HVAC Return Air Fan Coil Units

05/21/2011 4:33 PM

A single storey building in our project has many rooms. Each room has its own Fan Coil Unit mounted above the false ceiling whose 3 way valve is controlled by its own thermostat in the room. In other words, each room can be considered to be an independent zone, even though the temperatures of all adjacent or nearby rooms would nearly be the same. The walls of some rooms are of full height till the ceiling slab, therefore the return air drawn by the fan coil unit belongs to the room it serves. However, the walls of some rooms terminate at the false ceiling level. This makes it possible for the fan coil unit to pull the air not only from the room it serves but also from adjacent rooms and corridors as there is no partition between the room and these adjacent spaces above the false ceiling. Would this cause any functional or operational problem of temperature control or any other problem? If yes, is the anticipated problem significant enough to require the construction of the walls above the false ceiling all the way till the ceiling slab?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: HVAC Return Air Fan Coil Units

05/21/2011 9:43 PM

I'm not clear on the actual circuiting of the air. From where does each fan draw air, where does it blow the air, and then where does the air go after that?

The air for each apartment probably should not be mixed with the air from other apartments, because then cooking and smoking odors go to the wrong places.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: May 2011
Posts: 30
#2
In reply to #1

Re: HVAC Return Air Fan Coil Units

05/22/2011 2:05 AM

The ducted fan coil unit mounted above the false ceiling of each room supplies air through ceiling supply diffusers and the return is drawn from the return air diffusers also mounted in the same ceiling. However the return air is not ducted and it is drawn from the open plenum above the false ceiling. The plenum above the false ceiling in some rooms is totally partitioned from other adjacent spaces by walls and in some rooms it is not partitioned. Besides the infiltration of smell is there any other problem of temperature control, etc., due to the possibility of drawing return air from adjacent areas due to the absence of walls?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: HVAC Return Air Fan Coil Units

05/22/2011 2:16 AM

That sounds odd to me, but I am not a domestic/commercial HVAC guy. If several apartments were running warmer than others, the mixed return air would not help the apartments that were running cooler. This effect would probably be rather small; the odor carryover would be the greater concern, I suspect.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#4

Re: HVAC Return Air Fan Coil Units

05/22/2011 3:04 AM

Hi 786verycool

My experience of installations such as the one you describe is that the actual mixing of return air between the various fan coil units is not a major problem as the RA will be taking the path of least resistance. If the temperature of RA to the one unit is being affected by some air being taken from the adjacent unit's then, assuming that the temperature of the different RA not to vary more than a degree or so then the 3 way control valve should be able to respond and compensate for the slightly increased/decreased load.

As far as the walls being built up to full height this would more than likely be done from a privacy/security consideration. Yes, you would have closer control but not that much better than the ones drawing from the ceiling void.

Hope this helps.

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2011
Posts: 30
#5
In reply to #4

Re: HVAC Return Air Fan Coil Units

05/22/2011 7:48 AM

The problem actually stems from the very fact that you state viz. a viz., the RA will take the path of least resistance. The air above the false ceiling will be easier to draw than pull the return air from the room through return ceiling diffusers. Therefore, the bulk of the air that will be go through the FCU will not be the return air from the concerned room but from the air that is sitting above the plenum regardless of which space it belongs to.

Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#6
In reply to #5

Re: HVAC Return Air Fan Coil Units

05/22/2011 8:20 AM

Hi 786verycool,

You are correct in your belief about the origin of the FCU's on coil air in that there is no way that, drawing from the ceiling plenum, you will be able to ensure that any of the FCU's are actually getting the bulk of their on-coil air from the same area that they are serving. However, unless these are areas which require very close control and are not being air-conditioned purely on a comfort control basis then the partial mixture of return airs should not be a major problem. If it is then you would probably have to consider separating the conditioned areas by sealing off the voids above the ceilings to achieve this.

Places where I have come across this type of installation is in hotel guest rooms (RA drawn from that area only) and open offices with the fan coil units located in bulkheads down both sides of the office (common return air drawn from the complete office).

Things that may increase the problem you may have are a) the location of the FCU's (all together and ducted to conditioned areas?) or a ceiling void that is not sealed or picking up heat load from the roofing structure.

You may be able to check the room temperature at the return air grill and compare it with the on-coil temperature at the FCU serving that room. In the old days we used to observe air flow by use of a smoke generator which used to reveal some interesting results especially when looking at discharge patterns from diffuser I don't know if these tests are still used these days?

Hope this helps you address the problem.

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: HVAC Return Air Fan Coil Units

05/22/2011 8:30 AM

I am a commercial HVAC contractor. I don't see a problem. Most of the walls you refer to are probably fire rated and part of the overall design . What exactly is your question? Are you having a problem now or just trying to understand an open plenum system?

