (unless you're planning on broadcasting). Detuning factor is refering to how close to the resonant frequency you 're safe to go at this capacitor voltage safety margin. (400V>440V) i.e. 10% These are pre-calculated limits and are more or less convensional. It's not even safe to go that close because neither capacitors nor inductors are perfect devices and other (lesser) resonances WILL happen. S.M

__________________
Life is complex. It has a real part and an imaginary part.
Reply
2
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#21
In reply to #20

Re: Capacitor Bank Voltage

05/15/2011 10:20 PM

Correct.

Especially that modern capacitors are self healing. This is done by printing fusible pattern on the electrodes. If the dielectric breakdown in a small area, the corresponding section of electrode will be (hopefully) isolated by the printed fuses and the cap will keep operating. The net effect will be a reduction of the capacitance with time.

When we reduce the capacitance, the resonant frequency increases. This is why you de-tune on the upper side of harmonic so that your filter's resonance frequency will walk away from the nearest harmonic frequency.

Detuning on the upper side also reduces costs as the capacitance and inductance needed to obtain the resonance frequency desired are smaller.

As far as the resistance is concerned, they are only added to higher frequency filters as the lower frequency ones conduct too much 50/60Hz. Too much power would be lost. Normal plant loads usually participate to the overall dampening of the filters.

An oversight in most filter design is the neglect of the parallel inductance that interact with the filter(s) to produce other resonances frequencies. These frequencies often fall near an harmonic. This is one of the many "oops" that kill the design made by inexperienced people.

There are a few other subtle aspects but you need a book to cover them all.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply Good Answer (Score 2)
Anonymous Poster #1
#22

Re: Capacitor Bank Voltage

05/16/2011 12:54 AM

thank you all.................so the higher voltage selection for capacitance is due to the reactive voltage of the capacitance and detuned reactors is to prevent resonance condition. ...7% detuning is for filtering 5th ,7th harmonic and 14% for 3rd harmonic............thanks a lot...you guys have been of great help................

so for a 440v system , the voltage selection of the capacitance required must be greater thn 440v right?

Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#24
In reply to #22

Re: Capacitor Bank Voltage

05/16/2011 5:39 AM

For 7% detuning :

Consider a detuned filter circuit with a j100 ohm capacitor and a j7 ohm reactor( in series connection). The steady state voltage across the capacitor is :

Vc = -j100/(-j100+j7)*1pu = 1.075pu.

For 14% detuning :

Vc = -j100/(-j100+j14)*1 pu = 1.163 pu.

Therefore, it is seen that for different % of detuning filter, the voltage across the capacitor is different.

Thanks.

__________________
Manindra
Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#23

Re: Capacitor Bank Voltage

05/16/2011 1:11 AM

now to open a can of worms . . . .

so many amongst us here have answered with a probable presumption that harmonics are actually present on the bus under discussion . . . and explained the effectiveness of de-tuning reactors . . . .

however the reactor (if present) really adds nothing to the performance of the system in the absence of harmonics . . .

and the behavior of the system differs depending on the % load prersent at any time too . . . .

therefore :

i suggest that a load study (including a predictive harmonic spectrum) precede the design and installation of any capacitor bank, please.

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#25
In reply to #23

Re: Capacitor Bank Voltage

05/16/2011 10:05 AM

Soebfatehi,

You are correct that a study need to be conducted for every cases as they are all different.

But, there are always some harmonics generated by "linear" loads such as transformers and motors. You also have steps and impulses voltages caused by load switching and lightening strikes on the network.

This is why, passive filters look simple but are extremely difficult to design. Many customers now use active filters to avoid most of these problems even if the equipment is more expensive, the risks are lower.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Active Contributor

Join Date: Jul 2010
Posts: 23
#27

Re: Capacitor Bank Voltage

05/16/2011 2:22 PM

Capacitors charge to the Peak of the RMS incoming maintained at 120 degree intervals. A basic electronics text has all the formulas.

Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#28

Re: Capacitor Bank Voltage

05/22/2011 3:46 AM

Dear Friend,

The VECTOR DIAGRAM will explain why the incoming supply voltage is smaller than the the terminal voltage.

REFER standard Text Books.

rajeswari

Reply Off Topic (Score 4)
Active Contributor

Join Date: Jul 2010
Posts: 23
#29
In reply to #28

Re: Capacitor Bank Voltage

07/05/2011 2:31 PM

Keep studying math and applied technology.

Reply Off Topic (Score 5)
Reply to Forum Thread 29 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Anonymous Poster (1); BKR (1); Dickson (1); electricalexpert65 (4); John Oberuch Jr (2); manindra (1); marcot (4); rajeswari (3); redfred (1); rhkramer (3); SimpleMind (2); soebfatehi (2); thepackrat (1); welderman (1)

Previous in Forum: Flux Factor With Respect to Tube Lights (Lumens)   Next in Forum: Transformer Vector Group Selection

Advertisement