Wet Fiberglass Insulation at Chilled Water Lines

06/01/2011 2:06 PM

We have two chilled water lines within a walkable tunnel that have exposed piping. As a result the lines have condensed as the ambient temperature in the tunnel stays much higher then the chilled water lines. The chilled water lines must stay active. My question is can the fiberglass insulation which is saturated with condensation be replaced in its wet state with another type of insulation?.... such as cellular glass? Is there a means and methods to the re insullation of these chilled water lines while wet?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: Wet fiberglass insulation at chilled water lines

06/01/2011 2:48 PM

You could remove the fiberglass, and use a two part spray foam to permanently insulate the pipes.

I'm sure there are many better ways, this is just the first thing that came to mind. the spray foam would seal the insulation with a closed cell skin not allowing humid air to come into contact with the pipe, thus eliminating any condensation.

__________________
Don't believe everything you read on the Internet!
Register to Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#2

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/01/2011 5:23 PM

I'd go closed foam with duct tape to secure. Available at HVAC supply houses.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#3

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/01/2011 11:08 PM

John Manville has a good glass with acrylic wrap. We have used it in the past and it is very good and clean looking. We usually hire a company that specializes in insulation to complete the job so it looks professional. Good for hot or cold pipes. Not sure what length or size you are looking for but it is worth doing and a final solution.

The humidity in the tunnel may require some sort of dehumidifying process. It is the humidity in the air condensing on the cold pipe and dripping.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#4

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 12:08 AM

First make sure what you are removing really is fiberglass, many older plumbing installations were insulated with asbestos. Either way I would rather remove it wet as less fibers becomes airborne. Also, if the water line must stay active, it may also need to stay chilled, consider removing and replacing sections.

What you can replace it with will likely be determined by the size of the pipe. You are looking for something that will provide insulation and a vapor barrier. The closed cell foam shown by kramarat provides both when taped. It goes on fast, is durable, and unaffected by moisture. It's a good choice if you can find the size that fits your pipe. The pipes are probably large if you're looking at cellular glass. The manufacturer or distributor is going to be your best source for installation procedures for their product.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 12:35 AM

For larger pipes (say 2" or greater), one choice is expanded styrene or polyurethane foam, made in trough-shaped sections. An external vapor barrier such as Mylar, or bitumen-based "Insulrap", is essential; sheet PVC outer coating is too permeable to water vapor.

Joints in the insulation should be staggered/overlapped, and caulked. For longer pipe runs, where thermal expansion may be a factor, there are ways to make expansion joints in the insulation. Right now I am forgetting manufacturers' names, but they have installation guidelines. If you are good at cutting intersecting contours, you can do this yourself.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#6
In reply to #5

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 6:42 AM

You've got my vote... GA

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 7:00 AM

Heres a link to a site with different insulators and their operating ranges. http://www.crossroadsci.com/PRODUCTS/ThermalComparison/tabid/65/Default.aspx

I can't believe anyone would use glass where they knew moisture was a factor!

Anyways my vote would be to use "elastomeric". I've used this type of insulation about a million times. You can get more than 1 choice on wall thickness. I suggest you use the thickest wall that will fit in your application. The thicker the wall the less amount of heat that will be attacking your pipes. You can get this type of insulation that has been "split" from the factory. It's made to be slipped over existing pipes, almost all of them have 2 tacky surfaces that can form a tight seam once the insulation has been fitted and applied. Also be sure and seal all the joints and inspect them from time to time. So it's a good installation practice to have the gaps facing to where they can be inspected easily. Just a slight gap will allow warm air to enter and condense.

Follow my advice and you'll never replace the insulation again. Good luck

Register to Reply
Commentator

Join Date: Feb 2010
Location: Ceres, CA.
Posts: 61
#8

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 6:04 PM

Let me see if this is close.

We have applied a radiant barrier coating to interior AC ducts that were sweating heavily. It stopped the problem completely.

Think about it. Heat energy travels towards cold. In that process, it carries any humidity in the air with it until it runs into something solid, whether it's a wall, a pipe or an AC duct. That is why your pipes sweat, why your interior walls sweat in the winter, and why interior AC ducts can sweat.

Our URL is on my profile page.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9
In reply to #8

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 6:29 PM

Why did you put it on the inside?

Register to Reply
Commentator

Join Date: Feb 2010
Location: Ceres, CA.
Posts: 61
#10
In reply to #9

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 7:34 PM

Hi Fredski,

Our coating works as an insulating material on the inside or outside of a building or structure. It also works on the inside by not allowing any heat generated inside the building or structure to enter the walls or ceiling. On the other end of that, when applied to interior walls and ceilings, it also stops the radiant heat that has entered the walls and attic from radiating down /in to the living space.

It is a thermal energy barrier. Many people feel that because it is an Energy Star 'Cool Roof' coating, that is the only application where it is an effective insulation material.

It does alot more than roofs.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11
In reply to #10

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 8:27 PM

My question was about insulating the inside of ducts but thanks for taking the opportunity to make your sales pitch on all it's other uses.

Register to Reply
Commentator

Join Date: Feb 2010
Location: Ceres, CA.
Posts: 61
#12
In reply to #11

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/02/2011 9:16 PM

"Why did you put it on the inside?"

Thank you for making the question specific to ducts. I assumed you meant the "inside" of a building.

Guess I should of asked "Inside of what?".

Register to Reply
Associate

Join Date: Mar 2011
Posts: 29
Good Answers: 1
#13

Re: Wet Fiberglass Insulation at Chilled Water Lines

06/03/2011 12:29 AM

Pipe surface should be completely dry, hence stop chilled water flow for 24-48hours before applying adhesive or factory applied premoulded sections. Recommended insulations are nitrile rubber, poly urethane foam, expanded polyestyrene etc. Further ventilate tunnel to ensure fresh conditions & minimum humidity within. Fibre glass & rockwool are meant to insulate hot dry surfaces only

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Barchetta (1); Fredski (3); Geon Melek Zahir Ahsan (1); halskinner (3); kevinm (1); kramarat (1); RVZ717 (1); Tim in Mexico (1); Tornado (1)

Previous in Forum: The Internet   Next in Forum: Work Disrupt

Advertisement