Register to Reply
Associate

Join Date: May 2011
Posts: 30
#8
In reply to #7

Re: HVAC Return Air Fan Coil Units

05/22/2011 10:03 AM

Thanks for your feedback. The problem that we are having is that out of a total of 35 rooms in the building 5 have walls only till the false ceiling and above the false ceiling these rooms are open to each other and the corridor. given the scenario that some rooms might have the windows open or the FCU is OFF in some rooms, it could impose a greater load on the coils of the 5 rooms in question, more than what the coil could handle.

I hope this clarifies the problem at hand because the Consultant is insisting that the comfort conditon might not be achievable without the walls.

Register to Reply
Active Contributor

Join Date: Feb 2011
Location: GTA Canada
Posts: 15
Good Answers: 2
#9
In reply to #8

Re: HVAC Return Air Fan Coil Units

05/22/2011 11:43 PM

A little more information would be helpful; FCU sizing for the common plenium units, room sizes, which rooms have openable windows, etc... But with the information at hand, I do not see any reason for concern.

Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#10
In reply to #8

Re: HVAC Return Air Fan Coil Units

05/23/2011 2:51 AM

Hi 786verycool,

I think Fredski's assumption that the full height walls may be 'Fire Walls' is possibly the reason why not all the rooms are closed off.

One question is left begging here though - you mentioned a 'consultant'.

Was this an existing design/installation, was it designed/installed by you or designed by the consultant? If the latter is true then the consultant should be aware of the advantages and disadvantages of using FCU's in conjunction with an open plenum. The problem of open windows plus FCU's that may not be switched on is incidental and should have been allowed for in the original calculations/design.

Regards, Keith

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11
In reply to #8

Re: HVAC Return Air Fan Coil Units

05/23/2011 8:11 AM

Okay I understand what you're asking now.

Let me start by saying I'll give you the best answer I can according to California codes and practices (your's could be far different). IF these spaces were originally designed as dwellings (apartments, condos, etc) then you have an illegal installation. The fire codes require a fire rated (times can differ depending on municipal codes being stronger than state codes) wall between units. The basic idea is if you had a fire in one unit and an open plenum serving all 35 rooms the plenum would allow the fire to very quickly race in the upper ceiling. However.

If this were originally designed as an open area office space the design is acceptable for that purpose. It's really rather common in general office space and medium rise buildings. Could the building have been converted from an office to an apartment building? So to your question.

Your consultant is correct. That is if you had 3 rooms that were 500 square feet each and each was sized with a fan coil to condition 500 square feet they would only function properly if all 3 were running roughly at the same time. If one unit goes offline on a hot day it's load would drag the other 2 down.

You could simply throw up some plywood up and seal them all off individually and call it a day. But before you do anything like that I'd consult your local codes, especially as they pertain to fire codes and material ratings. I can assure you if the building was designed here in California the builder would be getting a call form the building owners attorney (we like to sue each other a lot here). Even if the building was erected at the time as a dwelling and was up to code and no walls were EVER MOVED you have a fire hazard. You owe it to your tenants to provide a safe living space, not a fire trap.

I hope this helps.

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12
In reply to #11

Re: HVAC Return Air Fan Coil Units

05/23/2011 8:25 AM

I forgot to include a vital note. Here in California each unit must have 15% new, fresh or make up air (all 3 mean the same thing). Depending on code if you change the design of what you have you'll need to install fire dampers whenever you penetrate any fire wall. So if your existing plenum simply has a blower on the roof that's charging the plenum with X amount of fresh air you'll have a problem. Each unit will still require their individual 15% of fresh air. You'd have to duct individual fresh air ducting with fire dampers at each penetration you make.

I think when you look at the dollars involved to do it right you'll see why some contractors would skip doing this correctly and take off with the cash.

Register to Reply Good Answer (Score 2)
Associate

Join Date: May 2011
Posts: 30
#14
In reply to #12

Re: HVAC Return Air Fan Coil Units

06/15/2011 9:37 AM

Actually some of the rooms that are without walls all the way to the ceiling are offices. If the walls were completed then the plenum above the false ceiling of rooms would become pressurized because the 100 CFM of fresh air that we are supplying to each of the fan coil unit would have no way of exiting from the room, given that these offices do not have attached toilets. Had the toilets been there, the 100 CFM of excess air would have been drawn into the toilet by the roof exhauster. So the pressurized plenum would then interfere with the return air diffuser ???

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#13

Re: HVAC Return Air Fan Coil Units

05/23/2011 11:48 AM

A short duct between the return air grille in the room ceiling and the fan coil unit will solve your concern. The remaining concern will be noise transmission and cross talk with an open plenum but, depending on the usage of the space, that may not be a problem. However every piece of material in the plenum will have to be fire and smoke rated. I would vote for that inexpensive piece of sheet metal duct.

Lou Bindner

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: