ABB Circuit Breaker System GEK3 Problem

05/18/2011 8:08 AM

Our power station uses ABB circuit breaker system GEK 3 for both of our gas turbine generator.

In one of our previous start-up, we were unable to close the generator circuit breaker when we tried to synchronize the unit with the grid. The closing signal to GCB was given and the GCB reacted to the closing signal.

However, instead of closing, the GCB closed-opened upon receiving the signal. "GCB air pressure low" alarm appeared explained the release of pneumatic air to operate the GCB mechanism.

After the air pressure was charged up, "GCB air pressure low" alarm was reset and the operators did another attempt to close the GCB. However, similar situation occurred. A total of 3 attempts were carried out including the above.

At the 4th attempt, the operators operated the GCB only after the GCB air pressure achieved 8.5 bars. GCB successfully closed and synchronize on the 4th attempt.

I was actually suspecting the permissive from the adjusted value pressure switch F1. I am unable to determine the set point for F1 at the moment as that requires unit shutdown. However, frankly speaking, we do have many experience of closing the GCB with air pressure below 8.5 bars. Normally the air compressor will cuts in when the compressed air receiver reached 8 - 8.1 bars and above that set point we can comfortably operate the GCB without having much problem.

Did anyone encountered similar problem as we did before and any troubleshooting scheme to recommend?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: ABB Circuit Breaker System GEK3 Problem

05/22/2011 12:15 AM

Apparently, the pressure switches in the GCB pneumatic system need calibration.

Generally speaking, the pressure at which the low pressure alarm is issued, the CB trip / lockout signal is issued, the compressor start signal is issued are all controlled by these pressure switches (which are also called density meters when the pressure is temperature compensated).

The pneumatic operating systems of circuit breakers that I know do not allow closing of the CB if the pressure is below a set value and if the low pressure occurs when the CB is in 'Closed' position, the system gives an alarm in first stage and locksout the breaker when the pressure dips further to the second stage.

The GCB 'closing and opening' on low pressure reported by you seems strange and is unwarranted and is also unnecessarily stressing the system. ABB may have some explanation.

__________________
Raghunath