Effect of External Interference in Partial Discharge Test

05/25/2011 9:13 AM

Can anyone tell the effect of external noise when we are doing a partial discharge test.

I heard that there will be some error if external interference is present....

__________________
If you can't find a way, make one........
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#1

Re: Effect of external interference in Partial discharge test

05/25/2011 12:09 PM

If there is external interference, you cannot determine if the disturbance if due to partial discharge or the external disturbance.

If you are able to increase the applied voltage slowly, the external interference will usually be displayed at a low voltage and the partial discharge will appear suddenly. (Except for oil filled equipment)